    Question Need Help

    We have an older Conquest T42 with a Fanus 18T control that was working fine the last time it was run, which was several weeks ago. When it was fired up today it had several alarms which are (1040 - Low Hydraulic Pressure), (1000 - OVL {OL-1 & OL-4}), and (1012 - Coolant pump overload). Any ideas??



  2. #2
    Member
    Join Date
    Apr 2011
    Location
    USA
    Posts
    841
    Downloads
    0
    Uploads
    0

    Default Re: Need Help

    Those are fed to the PMC as 24vdc inputs. I would check the 24 volt power supply. If that checks OK then see if those inputs are on the same I/O board. You may have tripped a breaker that feeds the I/O due to a short some where



  3. #3
    Registered
    Join Date
    Oct 2014
    Posts
    4
    Downloads
    0
    Uploads
    0

    Default Re: Need Help

    Thank you for your thoughts, we will be looking into this this morning, i will let you know what we find.



  4. #4
    Registered
    Join Date
    Oct 2014
    Posts
    4
    Downloads
    0
    Uploads
    0

    Default Re: Need Help

    To drdos, you were correct, we have a weak transformer within the power supply.
    Thanks again!!!