    Question Help - Get interference from Plasma on my PC

    Hi, I'm new to CNC Plasma cutting and need some help.

    I've build a 3-axis CNC machine to run a router on it and it worked very well.
    A while ago I decided to put a plasma cutter on it. I'm using a Thermadyne Inverter type with high-frequency arc start.

    The problem is, as soon as I "trigger" the plasma arc my computer pickup interference and either hangup or start with alarm beep and lose control of most functions.

    I've tried to isolate the cutting table from the gantry but it doesn't help. Even with the plasma cutter removed from the cnc machine and positioned 10' from the computer the problem remain the same.

    I assume the problem is the high-frequency arc, if so, how can I get arround this problem?


  2. #2
    Moderator HuFlungDung's Avatar
    Join Date
    Mar 2003
    Location
    Canada
    Posts
    4,826
    Downloads
    0
    Uploads
    0
    I've had a little experience with a plasma causing one of my PC's to reboot. I'd say that the motherboard had a design weakness that made it susceptible to the RF noise.

    Best to try a different PC. Before you actually go to all the work of changing over the PC in your control, you can just set up the prospective PC near the same location, and fire up the plasma and see how the PC reacts.

    Run the PC through a battery backup type UPS (surge protector). You should already be doing this.
    First you get good, then you get fast. Then grouchiness sets in.

    (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)


  3. #3
    Registered
    Join Date
    Jul 2005
    Location
    USA
    Posts
    1,952
    Downloads
    0
    Uploads
    0
    Grounding for noise and grounding for AC safety are two different topics. The HF noise from older plasma cutters is a real problem. If it reboots you computer it most likely will cause problems in the motion control electronics.

    Make sure your computer is not grounded locally to the table or the plasma side.

    It's ground needs to be from another source. Depending on the motor drives, power supply and control electronics you may not have the option to run a two ground system in which case you may have to put your PC inside a metal enclosure not connected to the table. We have several customers running MACH on a PC with our Digital THC with old HF start plasmas but they had to go to extreme grounding techniques to make it work.

    TOm Caudle
    www.CandCNC.com


  4. #4
    Registered
    Join Date
    Sep 2007
    Location
    South Africa
    Posts
    3
    Downloads
    0
    Uploads
    0

    Thumbs up HF Iterference

    After some testing, it seems that "extreme grounding" should solve my problems.

    Thanks for advice and info.


  • #5
    Registered
    Join Date
    Jan 2007
    Location
    CA
    Posts
    233
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by nicjac View Post
    After some testing, it seems that "extreme grounding" should solve my problems.

    Thanks for advice and info.

    In the wonderful world of plasma, there is no such thing as "extreme grounding"


  • #6
    Registered
    Join Date
    Oct 2006
    Location
    canada
    Posts
    37
    Downloads
    0
    Uploads
    0
    Very common problem with HF plasma systems. The first thing you should do is go to a plasma manufacturers web site, such as Hypertherm or Thermadyne and research the proper grounding techniques for providing a proper ground for plasma. One thing to remember is that just because a ground rod is driven into the ground, does not mean that it is 'connected' to earth ground. This is usualy the most common fault of plasma interfernce. People think that their ground rod is making earth ground just because it is in the ground.
    Once a good earth ground is established, follow the plasma manufacturers recommebdation for grounding the plasma and the table.


  • #7
    Registered
    Join Date
    Oct 2007
    Location
    USA
    Posts
    125
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by nicjac View Post
    After some testing, it seems that "extreme grounding" should solve my problems.

    Thanks for advice and info.
    NicJac, If I may ask, what did you end up doing to solve your HF interference problem? I have a problem with an ESAB PCM 1125 hf start, it's interfering with the MP1000thc from CandCNC.
    --Mike


  • #8
    Registered
    Join Date
    Sep 2007
    Location
    South Africa
    Posts
    3
    Downloads
    0
    Uploads
    0
    First thing was to isolate the cutting bed from the rest of the machine, either on rubber or other isolating material or by having the cutting bed as a loose table not connected to the machine.

    Equip the cutting bed or loose table with an earth cable connected to it's own earth-spike.

    The last thing I did was to use USB mouse & keyboard, the PS2 mouse and keyboard seems to be more acceptable to interference than their USB cousins.

    I still get a 1-step "jump" each time the plasma arc start, but through the speed reducer 1 step on my stepper motor is only a fraction of a millimeter and does not bother me.

    I hope this will help you.


  • #9
    Registered
    Join Date
    Jan 2008
    Location
    USA
    Posts
    1,861
    Downloads
    0
    Uploads
    0
    Most RF (high frequency) noise issues can be solved with by making the following changes:

    1. The electrical noise is generated by the high frequency circuit (as much as 15,000 volts at 2 mhz) in the plasma.....and the high frequency travels through the torch leads (20' or more) to the torch. Consider this the antenna that is transmitting the RF noise.

    On industrial systems the torch leads have a tinned copper braid that covers the leads...and is connected to the plasma system chassis on one end....and not connected on the other end. This shieded torch leads packeage is then isolated from all other wires and cables on the machine....either by running it through a plastic powertrack by itself....or by hanging it from an overhead boom. If there is excess length....do not coil it...rather, keep it layed out straight.

    You may be able to simply isolate the torch leads without shielding them....try rerouting them temporarily by hanging them from the ceiling...and keeping them away from other cables as much as possible. Try cutting with the machine....if this solves the problem than you now know where the noise is coming from...and you can work to isolate it.

    2. Grounding. A copper coated steel, 8' length ground rod should be driven as close as possible to the cutting machine. Short lengths of heavy gauge stranded cable (flat braided wire is actually best as high frequency travels on the outside of a conductor)...and this has the most surface area. The use of #12 single strand building wire is practically useless...use heavy gauge multistrand wire for grounding). Connect the cutting table to the ground rod...short wire. Connect the chassis of the plasma directly to the ground rod...sort wire. Connect the gantry (moving parts, both x and y axis) to the ground rod....short as possible wire. Do not "daisy chain the grounding...every compponent needs to be connected to a "star" ground directly at the ground rod. This will probably help.

    Jim Colt Hypertherm


  • #10
    Registered
    Join Date
    Oct 2007
    Location
    USA
    Posts
    125
    Downloads
    0
    Uploads
    0
    Thanks nicjac, I cannot isolate the cutting bed on my machine because it's all an integral table, but I'm working on it today.

    Jim, What about the plasma chassis ground that connects to bldg. ground? The ESAB unit has the power cord ground attached to the unit chassis inside, so if I run another ground to the star point on the table, (or directly to the 8' rod then it will be grounded both through bldg ground and my plasma table earth ground?

    Thanks for the input guys!


  • #11
    Registered
    Join Date
    Jan 2008
    Location
    USA
    Posts
    1,861
    Downloads
    0
    Uploads
    0
    The chassis ground that goes to electrical ground can create a "ground loop"....which can be problematic for noise......but safety concerns must overide that. I would suggest leaving the electrical ground as it is....but still ground the chassis to the ground rod. Ideally the plasma power supply should be very close to the ground rod.

    The goal is to get stray RF to follow a path of least resistance (large surface area conductors) directly to the ground rod. If there is any daisy chaining....it won't be direct!

    I have seen many sites over the years with noise issues (on big industrial machines) that had an overly complicated grounding system.....by simplifying it we were often able to eliminate the problem. Isolating the torch leads is the #1 best cure!

    We run high frequency plasma cnc machines at every trade show....with absolutely nothing but the electrical ground....with no problems whatsoever. We do pay special attention to routing of all leads and cables on these machines. Motor and encoder cables are low voltage, and the RF from the high frequency loves to inductively couple to these cable....wreaking havoc with the computer.

    Many of the newest industrial machines today use sercos drives all linked with fiber optics. noise problems eliminated!

    Jim Colt


  • #12
    Registered
    Join Date
    Jan 2008
    Location
    USA
    Posts
    1,861
    Downloads
    0
    Uploads
    0
    One other comment.....I would not attempt to isolate the table from the rest of the machine.....could be dangerous. All metal surfaces need to be at the same potential as the ground rod. Plasma systems can have open circuit voltages of 400 vdc.....if the table was isolated...and some sort of electrical failure ocurred within the plasma system...you could have some lethal voltages present.

    jim colt


  • Page 1 of 2 12 LastLast

    Similar Threads

    1. Offset Interference Alarm?
      By xqqqqme in forum Mazak, Mitsubishi, Mazatrol
      Replies: 4
      Last Post: 07-06-2008, 01:52 PM
    2. interference from plasma cable
      By calthaus in forum General Waterjet
      Replies: 3
      Last Post: 04-18-2007, 12:33 PM
    3. Hf Interference
      By Alex S.A in forum General Waterjet
      Replies: 2
      Last Post: 02-11-2007, 07:05 PM
    4. Electrical Interference
      By Scratch in forum General Waterjet
      Replies: 0
      Last Post: 01-13-2007, 11:49 AM
    5. Component / Computer Interference?
      By Harlow in forum General Electronics Discussion
      Replies: 4
      Last Post: 12-13-2004, 01:19 AM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.