Phase Converter Sizing & Compressor

I'm looking at purchasing a Super Mini Mill 2 (10K spindle) and an SL-10. From all the reading I've done it seems like the Phaseperfect phase converters are the way to go. My question is in regards to sizing. These machines are going in a home workshop. The Phaseperfect is supposed to be sized according to the actual horsepower of the machine. I've figured out from reading that the 15 HP rating of each of these machines is the max horsepower based on some short period of time. The nameplate rating on the motor is something less however Haas doesn't tell you what it is.

From reading Haas' preparation document it says that each of these machines has or needs a 40A machine breaker with a recommended service of 50A.

I called Phaseperfect. They seemed to think that I needed the PT-355 if I was only running each machine separately or the PT-380 if I wanted to be able to run them both at the same time. With the PT-355 they said I'd need a 125A breaker on the input side and for the PT-380 a 200A breaker. They were using the 1.73 factor to get the conversion on the single phase side. I think they were also concerned with any starting loads. My question is, do you think those recommendations are about right? Or is that overkill?

My house currently has the standard 200A service. In talking with an electrician no matter what I do I'm going to need to upgrade the service coming into the house to 400A from 200A at a cost of somewhere between $9K-$12K. I'm then looking at another $4700 (PT-355) or $6200 (PT-380) for the phase converter.

To throw another variable into the equation, I'm looking at a rotary screw compressor. The Chicago Pneumatic seems to be the most cost effective solution with a QRS 7.5 with dryer costing $5937 for the single phase model or $5244 for the 3 phase. So, do I go with the 3 phase and the larger phase converter? Can I get away with the smaller phase converter, run both Haas machines, and the compressor?

All of this is a bit confusing to be sure. The only reason I'd want to go with the QRS 7.5 as opposed to the 5 or 3 HP models is that the 7.5 is rated for 21CFM for airflow and I have a small blasting cabinet. That 21CFM rating is at the max pressure of 150 PSI. I think the blasting cabinet only uses about 20CFM at 90PSI. Won't I get a better CFM rating from the compressor at 90 PSI as opposed to max pressure (150PSI)? Note that I'd never plan on running the blasting cabinet at the same time as either of the Haas machines.

Wow, the price of this machine is really starting to add up when I figure in a new compressor, phase converter, and electrical service. And I haven't even gotten to tooling yet.
Tweet this Post!Share on Facebook
Reply With Quote

  #2  
Old 07-27-2009, 05:23 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

You are probably realizing that you are approaching a small industrial set up running from a residential service!
It may soon reach the point where you are going to bite the bullet and go into an industrial 3 phase equipped shop?
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 07-28-2009, 11:20 AM
 
Join Date: Jan 2007
Location: US
Posts: 422
TravisR100 is on a distinguished road

Any opinions on the sizing of the phase converter, Al?
Tweet this Post!Share on Facebook
Reply With Quote

  #4  
Old 07-28-2009, 12:42 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

The maximum hp rating is generally stipulated for 1/2 hr run period, continuous is generally two thirds that.
If you are going to run two or three items at a time, you have to consider your residential load also, such as stoves, dryer, air conditioner etc, being on at the same time, so I would say the 400amp would be right.
You may just squeak by with the 20hp rated PT-355, but often it is best to go with the higher margin, if later you find you need more capacity, you may kick yourself for not paying the extra.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 07-28-2009, 03:35 PM
 
Join Date: Apr 2005
Location: Paradise, Ca, USA
Age: 34
Posts: 513
Matt@RFR is on a distinguished road

If I were you, I'd look in to having your power company set you up with 3 phase. The cost of the single phase, 400A drop plus the phase converter may not be that much less than going 3 phase completely.

For your reference, I'm running a VF-2ss on a 200A single phase drop with a 50HP American Rotary phase converter. I can tell you that I'm RIGHT on the edge of not having a big enough service. I bought that phase converter incase I ever add machinery. American Rotary had to build me a custom panel with a **** load of capacitors and some different electronics just so I would keep from blowing the fuses on the power pole!
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 07-28-2009, 04:40 PM
 
Join Date: Oct 2007
Location: USA
Posts: 18
TEntpeg is on a distinguished road
Talking Phase Converter Sizing and Compressor

[QUOTE=TravisR100;643886]I'm looking at purchasing a Super Mini Mill 2 (10K spindle) and an SL-10. From all the reading I've done it seems like the Phaseperfect phase converters are the way to go.

[snip]

Travis, we are in the same boat.
I am a long time lurker and hobby machinest wannabe.
The price of admission is really steep for a hobby but in the end you own the shop and the machines for a life time of use. What could be better?

All of the rotary phase converter (RPC) folks will tell you the same thing regarding the power requirements. You can do the math yourself to prove it. The last thing you want to do is have the Haas tech tell you that the intermittent alarm problem is your marginal power supply. Go for the largest phase converter you can afford. I run a 40hp RPC off a 200 amp subpanel for a VF 1 and an SL 10. There is only me in the shop and I really not sure that I have the projects to keep them both running simultaneously. Besides, if the power consumption runs too high you may have unmarked vehicles surveiling your "grow-op"

The next question is why do you think that you need a digital phase converter? I think that four members on this forum run RPCs for their machines including a VF 2SS.
Why spend $6200 for a digital when you can get a 40hp RPC delivered for less than $3000?

I spent quite a bit less than what you are being quoted to upgrade to 400 amps.
I contracted out the trenching to run a new line. The electrician hooked up the incoming power to the new 400 amp service panel, made the existing house panel into subpanel "A" and ran 4-0 to subpanel "B", which became the shop panel. Then you can run the rest of the shop power yourself. Learn how to bend conduit and all about ampacity in "Ugly's Electrical Refernces" ISBN 0-9623229-6-2. Just make sure that you do it all to code or above.

A rotary screw compressor sure looks nice, but do you want to spend your hard earned cash on tooling, toys and stock or do you want it sitting in a compressor shed? A 5 hp reciprocating 220v compressor with a 5 micron pre-filter, a coalescing filter and a dryer should do about 80% of what you want for less than $2000 or are you really going to be sand blasting all day long without stopping ??? Just askin

regards

TEntpeg
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 07-28-2009, 04:46 PM
 
Join Date: Jan 2007
Location: US
Posts: 422
TravisR100 is on a distinguished road

Tentpeg, thanks for the info. Reading the Haas literature it seems that they highly recommend a digital phase converter for their machines. I just didn't want them to be able to blame any problems on weak/bad power. My other issue is the heat from a rotary phase converter. I have a small space and even the small rotary I have now puts out an awful lot of heat.

You had to have the elctric company put in the new 400 Amp service though, right?

My issue with the compressor is my neighbors. I will work almost exclusively at night. I don't think they'll appreciate the noise from the piston compressor.
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 07-28-2009, 05:43 PM
l u k e's Avatar  
Join Date: Apr 2005
Location: USA
Posts: 764
l u k e is on a distinguished road

Originally Posted by Matt@RFR View Post
If I were you, I'd look in to having your power company set you up with 3 phase.
I checked into that myself. They (APS) have 3 phase power 25 feet from my shop (for the place next door) they wanted $10,000.00 (yes 10K) to supply me 3 phase power!

That's BS!
Tweet this Post!Share on Facebook
Reply With Quote

  #9   Ban this user!
Old 07-29-2009, 01:17 AM
 
Join Date: Apr 2005
Location: Paradise, Ca, USA
Age: 34
Posts: 513
Matt@RFR is on a distinguished road

It is rediculous, I agree there. But if the choice is $10k for 3 phase or $6200for a phase converter, get the three phase!

I will say though, that the Haas tech that set my mill up commented on how good my power is through my phase converter...and it's not digital. I'd just rather do without the heat and noise.
Tweet this Post!Share on Facebook
Reply With Quote

  #10   Ban this user!
Old 07-29-2009, 02:35 AM
 
Join Date: Apr 2009
Location: USA
Posts: 24
123tool is on a distinguished road

I just had a TM-1P and a SL-10 delivered last week, the SL-10 sat at the riggers for months waiting for the mill. I'm in a home shop and plan to use the PT-355 to power both... hopefully at the same time. If the machines aren't under full load how much power could they draw, the hp is always rated higher.

Travis, it all depends on your business, prototypes or production and how much to you plan to run. If your business is going strong then go big, if your just starting take it one step at a time. Let us know what you decide.

Doug
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 07-29-2009, 12:47 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,419
Geof will become famous soon enough

Before comitting yourself to a compressor look around and see if you can find one that keeps the motor running and cycles the air end on and off when the set pressure is reached.

I am pretty sure the Chicago Pneumatic unit turns the motor off and when it restarts you get a big starting surge which could pull your voltage down low enough to trigger an alarm on the CNC machines. However if you have this motor running constantly it enhances the quality of the power from the phase converter and acts as a bit of reserve power when these machines start.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Tweet this Post!Share on Facebook
Reply With Quote

  #12   Ban this user!
Old 07-29-2009, 08:33 PM
 
Join Date: Oct 2006
Location: USA
Posts: 205
123CNC is on a distinguished road
Neighbors and Compressors

Geoff makes a good point about the load/unload of the compressor motor.

Regarding noise and neighbors, rotary screws are much quietier then reciprocating, but you may also want to consider scroll compressors. They are inherently quiet and can be quite efficient if you get a multiple compressor unit that is staged to run based on demand.
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
wtb: 20 or 30 hp phase perfect phase converter gaugemate Want To Buy...Need help! 0 10-23-2008 01:06 PM
phase converter rob jerico Fadal 13 09-02-2007 01:32 AM
HELP rotary converter for air compressor gman1487 General Electronics Discussion 0 06-04-2007 12:22 AM
DIY phase converter? wyobmf Phase Converters and VFD 9 07-26-2006 05:37 PM
RF from phase converter ? DieGuy Phase Converters and VFD 1 10-20-2005 08:14 AM




All times are GMT -5. The time now is 07:32 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353