    We have in our shop 3 phase 230 volt power,

    We purchased an air compressor a year ago, It uses single phase 230 volt power

    I hooked it up last year and its been working since with no problem.... Until Today. Pop it on and nothing happens, magnetic starter doesnt pull down, motor doesnt turn on

    Troubleshooting I've done.

    I get L1 to ground and ground to neutral 110 volts, not a problem, thats expected, but to go L1 to neutral (in reality L1 to L2 since I have 3 phase) I get 0 volts,

    I reiterate, NOTHING Changed from last night to this morning, and suddenly my compressor doesnt work and the power to the compressor magically defies the laws of electricity.

    Any guesses?


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,958
    Downloads
    0
    Uploads
    0
    Not quite following the logic?
    If you have 3 phase star, then the star is usually at ground potential, you would then expect 110v from each phase to either ground or neutral.
    If you have a Delta supply, (doubt it) things may be different.
    What is the reading across all three phases?
    Sounds like you have lost a phase, have you checked all fuses?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered
    Join Date
    Feb 2011
    Location
    USA
    Posts
    24
    Downloads
    0
    Uploads
    0
    No fuses, simple circuit breaker for "on/off"

    what has been done in order to supply the compressor motor with its single phase in 230 volts is to use legs 1 and 2 of the 3 phase and also the ground

    now, ostensibly that should give me no reading L1 or 2 to the ground and simply 230 from L1 to L2

    mathematically and logically that works in theory, (and reality till a day ago)

    but now I'm coming up with current L1 to ground and L2 to Ground but nothing L1 to L2

    I'm leaning towards a combination of your theory of having lost a phase along with another one of a re-wired (without my knowledge) plug/receptacle

    I tested the receptacle and I got L1 to Ground 230, L2 to ground 110, and L1 to L2 nothing, Guess I have to open the recep and see what the heck gives, not sure why at the compressor box I get 110 L1 and L2 to ground and recep something different though

    so current best guess is recep is wired so ground is really L1, L2 is really ground and L1 is really common? (except in 3phase I didnt think there was truly a common

    <-- idiot supplicant to the electrical Gods for a miracle


  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,958
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by AndrewEvans View Post
    No fuses, simple circuit breaker for "on/off"

    what has been done in order to supply the compressor motor with its single phase in 230 volts is to use legs 1 and 2 of the 3 phase and also the ground

    now, ostensibly that should give me no reading L1 or 2 to the ground and simply 230 from L1 to L2
    Not by my reckoning, like I said it depends on what type supply you have, but normally I would expect L1 & L2 to read ~110v to ground, if your 3 phase secondary is not referenced to ground, there would be no point in taking a ground to the compressor, it is not going to achieve anything.
    A 208 3 phase system would give you around 120v to star point.
    http://www.allaboutcircuits.com/vol_2/chpt_10/5.html
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #5
    Registered
    Join Date
    Aug 2007
    Location
    Australia
    Posts
    2
    Downloads
    0
    Uploads
    0
    THere are two explanations for what you have measured:

    1. L1 & L2 are now for some reason in phase.

    2. You have lost one phase and are using a high impedance meter, which is picking up a stray voltage from some connected piece of equipment.

    Obviously you have a supply problem, and 2. shows why in the electrical field we are taught to disconnect, then test again!


  • #6
    Registered
    Join Date
    Aug 2009
    Location
    US
    Posts
    3
    Downloads
    0
    Uploads
    0

    Logic of electricity.

    Remember, when you lose the supply to any leg to a motor, the other leg feeds back through the motor winding and you'll read the L1 voltage on the L2 leg, or L2 on L1. If you check with an oscilloscope, and you'll find they are in phase and there is no voltage difference between the two.

    The same is true with any light bulb circuit. If you interrupt the neutral return, and you read the same voltage on each side of the filament, but no difference of potential that will light up the bulb.

    Easy way to diagnose: Disconnect the motor from the supply and then check the supply voltages. One of them is likely gone. When the motor is disconnected, you can also check DC resistance of the windings (should be only a few ohms).


  • #7
    Registered
    Join Date
    Feb 2011
    Location
    USA
    Posts
    24
    Downloads
    0
    Uploads
    0
    after much to-do and heming and hawing I have it resolved thanks to your huge amounts of help.

    Well, the motor, the wiring (in the compressor & compressor plug) was just fine, but the receptacle wiring was a bit wonky & yep I lost my 3rd leg finding WHERE it was was a pain, turned out to simply be the breaker, guess thats what you get after 40 years

    maybe it'll be a while before I have to touch the zappy stuff that makes my machines go *crosses fingers* I'm no grease monkey but I sure enjoy mechanical more than electrical troubleshooting


  • Similar Threads

    1. Need Help!- A electrical moron
      By Edgdais in forum Mach Software (ArtSoft software)
      Replies: 1
      Last Post: 10-08-2010, 11:06 AM
    2. Need Help!- Electrical schematic
      By JerryF in forum General Metal Working Machines
      Replies: 0
      Last Post: 11-06-2008, 01:34 PM
    3. Need electrical drawings!
      By mte.jalal in forum Cincinnati CNC
      Replies: 7
      Last Post: 10-15-2008, 05:05 PM
    4. electrical noise on X2
      By X2cnc in forum Benchtop Machines
      Replies: 5
      Last Post: 08-27-2008, 01:58 PM
    5. well the electrical part is almost done
      By truman in forum DIY CNC Router Table Machines
      Replies: 2
      Last Post: 08-13-2006, 12:04 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.