Question on wiring the Powermax 85

I have read the section in the manual regarding the electrical hook up of the power supply
and understand Hypertherm recommends using a disconnect switch and slow blow fuses.
However, I would like to install a plug on the power cord to be able to plug into two separately located wall receptacles in my shop.
I have single phase 100 amp 220 volt service in my building. What size breaker should I use to do this?

If you guys could share your set-ups that would be appreciated.

If this plan is totally not recommended please share that as well.

Thanks in advance for all your input.

Regards, Ian
Reply With Quote

  #2   Ban this user!
Old 05-17-2011, 08:24 AM
 
Join Date: Jan 2008
Location: USA
Posts: 1,586
jimcolt is on a distinguished road

The breaker size is dependant on the voltage that you have available to operate your Powermax85. It can operate on voltages from 200 volts to 600 volts, single or three phase. The current (amperage) draw is highest at the low voltages and lowest at the highest voltage.

Let me know what your input power is, and I'll show you where (in the manual) you can find the breaker and amperage sizing information.

Jim Colt


Originally Posted by iou View Post
I have read the section in the manual regarding the electrical hook up of the power supply
and understand Hypertherm recommends using a disconnect switch and slow blow fuses.
However, I would like to install a plug on the power cord to be able to plug into two separately located wall receptacles in my shop.
I have single phase 100 amp 220 volt service in my building. What size breaker should I use to do this?

If you guys could share your set-ups that would be appreciated.

If this plan is totally not recommended please share that as well.

Thanks in advance for all your input.

Regards, Ian
Reply With Quote

  #3   Ban this user!
Old 05-17-2011, 09:14 AM
iou iou is offline
 
Join Date: Jan 2011
Location: USA
Posts: 8
iou is on a distinguished road

Thanks Jim, but you might have missed it. I have single phase 240 volt (checked with a DVM) 100 amp service in my building.

If you are referring to the table on page 2-8 it only mentions 100 amp slow blow fuses at 230-240v single phase.

I also understand that I will need to change out the power cord for a 3-wire 6ga cord.

Thanks for the help. Maybe I missed something or maybe I've got under-sized service for an over-sized machine.
I just jumped on this deal without fully understanding it requirements. The only thing I really paid attention to was the single phase 240 volt input.

You've been a ton of help, and I'd like to get this thing up and running and work towards my cnc table goal which I'm sure will pose more questions.

Thanks again,
Ian
Reply With Quote

  #4   Ban this user!
Old 05-17-2011, 09:44 AM
 
Join Date: Jan 2008
Location: USA
Posts: 1,586
jimcolt is on a distinguished road

Sorry Ian, I must have read your post too quickly...now I see that you have a voltage listed!

The information that is supplied in the manual is based on National Electrical Code rules. There are occasional local code requirements that supercede the NEC....so it most often is the best practice to consult with a local electrician for this kind of advice.

You can refer to the wire conductor sizes listed in section two of the manual which are based on length of the wiring to the outlet...obviously if the length of the wiring to your outlet is over a certain length...then the conductor sizes need to be larger. Most users of Powermax85's are running on 100 amp circuit breakers without any issues. Under the majority of cutting conditions the actual draw of the Powermax 85 will be less than 60 amps.....higher input current draw will only occurr when you are stretching the arc or cutting materials that are near or exceeding the maximum recommended thicknesses. Cutting thinner materials, even at full amperage output, will draw much lower current.

I have been running my Powermax85 on a 60 amp circuit for about 6 months.....and have cut up to 3/4" steel without any issues. I use a 50' SO type extension cord (#6 awg wire) and am using standard 50 amp welder plugs......(none of which meets code). If I did a lot of production cutting...or cutting thicker materials I would expect to trip the breaker.....and overheat my extension cord or plugs/receptacles.

Slow blow fuses are recommended as plasma systems tend to have a very high inrush current rating...when the arc fires the power supply draws a lot of power for a few miliseconds in order to establish and maintain the arc. If there are issues with even a 100 amp circuit breaker tripping....it would be recomended that it be replaced with a breaker with a high inrush rating. This specification is less of an issue with todays highly efficient inverter power supplies...and it is extremely rare to hear of an inrush current issue.

If you decide to use a disconnect switch box (either by choice or by local code requirements) often the disconnect boxes have fuse slots....and inrush current is why "slow blow" fuses are recommended.

Receptacles for 100 amp single phase connections are available....but not at the local Home Depot!

Best regards, Jim Colt

Originally Posted by iou View Post
I have read the section in the manual regarding the electrical hook up of the power supply
and understand Hypertherm recommends using a disconnect switch and slow blow fuses.
However, I would like to install a plug on the power cord to be able to plug into two separately located wall receptacles in my shop.
I have single phase 100 amp 220 volt service in my building. What size breaker should I use to do this?

If you guys could share your set-ups that would be appreciated.

If this plan is totally not recommended please share that as well.

Thanks in advance for all your input.

Regards, Ian
Reply With Quote

  #5   Ban this user!
Old 05-17-2011, 09:59 AM
iou iou is offline
 
Join Date: Jan 2011
Location: USA
Posts: 8
iou is on a distinguished road

Thank you Jim for your quick and honest reply that answers all my questions.
This gives me a good place to start and sets up a trip to the local electrical supply/electrician for some more reassurance.
I can't wait to finally flip the switch.

Thanks again Jim for all your help.
Ian
Reply With Quote

Sponsored Links
Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Powermax 45 question cruzin Hypertherm Plasma 10 04-27-2011 12:25 AM
Powermax 85 question tinman13 Hypertherm Plasma 10 03-03-2011 06:45 AM
powermax 600 wiring for cnc control landmark Hypertherm Plasma 1 04-18-2010 08:32 PM
Powermax 45 question microdot Hypertherm Plasma 3 12-17-2009 12:02 PM
Wiring in Powermax 600 IHscout Plasma, EDM and other similar machine Project Log 1 10-21-2009 08:51 AM




All times are GMT -5. The time now is 03:56 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361