    Exclamation Fan alarm 2060 in OSP200L

    Help me please! I have an alarm in an OKUMA control OSP200L; 2060 ALARM B FAN ERROR IN PC UNIT 10101, I find the fan destroyed, I changed it, but the alarm not dissapear, what else must to do?


  2. #2
    Registered Superman's Avatar
    Join Date
    Dec 2008
    Location
    Krypton
    Posts
    1,769
    Downloads
    0
    Uploads
    0
    Try checking the thermal overload relays ( in the elect. cabinet ), one may need resetting

    These act like a fuse on a circuit if too much current get drawn through them


  3. #3
    Registered
    Join Date
    Jun 2009
    Location
    Mexico
    Posts
    93
    Downloads
    0
    Uploads
    0

    Red face The problem continuoes

    I've checked al thermal overloads relays, are OK.
    The problem persists!!!


  4. #4
    Registered
    Join Date
    Jun 2009
    Location
    Mexico
    Posts
    93
    Downloads
    0
    Uploads
    0
    Superman, do you have another recomendation?


  • #5
    Registered Superman's Avatar
    Join Date
    Dec 2008
    Location
    Krypton
    Posts
    1,769
    Downloads
    0
    Uploads
    0
    I am unfamiliar with a OSP200L ----what model lathe is it ?

    Sometimes there is more than 1 fan,
    I'm guessing that you have checked all of them ?
    If we knew what machine, others may know how many fans there should be.

    Find a fan, you know is working on a different machine, using a multi-meter,(machine turned OFF and with the wires disconnected ) measure the resistance arcoss the wires and compare this reading to the other fans on the faulty machine, you may find one that you thought was working.

    Some other questions are...
    Why or How did they become faulty ?
    Is there anything in the surrounding area that contributes to the problem ?
    ie. oils, coolants, dust, dirty filters, regular maintainence being done,

    I've seen where a fan has become faulty after a hot motor melted the insulation out of the fan, the actual fault was in the motor

    So be advised, there may also be a bigger problem just around the corner
    you may be lucky, and it's just the fans


  • #6
    Registered
    Join Date
    Jun 2012
    Location
    usa
    Posts
    5
    Downloads
    0
    Uploads
    0
    I realize this is is an old post but i thought i would reply in case somebody searches for it like i did.

    i had this same problem/same alarm this morning. inside the control panel there is a small CPU fan, it had run its course. Took a drive to the local computer repair shop and picked up a new fan and we are back up and running like new.

    (note: the fan i got from the shop had the wires in a different order, had to re-arrange the colors to match the fan i took out, but other than that, went without a hitch)


  • Similar Threads

    1. ALARM shuttle drawbar alarm haas
      By timmydabull in forum Haas Mills
      Replies: 28
      Last Post: 02-18-2013, 01:47 PM
    2. Replies: 6
      Last Post: 04-29-2011, 06:20 PM
    3. Need Help!- 750 ALARM SPINDLE-1 ALARM DETECT (AL11)
      By PICMAN in forum Fanuc
      Replies: 9
      Last Post: 03-27-2011, 07:14 PM
    4. Alarm 409-servo alarm- z axis torque alm
      By jessebpm in forum Hyundai Kia machine
      Replies: 3
      Last Post: 06-14-2010, 08:45 PM
    5. Need Help!- DAEWOO 8 Steady rest pressure alarm, External feed hold alarm
      By doubleeagle in forum Daewoo/Doosan
      Replies: 4
      Last Post: 06-12-2009, 04:15 PM

    Tags for this Thread

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.