I see the problem. I would have to be sitting in front of that inverter with the manual in my hand to program it. That is a pretty sophisticated inverter and a manual written for a controls engineer. It's about like trying to read some of the Chinese - English translations.
Section 3 is where you want to start, then read through section 4
Take a look at parameters 31 and 32. I think 31 should be around 120 and 32 should be 400. 32 should match the spindle motor data plate HZ
Parameters 21 and 24 sets the input mode. In other words where the run and frequency commands are coming from, Keypad or terminals.
Parameters 42 and 43 are the accel and decel, in seconds, factory default seems to be 3 seconds. Probably should be more like 5- 8 seconds for a spindle motor.
If it will run with parameter 51 set to 6, vector control mode, that would be my preference. Follow the auto tune instructions in section 3.9
Parameter 59, set to motor rated voltage.
I'm not able to find the Motor Rated Amps parameter, normally it's obvious.
I hope this helps.