    Electricity isolated from power-grid?

    Hi


    I am thinking about building and experimenting with EDM. I am conserned about power shocks damaging wires in walls, appliances and electricity meter, so i thought i could totaly isolate power for edm:
    using two drilling machines connected by shaft: one runing from power-grid and other being off grid and "PRODUCING" electricity for EDM?
    Is this feasible?
    Will power shocks destroy such dynamo, will brushes burn off?

    thanks for any advices


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    19112
    Downloads
    0
    Uploads
    0
    A transformer provides isolation, fuses and breakers protect from over-current.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered
    Join Date
    Mar 2006
    Location
    USA
    Posts
    17
    Downloads
    0
    Uploads
    0
    A transformer provides isolation only to a limited degree. You can and will still transmit spikes, sags, weird harmonisc etc through most transformers. The device you are refering to is a simple version of an MG set (or motor generator set) This will prvide complete electrical isolation from the line as the only connection betwene your input and output is mechanical. The company I work Manufactures transformers, MG sets and many other power conditioning and conversion equipment on a larger scale. You can read more about the benifets of MG sets at: http://www.3phasepower.org/3phasefre...converters.htm

    There's alott of information there. Good luck


  4. #4
    Registered
    Join Date
    Mar 2006
    Location
    USA
    Posts
    17
    Downloads
    0
    Uploads
    0
    Note: The page I linked to refers to an MG set version for changing the frequency however, the gains on a unit which runs on the same power input and out still apply.