Replace U14 & U15 on the CPU (MC1488 & MC1489), replace the MC1488 & MC1489 on the CRT controller and also the P8255A on the CRT controller.
Hi i recently acquired an MD1 Hurco
we installed it and got it running yesterday and was running some small test programs and changing tools all fine
it would appear that the machine has developed a fault when i switched it back on today the system boots to the main page
but wont respond to any control inputs is this a common fault with the control ?
would like advice as in either repairing the existing control or obtaining a wiring diagram for the machine to retrofit a new control in its place (EMC2)
Thanks
Replace U14 & U15 on the CPU (MC1488 & MC1489), replace the MC1488 & MC1489 on the CRT controller and also the P8255A on the CRT controller.
Thanks for the info
What is it these parts do ?
are they all in the main computer cradle in the rear cabinet ?
thanks
-Colin
The CPU is in the rear cabinet, the CRT controller is in the console.
ok thanks
iv found the parts on eBay hopefully it will solve the problem
is the P8255A replaceable with P8255A-5?
Not tried it but it should be ok.
You could also use an Intel P82C55A2 or an NEC D71055C-10
I did as you suggested but is hasn't cured the problem, is there anything else i can try ?
Not without a few boards to try swapping. Where are ya in blighty?
Brackley, Northamptonshire
its near to silverstone race track
i do have a spare hurco computer but i cant gaurantee the state of that one as i stripped that for mechanical spares due to faulty memory boads
When you say it boots to the main screen. Is this the configuration screen (where it shows the machine travel limits) or will it exit to the main input screen?
If it is on the config screen, are the displayed values in Metric or English?
If in Metric then press the bottom softkey, press enter button, press 999, then press enter button again. then select exit (Bottom softkey).
Control should reboot and display english values for travels.
Goodluck
yes stuck on the config screen
its displaying limits in inches
and softkey is unresponsive