    Amperage Service Needed?

    Hi guys,

    I have been on here a few times posting, but since forgot my log in and email i used to register... don't you hate it when that happens.

    I run a small composites shop, but want to expand. I'm not sure when looking for a building what amperage service would meet my requirements. I understand 3 phase is just about necessary if not completely necessary.

    I would like to power a HAAS VF3 mill, HAAS SL30 lathe, and I will be adding an autoclave and possibly a 5 axis router, and of course a 5hp air compressor. The clave will be electrically heated, verses steam.

    How do i go about calculating how much electrical power service I need?
    I'd hate to move into a building only to find out there isn't enough power.

    Thanks


  2. #2
    Registered
    Join Date
    Feb 2009
    Location
    usa
    Posts
    4093
    Downloads
    0
    Uploads
    0
    For a VF3 3 phase would be mandatory. You simply need to find out what the FLA (full load amp) of each unit is, and add them together. I'm guessing the autoclave will require the most. You also might want to consider 480V for the autoclave and air compressor, then put transformers on the Haas. Might lower your electric bill by a bit.


  3. #3
    Registered lgalla's Avatar
    Join Date
    Jul 2006
    Location
    canada
    Posts
    1251
    Downloads
    0
    Uploads
    0

    service drop

    I agree with underthetire.480V/3ph is the way to go.You have not given enough information even to hazard a guess.An electric auto clave requires gobs of power even if small.Your compressor at 5Hp is small considering the machines you want to power
    Larry
    L GALILEO THE EPOXY SURFACE PLATE IS FLAT


  4. #4
    Registered
    Join Date
    May 2004
    Location
    United States
    Posts
    4519
    Downloads
    0
    Uploads
    0
    As stated, for a smaller operation, just add up all of the max demand like if you were to switch on every single piece of equipment in start mode at once. Usually it works better to get the kVa numbers then determine voltage and back into the ampere demand. If you will contact your electric supplier, they are generally happy to help you with the calculations, since they see it as a possible increase in their business.

    In a larger operation, an electrical engineer would make the calculations based off of peak average demand. In a smaller operation, it is much more difficult to calculate an average because your demand will swing wildly due to production changes. Better to just add them all up and go with that.
    http://www.kirkcon.com/


  • #5
    Registered
    Join Date
    May 2005
    Location
    USA
    Posts
    1442
    Downloads
    0
    Uploads
    0

    You already have good advice.

    The key is to add up the full load amps. However don't forget all the other facilities needs. This includes things like lights, heating and hot water.

    Also a 5 HP compressor might be on the small side if any of those machines consume air. So do the same thing and add up air consumption levels if any.

    Quote Originally Posted by cfcreations View Post
    Hi guys,

    I have been on here a few times posting, but since forgot my log in and email i used to register... don't you hate it when that happens.

    I run a small composites shop, but want to expand. I'm not sure when looking for a building what amperage service would meet my requirements. I understand 3 phase is just about necessary if not completely necessary.

    I would like to power a HAAS VF3 mill, HAAS SL30 lathe, and I will be adding an autoclave and possibly a 5 axis router, and of course a 5hp air compressor. The clave will be electrically heated, verses steam.

    How do i go about calculating how much electrical power service I need?
    I'd hate to move into a building only to find out there isn't enough power.

    Thanks


  • Similar Threads

    1. Mazak Service Tech Needed
      By easymoney in forum Want To Buy...Need help!
      Replies: 4
      Last Post: 03-29-2012, 08:04 PM
    2. Job Opening cnc service techs needed
      By BILL WRIGHT CCR in forum Employment Opportunity
      Replies: 0
      Last Post: 09-12-2010, 04:21 PM
    3. Service manual needed DWC200
      By tcforge in forum General Waterjet
      Replies: 2
      Last Post: 01-21-2009, 12:15 PM
    4. Cincinatti Arrow Service Needed
      By mlkaiser99 in forum Machine Problems, Solutions , Wireless DNC, serial port
      Replies: 0
      Last Post: 09-14-2007, 02:42 PM
    5. Northwest CNC service needed
      By divebo in forum Employment Opportunity
      Replies: 8
      Last Post: 03-30-2004, 08:12 AM

    Posting Permissions



    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.