Thread: Aluminum wire for connecting machines

  1. #1
    Registered
    Join Date
    Jul 2005
    Location
    Canada
    Posts
    11,960
    Downloads
    0
    Uploads
    0

    Aluminum wire for connecting machines

    Any reason to not use aluminum wire for the incoming line to the machine? Correctly installed with the goop the electricians put on the connection of course.

    I am moving 26 machines to a new location and the cost saving using aluminum instead of copper for the new wiring is a reasonable sum of money.
    An open mind is a virtue...so long as all the common sense has not leaked out.


  2. #2
    Registered
    Join Date
    Oct 2005
    Location
    United States
    Posts
    21
    Downloads
    0
    Uploads
    0
    Use of the goop keeps the aluminum wiring from oxidizing and creating a high resistance connection. The problem with using aluminum wire for equipment with a high current draw is that it still gets warm, expands, deforms slightly due to its' plasticity at elevated temperature, then keeps that shape when it cools. It is now ever so slightly looser a connection than before. Over time, the connection gets looser and looser and eventually becomes a high resistance connection, and a fire hazard. If you must use aluminum wire to connect your machines, protect yourself by re-tightening all connections on a regular basis, and get someone in to do an IR scan of your connections to make sure none of them are running at a higher temperature than they should, because a connection running at an elevated temperature won't be visible until it starts to burn the insulation off the wire.


  3. #3
    Registered
    Join Date
    Apr 2005
    Location
    Paradise, Ca, USA
    Posts
    623
    Downloads
    0
    Uploads
    0
    My VF-2ss is hooked up with aluminum wire and has been just fine since '07. I don't use mine as much as you use your machines, but the connections have never loosened up at all. I check them roughly once every 6 months.


  4. #4
    Registered
    Join Date
    Jan 2007
    Location
    USA
    Posts
    1,378
    Downloads
    0
    Uploads
    0
    alum will work fine for a smaller haas they run 5 ton a/c units all the time in AZ on them and they run on and off for ever.
    we had 2 hardinge ahc'c and a omniturn running in our garage with alum wire back in 92 ( not because it was cheap but thats teh way the garage was wired)they ran bar feed work and anyone that knows hardinge ahcs know they draw tons of power. so I would say you would be fine. and the goop is needed.
    only thing with alum is get into the habit of check tighness alot during the 1st 3 months then every 6months- a year after that.


  • #5
    Registered
    Join Date
    Jun 2007
    Location
    Canada
    Posts
    67
    Downloads
    0
    Uploads
    0
    The savings will be great but will it be to code?
    What about your insurance?


  • #6
    Registered
    Join Date
    Jul 2005
    Location
    Canada
    Posts
    11,960
    Downloads
    0
    Uploads
    0
    ....protect yourself by re-tightening all connections on a regular basis,...

    ...I check them roughly once every 6 months...

    ...check tighness alot during the 1st 3 months then every 6months- a year after that...

    Everybody seems to be singing the same tune; which is a deal killer.

    When I do the calculation to amortize the initial saving over the nuisance value of having to get into the back of the machines on a regular basis over the years it is not worth it.
    An open mind is a virtue...so long as all the common sense has not leaked out.


  • #7
    Registered Machineit's Avatar
    Join Date
    Mar 2010
    Location
    USA
    Posts
    1,010
    Downloads
    0
    Uploads
    0
    You might look at the copper as an investment! It will probably be worth much more in the future.
    Haas VF-2, HA5C, Hardinge CHNC 1, BobCAD V23


  • #8
    Registered
    Join Date
    Jan 2005
    Location
    USA
    Posts
    2,920
    Downloads
    0
    Uploads
    0
    Geof

    Could you not take most/some of the wire from your old shop & reuse it were you can
    Mactec54


  • #9
    Registered
    Join Date
    Jul 2005
    Location
    Canada
    Posts
    11,960
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by mactec54 View Post
    Geof

    Could you not take most/some of the wire from your old shop & reuse it were you can
    We will but not much will be useful. In the old shop the transformer and distribution panel were about in the middle of the machines. In the new shop they are on a wall at one end so most of the wire runs are a lot longer. The transformer is also mounted high up so we get back all the floor space that used to be lost to the clearance code requires in front of the panel. It is a case of gain some lose some; we gain floor space at the cost of new wiring.
    An open mind is a virtue...so long as all the common sense has not leaked out.


  • #10
    Registered
    Join Date
    Jan 2007
    Location
    USA
    Posts
    1,378
    Downloads
    0
    Uploads
    0
    Geof
    My experance with the alum wire is in a/c on residential and in 120 degree heat that goes down to 30 degrees in the winter time. in a shop it may not work the same as a wont fluctuate 70º
    the only place I had to check/tighten the wire is 90% at the main fuse box thats outside on the east and west walls.

    hope that helps
    Delw


  • #11
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    I am not a particular lover of aluminum wiring, you are supposed to clean any trace of (invisible) oxide off before applying the inhibitor, also you should only be using aluminum or aluminum/copper compatible connection points.
    If yours are copper only rated, you may have problems.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #12
    Registered
    Join Date
    Jul 2005
    Location
    Canada
    Posts
    11,960
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by Al_The_Man View Post
    ....If yours are copper only rated, you may have problems.
    Al.
    I won't have problems, I am going to be conservative and go with copper. The cost difference is only four 'latte factors'. A latte factor is my annual expense at Starbucks buying lattes, steamed milks, chai teas, what-have-you for me and others.
    An open mind is a virtue...so long as all the common sense has not leaked out.


  • Page 1 of 2 12 LastLast

    Similar Threads

    1. Replies: 1
      Last Post: 04-28-2013, 10:12 PM
    2. Replies: 0
      Last Post: 07-13-2011, 09:50 AM
    3. Replies: 0
      Last Post: 12-21-2010, 10:05 AM
    4. Connecting bipolar motors without knowing which wire is which?
      By Witsenburg in forum Stepper Motors and Drives
      Replies: 1
      Last Post: 05-12-2007, 11:29 AM
    5. connecting to machines
      By watzmann in forum CNCzone Club House
      Replies: 2
      Last Post: 06-20-2006, 07:37 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.