Hi for all!
Problem:
Mori Seiki SH 5000/40 with Fanuc 18i/MSG-501 control. (APC with 2 palets)
When turning on machine, system is booting and after massege "Open and close the door" when I open and closed the door turning on power for servo amps ATC and APC (SVU-20), in some seconds turning off it and after that turning on it again excepting APC servo amp.
Not any alarm or massage after that and not any movement.
Is there anybody who can explain me what may be the cause of this behavior?
Thanks in advance!
Similar Threads:
Last edited by coldrex; 06-04-2013 at 01:37 PM.
See the Interlocks in ladder
APC servo amp won't show much until time for pallet change. Check the MPG and make sure it's snapped in to the holder tight.
I have Servo alarm (APC) EX1664 (319).
And in manual operation do not rotating palet changer.
I am working with Mori Seiki the first time and know not so much about it.
So I need help very much.
The EX stands for External Alarm ( you can see the Details in ladder ) , Might be Check the Field Components / Fittings like , Air pressure / Proximity / Limits / Adjustments etc..
You will need to go to the PMM (power Motion Manager) and see what alarm is on the Beta power mate controller. Most likely a dead battery and need zero return.
Thanks for advices to all. It needs to set zero points so I am looking for Zero Point Adjustment SH5000-8000 instruction.
Both codrex and Cabron, Have you gotten the problems fixed? Did you get the home procedures? If not please let me know