  1. #41
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Quote Originally Posted by retske View Post


    If I'm reading this right, 24v applied to 510/511 wire would signal Spindle Enable Off; would this bypass the controller to look for it?

    I tested the voltage off the board and 760 has 24, but 770 does not. In fact everything in that bundle have 24 except 770.
    But wouldn't supplying 770 with 24V give it the inverter fault signal?
    As far as I can tell, 770 wants to have 24V+ to signal OK. I don't think 770 is in 510 circuit. 770 might be connected through the overload contacts on M5, if they exist.

    The schematic I supplied should only be used as a guideline. It is probably close but not exactly like your machine.



  2. #42
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Same errors, with 24V going to both 760 and 770.

    760 and 770 run to the grey block below, which is labeled inverter 1.



    Attached Thumbnails Attached Thumbnails TB Woods Inverter to Perske Programing-img_20170928_102631-jpg   TB Woods Inverter to Perske Programing-img_20170928_102636-jpg  


  3. #43
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Now I'm confused. This is beginning to sound like a parameter setup issue in the controller. I suspect the original file was set to ignore the inverter feedback and the current file wants something that we haven't figured out yet. When working OK the MultiCam system works fine, but for troubleshooting it leaves something to be desired. Especially when getting documentation is next to impossible.

    I have attached a UC (with a txt extension) file from the router I have been working on. The first 20 lines or so are the calibration parameters for the axes, but not sure what the rest does. But it might be worth comparing your file with one that is running on a similar system. The primary difference between the two is that my file has a tool changer installed.

    I know a MultiCam genius in my local area, so I may have to get you guys together. I'll send a PM with his contact information.

    Attached Files Attached Files


  4. #44
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Here are the only parameter descriptions that I have




    Attached Thumbnails Attached Thumbnails TB Woods Inverter to Perske Programing-20160930_155612-jpg   TB Woods Inverter to Perske Programing-20160930_155549-jpg  


  5. #45
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Thank you, that would be awesome. I was beginning to suspect that it was in the program somewhere, because of the timing and the fact that nothing has made any impact. Again, thank you for your help. I'll let you know how this turns out.



  6. #46
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    When I try to run a program, Motion Mechanic says the MODBUS is not initialized. I'm wondering if there is a missing setting for the modbus.



  7. #47
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    This might be helpful. Look at parameters 290 and 291

    http://www2.ketele.com/techdocs/Mult...Flash_List.pdf



  8. #48
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    I saw those, so would changing 290 to 0 , would that say the the slave(which I assume is the inverter) is not controlled by the controller?

    What about para 30? Mine is set to 0, the file you sent is 3. I have an M24 K520, so if I change that, that may solve this?



  9. #49
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    I don't know. It can't hurt to try. Just make sure you have a backup file of the original.

    This is how you read and set the values from Motion Mechanic terminal

    Read:
    30 gi .


    290 gi .



    And to set the value:
    X 30 set_integer (or set_float in the case of a floating point value)
    X 290 set_integer

    where X is the value to be set



  10. #50
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    After some searching in that doc you sent:
    Para 109: set that to Tool=** That sounds like an external tool on the system is used. Does that sound good?

    Para 176: set this to 1 for do not use?

    Para 196 and 300: Maybe change that to disable MODBUS. 300-307 set to 0, then I just control externally?



  11. #51
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    109 that seems reasonable
    176 0 seems like the correct setting in this case
    196 0 seems to be the correct setting
    300-307 0 seems correct, since there is no MODBUS comms with the inverter.

    Disclaimer: I'm making my best guess based on the available information.

    Changing the parameters should not cause any permanent damage so normally safe to experiment.



  12. #52
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Set all as we discussed, except 109 which is left set 0. 300 was set 1.

    Now my job console repeats fault detected when I load a program.
    JC :TIMER_JM_SETUP



  13. #53
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Communication timeout maybe? Maybe a setting in Job Server?

    Change the value of 290 maybe? I can't find any timeout parameters.



  14. #54
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    I found these regarding JC error Looks like it might be a software setup issue in Job Server or at least on that end somewhere.

    JC Start Error - Xenetech :: Knowledgebase

    https://talk.dallasmakerspace.org/t/...rt-error/14141

    EDIT: I have to be gone for about 3 hours or so.



  15. #55
    Member mactec54's Avatar
    Join Date
    Jan 2005
    Location
    USA
    Posts
    15362
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Quote Originally Posted by retske View Post
    When I try to run a program, Motion Mechanic says the MODBUS is not initialized. I'm wondering if there is a missing setting for the modbus.
    If you changed anything in the computer, or reloaded the software then the Modbus would have to be setup, I did also think that some of these use Modbus for spindle control also, but that would be if the VFD Drive had Modbus

    Mactec54


  16. #56
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Yeah, I finally got it worked out in there. I had the tech from the manufacturer remote in and he never mentioned that as a potential issue.

    The good news is that I understand this machine a lot more than I ever need.



  17. #57
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Is it running now?



  18. #58
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    Yes-ish. I got the JC error cleared, just had to go to connection manager and delete and reinstall the machine. Now I'm getting a Z height thing, but that might be the job itself. But as far as I can tell it should be good once I have the right job in.



  19. #59
    Community Moderator Jim Dawson's Avatar
    Join Date
    Dec 2013
    Posts
    5717
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    AWESOME !



  20. #60
    Registered
    Join Date
    Sep 2017
    Location
    United States
    Posts
    39
    Downloads
    0
    Uploads
    0

    Default Re: TB Woods Inverter to Perske Programing

    I'm going to say it is official, she works.



Page 3 of 4 FirstFirst 1234 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  


About CNCzone.com

    We are the largest and most active discussion forum for manufacturing industry. The site is 100% free to join and use, so join today!

Follow us on


Our Brands

TB Woods Inverter to Perske Programing

TB Woods Inverter to Perske Programing