torroid transformer wiring

i recently purchased a really nice transformer from ebay, however, i'm just wanting to make sure i'm correct in my thoughts before i wire this for my power suppply.

This transformer is in ther neighborhood of 100ova i have the spec sheet here in front of me, but , like i sadi, I'm not an electrician, so i need a little advice.
It shows to sets of primary leads and secondary leads. However they are all sharing a ground ( 3 wires on each tap)

I'm wanting to use one secondary tap, which states it is @29v ac and @19 amp. This is all i need, but i have an idea later to use the other tap for another machine.

My question is about this third wire in each bundle. I'm thinking on the primary side that i can wire the two coils together with the two 110 and just use the two grounds to get my 110 on both coils, but i guess it's not necessay if i only use one coil and secondary tap for now.

Can someone tell me if i'm even in the ballpark of what is correct.
Also, can someone tell me the different combinations of currents i can achieve with this . The gentleman that sold it to me said i could wire both secondary taps in series to acchieve 2-54vac taps, i don't see that possible becasue it's only a 1000va. I only need 1-29 volt 19 amp tap for now, but would like to know if i'll have the same on the other for later on for another machine.

PLEASE SEE THE ATTACHED SHCEMATIC!
Thanks in advance
Mark
Attached Thumbnails
Click image for larger version

Name:	torroid.jpg‎
Views:	134
Size:	72.7 KB
ID:	74444  
Tweet this Post!Share on Facebook
Reply With Quote

  #2  
Old 01-25-2009, 03:10 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

If I read the print right, a bit faint in places, the primary has two separate windings 0-100-120v?
If so you could either wire them in series for 240vac input or parallel them for 120v, make sure you use the same wire numbers for each connection, otherwise it will be out of phase, obviously do not connect the 100v wires when hooking up for 120v..
The secondaries appear to be two 27-0-27 or 54v centre tapped.
You can use this one of two ways for 27vac, either put a full wave bridge from a 0 cenre tap to one 27v out.
Or use the centre tap as common and put one Rectifier in each of the 27v sides for one set of windings, this is full-wave centre tap arrangement.
Any parallelling of windings must use the same numbered wire to connect together.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 01-25-2009, 03:22 PM
 
Join Date: Apr 2007
Location: usa
Posts: 84
m8kingit is on a distinguished road

Originally Posted by Al_The_Man View Post
If I read the print right, a bit faint in places, the primary has two separate windings 0-100-120v?
If so you could either wire them in series for 240vac input or parallel them for 120v, make sure you use the same wire numbers for each connection, otherwise it will be out of phase, obviously do not connect the 100v wires when hooking up for 120v..
The secondaries appear to be two 27-0-27 or 54v centre tapped.
You can use this one of two ways for 27vac, either put a full wave bridge from a 0 cenre tap to one 27v out.
Or use the centre tap as common and put one Rectifier in each of the 27v sides for one set of windings, this is full-wave centre tap arrangement.
Any parallelling of windings must use the same numbered wire to connect together.
Al.

Al, is it necessary to paralell the two 120 along with the 2 center taps on the primary side. to get 120 input for both coils?

if i'm only wanting 120v input, do I just cap the 100v input wires?

When you say keep the wires in sequence do you mean as in from top to bottom as they read on the schematic?

Also, if i chose not paralell the secondary side, will i have two separte taps at 27 volts and 19 amps if i only connect each to a rectifier and a center tap?
Tweet this Post!Share on Facebook
Reply With Quote

  #4   Ban this user!
Old 01-25-2009, 03:34 PM
 
Join Date: Jul 2008
Location: UK
Age: 53
Posts: 411
irving2008 is on a distinguished road

If you zoom it to 500% you can read it OK...

The primaries are indeed 0-100-120
The secondaries are 27.2V onload. 29v off load

The small print at the bottom says 'Calculated temperature rise at 1240VA cont load: 80degC'

Wire as follows for 120V primary:
Black + White (0v)
Brown + Grey (120V)
Isolate blue and orange wires

I think there's some mistake in the datasheet or this is more than 1240VA... not all secondaries can be 27.2 @19A simultaneously. I think the 19A refers to the whole secondary when used as a 1/2 bridge configuration

so thats 2 x 27v @ 19A with a bit to spare.

[edit]seems a quick google shows these transformers are well liked by the DIY audio crowd and they are indeed spec'd as above[/edit]

Last edited by irving2008; 01-25-2009 at 03:55 PM.
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 01-25-2009, 06:19 PM
 
Join Date: Jul 2008
Location: UK
Age: 53
Posts: 411
irving2008 is on a distinguished road

Mark,

Following on from your PM...

This transformer is fine for your needs and the SB254 rectifier will do the job. You can certainly expect to get two 27v @ 12A out of it using those rectifiers and you may well go higher but you may find it doesnt get to 19A. this is because only 1/2 the winding is used over the full AC cycle so the average current density in the winding is higher and it may either get too hot or the magnetic core may saturate limiting the current output. I cant guarantee this will happen and it may be you can get close to 19A... just dont be surprised if you can't. It all depends on the way the windings are put on the core...

With a half-bridge each 1/2 of the winding is used on alternate half cycles so the average current density and core magnetic density is less.

As to the difference between full and half bridge, see the attached pic...

Incidentally you can still use the SB254 in the 1/2 bridge arrangement. The outer leg of the windings connect to the ~ inputs on the bridge but you only take the + output as your common output from the rectifier, the - side of the DC coming from the winding centre tap instead of the rectifier.
Attached Thumbnails
Click image for larger version

Name:	Slide1.GIF‎
Views:	89
Size:	7.5 KB
ID:	74462  
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 01-25-2009, 06:32 PM
jalessi's Avatar  
Join Date: Feb 2007
Location: U.S.A.
Posts: 3,099
jalessi is on a distinguished road
Smile Easy to read PDF for this transformer.

Mark,

Easy to read PDF for this transformer.

Jeff...
Attached Files
File Type: pdf TT.pdf‎ (165.5 KB, 98 views)
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 01-26-2009, 02:40 AM
 
Join Date: Jul 2008
Location: UK
Age: 53
Posts: 411
irving2008 is on a distinguished road
Toroidal transformer - 1/2 bridge

Mark,

See attached as to how to use the SB254 full-bridge as a half bridge. This will work fine.

I may be teaching grandmothers etc, but for safety I would insulate the - terminal of the bridge with a push-on connector and sleeve as it will be -80v relative to the + terminal and with the available current that would be potentially life threatening (50v is usually considered safe max). In any case you should never work on these sorts of voltages/currents when they are live and if you must (i.e. to measure volts), only with one hand at a time (and no jewellery/rings - I once saw someone burn their finger through when their ring shorted a 50v 100A buss in a phone exchange)

regards,
Irving...
Attached Thumbnails
Click image for larger version

Name:	Slide1.GIF‎
Views:	79
Size:	8.9 KB
ID:	74479  
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 01-26-2009, 12:07 PM
 
Join Date: Jul 2008
Location: UK
Age: 53
Posts: 411
irving2008 is on a distinguished road

Originally Posted by m8kingit
...i planned on using 33,000mfd caps for each tap, do you think that will be sufficient.

mark
I'll reply here Mark as your mailbox is full...

Capacitor in mFd = 80000 * I/V =80000*15/40= 30,000mFd for 0.1v ripple. or 10,000mFd for 0.3V ripple

You also need to consider inrush current... crudely:
C x V = I x t so:

I = C x V/t = .03(F) x 40 (v) / .016(s) = 75A (for 30,000mfd)

I = C x V/t = .01(F) x 40 (v) / .016(s) = 25A (for 10,000mfd)

SB254 good for 300A surge so no probs there but with 30,000mFd the primary current will be 20A surge against 5A running so need to fuse accordingly.

1% ripple is good enough so I'd probably go lower than 30,000mFd, but no lower than 10,000mFd
__________________
If you're in Europe why not come and visit the UK CNC Community at http://www.mycncuk.com
Tweet this Post!Share on Facebook
Reply With Quote

  #9  
Old 01-26-2009, 02:22 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

I generally design for 5% ripple, an increase in capacitance for lower ripple results in a higher transformer VA required at rated current.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #10   Ban this user!
Old 01-26-2009, 04:55 PM
 
Join Date: Apr 2007
Location: usa
Posts: 84
m8kingit is on a distinguished road

Originally Posted by Al_The_Man View Post
I generally design for 5% ripple, an increase in capacitance for lower ripple results in a higher transformer VA required at rated current.
Al.
okay, now I im into another dilema. Someone, please tell me what type of capacitance in going to work best here.
I'm using gecko 201's and 3 motors rated at 5 amps.
Thanks
mark
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11  
Old 01-26-2009, 05:12 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

The numbers I come up with for load of 15A at 40vdc and a 5% ripple at max load would be 25,000µfd the VA rating would be 534VA for 60% duty cycle.
I would go with at least 65vdc voltage rating for the capacitors.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #12   Ban this user!
Old 01-27-2009, 11:03 AM
 
Join Date: Apr 2007
Location: usa
Posts: 84
m8kingit is on a distinguished road

Al, do you think i will blow a 20 amp breaker from the power surge when i power up using your advice on 25000 mfd filter caps. Keep in mind that eventually, I'll want to use both taps at 40v 19 amp at the same time, also, should i use a resistor connected to the caps to bleed them down when powered off?
Thanks
Mark
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a dual-coil toroidal transformer... mzungu General Electronics Discussion 2 01-24-2008 08:23 AM
Transformer wiring question Bimmerkc1 General Electronics Discussion 3 01-13-2007 08:41 AM
wiring transformer/votage to high scheek General Electronics Discussion 12 10-19-2006 08:02 AM
Sola CVDC transformer wiring: Please Help Mini Miller General Electronics Discussion 7 12-01-2004 12:46 AM
Wiring diagram for single phase T-813 Transformer to VMC 4020 Fudd Fadal 11 03-07-2004 10:28 PM




All times are GMT -5. The time now is 03:53 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353