    Quote Originally Posted by Wiseco View Post

    If you plan to stripped the machine, consider to go with 24vdc input and output. They are safe and wire can be smaller.
    I agree with the 24vdc, even for the solenoids, the beauty of DC for solenoids, you do not get the burn-out failure for stuck armatures or somebody pushing them over manually, like you do with AC type.
    Also to conserve wiring space, I have gone over to using TR64 instead of TEW as the OA dia. is greatly reduced, still 300v rating.
    Its a bit harder to get, but when you have a bundle of 20 or 30 wires, it makes a difference.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  2. #14
    Registered
    Join Date
    Mar 2005
    Location
    USA
    Posts
    34
    Downloads
    0
    Uploads
    0

    Trol PLC

    For a bare bones PLC try www.trolsystems.com Kind of like PLC for dummies. Not fancy but easy to program. Use some digital temp controls from e-bay or PPEs budget catalog. You got a control for around $1000 or less.
    Richard