    LB9 CNC lathe- No display from Monitor and VACIII unit

    Hi,

    I have been trying to repair this machine (CNC lathe LB9 OSP500L-G)and hope someone can help me with these:

    1) There is no display on the monitor when the machine's main breaker is
    switched ON
    The Control ON/Reset switch when pressed lights up with the NC status lamps and then all trips OFF. On tripping OFF, the OPUS 500 unit(CPU rack) shows 3 lamps on ON state; i) under voltage ii) +24V iii)+12V

    If CPU power supply module is removed from its "connector slot" and the main breaker switched ON, the Control ON/Reset switch lamp lights up when pressed.No alarm lamps light up on the CPU rack but +5VDC,+12VDC and +24VDC are measured on the power supply unit with the multimeter.


    2) None of LED's on the VAC III spindle drive unit are ON.
    The voltages measured between the inputs of 3P lines to the spindle drive unit are 200V AC.The labeling on the 3 phase lines are: R2B,S2B and T2B.
    The output lines to VAC motor (labelled U1,V1 and W1) measured zero between phases and 3.5V AC when measured to ground.

    On the spindle drive Control PCB, CN7 connector pins 1 and 3 measured 7.5V AC and connector pins 2 and 3 measured zero volts .As the measured voltages are not 19V AC the manual states to replace power supply unit.
    I have not found this power supply unit yet so I have decided to post this thread for feedback. Im a fitter machinist with CNC programing and machining experience and studying mechatronics.
    Please any help on troubleshooting the above mentioned problems will be greatly appreciated. Thank you


  2. #2
    Registered fordav11's Avatar
    Join Date
    Aug 2011
    Location
    Fordaville
    Posts
    1,668
    Downloads
    0
    Uploads
    0
    the 'under voltage' lamp suggests a power supply problem as you have found when you measured it and got 7.5V where there should be 19V.
    so you need to find the power supply that is the source of the 19V and check it / repair it / replace it.
    Power supplies are pretty easy to repair with some basic electronics knowledge and a little experience.
    It'll be expensive to buy a new one (if you can find one) but you should try getting it repaired at a TV repair shop or a similar place.


  3. #3
    Registered
    Join Date
    Oct 2011
    Location
    Fiji
    Posts
    13
    Downloads
    0
    Uploads
    0
    Thank you fordav11.
    After removing power supply board (VAC III unit with 50 screws on it) I found the transformer, magnetic contactor ,huge capacitor,transistors etc. behind the board.I discovered that almost all the screws represent test points on the power board so I fitted them back,switched on the main breaker and tested the board.
    The inputs to the transformer were the same as the outputs (200V AC between the 3 phases or 115V between a line and ground).

    The outputs from the transformer are connected to the magnetic contactor. There are no output voltages from the contactor and the two points for relay circuits of the contactor also measured 115V AC to ground.

    Please if some one can help me with the what the output voltage from transformer be for this VAC III spindle drive unit?


  4. #4
    Registered
    Join Date
    Oct 2011
    Location
    Fiji
    Posts
    13
    Downloads
    0
    Uploads
    0


    Ive found that the transformer I mentioned in my last thread is not a transformer but a choke coil.

    My eagerness to learn this electrical/electronics troubleshooting is making me feel stupid. My apologies.

    I would like to say thanks to diegojulio for the VAC III maintenance manual
    Im going through it and looking at my last thread the voltage measured between the two contact points of the relay for magnetic contactor was zero
    any one of these points to ground =115V AC
    The circuit for the relay for the magnetic contactor switch seems to be the problem

    Ill post again when sort fix this problem


  • #5
    Registered Algirdas's Avatar
    Join Date
    Mar 2009
    Location
    Lithuania
    Posts
    1,042
    Downloads
    0
    Uploads
    0
    1. Do You have electric diagram of the machine?
    2. Did You checked the +24V and, if it is there -24V ?
    3. Are You trying to fix spindle drive unit? It looks, the control doesn't powers up, so Spindle drive is not the first to fix ...


  • #6
    Registered
    Join Date
    Oct 2011
    Location
    Fiji
    Posts
    13
    Downloads
    0
    Uploads
    0
    Thanks Algirdas, with my little knowledge on electrical/electronics please guide me.

    1. Do You have electric diagram of the machine?
    No I do not have.

    2. Did You checked the +24V and, if it is there -24V ?
    Please help me on this one?

    Ive checked -24VDC on a power supply - maybe for servo board???
    Also measured +24V DC on (CPU power supply-rack insert type)

    If +-24V is not from above but from VAC III spindle drive unit then please help me locate it?

    3. Are You trying to fix spindle drive unit? It looks, the control doesn't powers up, so Spindle drive is not the first to fix ...


    yes i was looking to remove magnetic contactor switch to find out why its not relaying from the input to its output.

    Please point me in the right direction if not spindle drive?

    Ive just measured CN8 (is it connector 8 ?) between pins 3 and 4 and its about 287V DC . VAC III manual says if not 300V DC then no power is going to Control PCB.


  • #7
    Registered Algirdas's Avatar
    Join Date
    Mar 2009
    Location
    Lithuania
    Posts
    1,042
    Downloads
    0
    Uploads
    0
    Let's start from the beginning:
    1. no electric diagram.
    no comment. nothing to comment. I would strive to get the one whatever costs. Okuma dealer must be able to provide, I believe.
    2. +24V and -24V must be present on power supply block. It's in the CPU rack, most likely.
    if You have +24V on Emergency stop terminals, it means, that control is powered up. If You have ±24V somewhere else, it means, control is ready to be powered up. Roughly saying ...
    if control is powered up, You must see indication on OP. All indicators are on for a while on POST, to be sure they work.
    3. i was looking to remove magnetic contactor switch to find out why its not relaying from the input to its output
    please explain. what is not relaying from input to output?
    4. Is there a reason to dig inside the drive unit?
    can You switch on: - the machine; - the OSP?


  • #8
    Registered
    Join Date
    Oct 2011
    Location
    Fiji
    Posts
    13
    Downloads
    0
    Uploads
    0
    3. i was looking to remove magnetic contactor switch to find out why its not relaying from the input to its output
    please explain. what is not relaying from input to output?

    Ok I was sick and now im back. ive drawn a diagram attached
    There are voltages from the SDU input terminal to the magnetic (switch), but there are no output voltages from the magnetic switch to the three transistors.

    4. Is there a reason to dig inside the drive unit?
    can You switch on: - the machine; - the OSP?


    Yes can switch On but the machine is not booting up nor display from monitor.
    I was looking for the SDU power supply(stepdown,rectifier)...?? not sure...that is if DC voltage not from CPU or other power supplies.

    1. no electric diagram.
    no comment. nothing to comment. I would strive to get the one whatever costs. Okuma dealer must be able to provide, I believe.


    Ive emailed Okuma dealer after I read your comment and with all that ive read about Okuma, wasnt raising my hopes but i received the wiring diagram today,great.Thanks, Im trying to understand the Japanese/English on it ha ha .....ill post the above anyway....
    Attached Thumbnails Attached Thumbnails LB9 CNC lathe- No display from Monitor and VACIII  unit-e_vac_layout1_1.pdf  


  • #9
    Registered Algirdas's Avatar
    Join Date
    Mar 2009
    Location
    Lithuania
    Posts
    1,042
    Downloads
    0
    Uploads
    0
    but there are no output voltages from the magnetic switch to the three transistors
    Did You applied control voltage on contactor coil? No. Right, don't do that. Contactor is not on until is not commanded to. That's right
    but the machine is not booting up nor display from monitor
    this is a start position to diagnose: power supply first[/COLOR]
    i received the wiring diagram today,great
    Lucky You. Now You can handle where control voltage is missing and why.


  • #10
    Registered
    Join Date
    Oct 2011
    Location
    Fiji
    Posts
    13
    Downloads
    0
    Uploads
    0
    Please help
    Attached is the control Power Supply diagram.Ladder diagram?

    Cant figure out the control voltage between +AL and -AL.?
    zero voltage was measured between +-AL.
    Is there a problem with this power supply?
    Attached Thumbnails Attached Thumbnails LB9 CNC lathe- No display from Monitor and VACIII  unit-power_supply.pdf  


  • #11
    Registered Algirdas's Avatar
    Join Date
    Mar 2009
    Location
    Lithuania
    Posts
    1,042
    Downloads
    0
    Uploads
    0
    the diagram looks familiar :-) what it means:
    if voltage between AC1 and AC2 is about ~200V
    and
    there is no short circuit on +V -V terminals
    and
    P.S.C. unit is healthy
    and
    Control line "54N" is alive (+24V, I guess)
    then
    CB2 (Control Button #2 ?) is ready to switch on EC control voltage.
    ~~~~~~~~~
    if line "56N" is alive (+24V, I guess)
    EC control voltage can be switched on
    ~~~~~~~~~
    +AL_-AL can be spikes (pulse). Measuring as constant voltage maybe wrong. check it


  • #12
    Registered
    Join Date
    Oct 2011
    Location
    Fiji
    Posts
    13
    Downloads
    0
    Uploads
    0
    Thanks again Algirdas

    After some testing there is DC 24V across 54N and 56N and also across +V and -V so there's no problem with the control power supply.

    Testing the CPU power supply there are DC +5V, +12V, +24V, ISO+24V on its test terminals when powered ON and not connected to CPU rack

    When connected to CPU rack and powered ON, none of voltages appeared(measured) on test terminals. Power supply alarm indicating lamps on CPU rack light up for under voltage, +24V and +12V.

    From the manual these alarms indicate abnormality in the power supply or in input or output parts.

    Please help me from here
    From the above tests there don't seem to be a problem with power supply?

    assuming the problem to be output from power supply to bubble memory(bubble memory require DC +24V and where loading is done) I cant tell if my system is loading or not because there is no display on control panel
    How can I test the bubble card or CRP Board -II D which interfaces Control panel?
    Or am I missing something ???????

    another glitch!!;
    Is it ladder diagram on control power supply diagram attached last thread?

    Ive done PLC programing and interfacing but I still cant find what some of the symbols represent on the wiring diagrams?
    i) two arrow heads ( PS diagram)
    ii) line with circle and labelled pt (PS diagram)
    iii) switch (normally open contact) with a number written to the left and right of it. what the numbers indicate?
    iv) capacitor symbol or something else?( across +AL and -AL ---PS diagram)

    Any help, contribution on the above will be greatly appreciated.
    Thank you


  • Page 1 of 2 12 LastLast

    Similar Threads

    1. Need Help!- Have basic ?s about Set-up, and Display Positions For Hass SL Lathe.
      By Stampede in forum Haas Lathes
      Replies: 3
      Last Post: 02-26-2010, 06:25 PM
    2. Problem- Maztrol M32 - No monitor display No drive light
      By nbodie in forum Mazak, Mitsubishi, Mazatrol
      Replies: 3
      Last Post: 09-17-2008, 03:26 PM
    3. Change Japanese display on monitor?!
      By nkd in forum CNC Machining Centers
      Replies: 1
      Last Post: 04-02-2007, 05:29 PM
    4. spindle unit for a lathe
      By veteq in forum General Metal Working Machines
      Replies: 4
      Last Post: 01-18-2007, 06:39 PM
    5. Problem with OM Monitor/Display
      By darrylh in forum Fanuc
      Replies: 0
      Last Post: 01-13-2006, 07:04 PM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.