Question adding external limit switches

i've been given the task to add a limit switch to both pallets of my HS2-RP ( HMC ) that will check to make sure the parts are clamped before the pallet changes.

I have plenty of unused and spare variables in my deiscrete inputs 2
and know how to write the macro make the check for the switch, but i dont know how to wire the switch in, and cannot find anything in the manual on it.

Any ideas on how to wire it in would be a great help.
Tweet this Post!Share on Facebook
Reply With Quote

  #2   Ban this user!
Old 06-20-2008, 10:50 PM
automizer's Avatar  
Join Date: Dec 2005
Location: Canada
Age: 27
Posts: 438
automizer is on a distinguished road

I have found that as well. I am trying to wire in to my extra M functions and its so hard to get info about it. I asked a Haas Tech. at out local Haas Demo Day this week, and got some info I needed but not all. Try calling your HFO and see what you can get out of them.
__________________
I'm not lazy..., I'm efficient!
HAAS GR-408
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 06-21-2008, 07:09 AM
serviceman's Avatar  
Join Date: Apr 2007
Location: usa
Posts: 178
serviceman is on a distinguished road

on the left side of the io board most of the small connectors are inputs what you have is a sinking logic, basically you have to take a ground wire and short it to one of the inputs and you should see the diagnostic change from say one to zero the input address can be found out by using the diagnostic page the input addresses i believe start with 1000 on the diag page the top left bit would be 0 and 1 would be next going down so say #1000 would be tool changer in and #1001 would be tool changer out there are more inputs and the second page but i cannot remember what number they start with. there is more info in the service manuals. you may also be able to use he m-fin. you can basically wire as many inputs as you want to the m fin in parallel and check for the m fin before doing to the next line. so if the pallet comes down and the switch changes state the pallet clamped. if m fin does not cycle then alarm. good luck
__________________
REYTECH Machine Service Corp. CNC repair NY, NJ
http://www.reytechmachine.com
Tweet this Post!Share on Facebook
Reply With Quote

  #4   Ban this user!
Old 06-21-2008, 09:37 AM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,419
Geof will become famous soon enough

Go to the Mill Manual pdf on the Haas website, here is a link, search the pdf using M-FIN or user M function and you will find some description of what serviceman is referring to. Also go through the Haas Mills forum and you will find some threads about these, I posted some pictures of the location of the contacts in one of them.



http://www.haascnc.com/customer_serv...mc/96-8000.pdf
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 06-23-2008, 09:59 AM
 
Join Date: Nov 2006
Location: america
Posts: 46
hydrospin01 is on a distinguished road

I thought of using the M-fin function but decided not to when i relized my machine only has one M-fin input. since i have to pallets i need to monitor the switches seperatly other wise one pallet could be un-clamped the other one clamped and the m-fin function would would find this exceptable. I tried calling my local HFO, they told me that they would have to check with the factory because what i want to do may be considered altering safety and they dont want to be liable if anything goes wrong.
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 06-23-2008, 10:04 AM
 
Join Date: Nov 2006
Location: america
Posts: 46
hydrospin01 is on a distinguished road

Originally Posted by serviceman View Post
on the left side of the io board most of the small connectors are inputs what you have is a sinking logic, basically you have to take a ground wire and short it to one of the inputs and you should see the diagnostic change from say one to zero
Thank you sir
i think your on to what im looking for, im going to have to dig into my machine and give that a try
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 06-23-2008, 10:32 AM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,419
Geof will become famous soon enough

Here is a (possible?) way to do it using the M-FIN and three of the User M functions.

Wire the M-FIN through a relay that is operated by the User M with the circuit going through a switch on the pallet.

The test sequence would be to program the User M then the M-FIN to test for the relay closure. If the pallet switch is open the relay stays open and the machine stops at the M-FIN. If the pallet switch is closed the machine continues and you cancel the User M.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 06-23-2008, 08:53 PM
serviceman's Avatar  
Join Date: Apr 2007
Location: usa
Posts: 178
serviceman is on a distinguished road

i have set up a midaco 4 pallet system 2 on either side of the machine it depends what io board you have to know what the input addresses are the inputs for the pallets are already there. there are pin clear and pallet home inputs and there are plenty because haas uses a quad changer. i wired the midaco switches into the existing haas inputs and it did go very well. and it made sense in the end since we were using inputs that were already labelled for pallet changers look at your diagnostics and watch them change and find the connector for the inputs for the pallets it's pretty simple. once you have them the address is simple to figure out
good luck
__________________
REYTECH Machine Service Corp. CNC repair NY, NJ
http://www.reytechmachine.com
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Limit switches BobF General Electronics Discussion 8 06-15-2008 07:31 PM
Limit switches and homing switches AeroKam Open Source CNC Machine Designs 16 01-05-2008 08:56 AM
The relationship of limit switches to home switches. MikeAber General Electronics Discussion 4 11-04-2004 02:28 PM
Limit switches and home switches viktorcnc TurboCNC 2 08-03-2004 07:11 AM
Home switches and limit switches. ynneb General Electronics Discussion 5 04-08-2004 06:32 PM




All times are GMT -5. The time now is 04:09 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353