The Power Failure Detection Module is not just an isolation transformer. I had to get one installed on my gantry machine becasue the spindle would drop about 0.1 when the power was cut. The explanation below is more or less what the Hass tech told me.
On the Haas vertical spindle machines the Z axis does not have a counterweight in normal use when the servos are powered the weight of the axis sits on the servo; this is why the Z servo always shows a load that varies from around 25-30% for the MiniMills up to almost 60% for the gantry machines with the extended Z axis.
When the power to the servos is turned off a magnetic brake on the end of the servo motor locks down and holds the load. The brake is electrically released and power to release the brake must be turned off a miniscule time earlier than the power to the servoes so that brake is fully engaged before the servo stops supporting the load.
When E stop is hit to turn off the servo power the brake takes the load correctly before the servoes go off because all the power supplies are still producing power. However, when the power off button is pushed or when there is a power failure or blip down in the incoming power all the power supplies go down at the same time. Because there is some lag in the brake acting, when all the power goes down at the same time the Z axis screw can rotate a little before the brake locks down.
The Power Failure Detection Module monitors the incoming power and when it drops this module acts to keep the servo power up while the brake locks; or it kills the brake power immediately before the servoes go down. I don't know the exact operation but it is acting something like the E stop sequence.