    mitsubishi meldas control trips breaker

    i have a mitsubishi lathe with a meldas 300v control and when i turn the power on to it it trips a breaker immediatly in back, it is the CP1 Location. the wires coming out of the bottom of the breaker go to two power supplies or transformers? labeled AVR1 and AVR2, the wires are labeled L5 and L7, and i noticed two wires on the back door labeled the same and they go to the cooling fans on the door.


  2. #2
    Registered
    Join Date
    May 2005
    Location
    usa
    Posts
    56
    Downloads
    0
    Uploads
    0
    and also the machine wont come out of emergency stop, the control powers up, but nothing else works


  3. #3
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,925
    Downloads
    0
    Uploads
    0
    Do you have the schematics? If the breaker feeds several sources then it will be a process of elimination, hopefully using the schematic.
    Disconnect a breaker load one at a time until the breaker stays in, once the circuit is identified then further diagnosis can go from there, this procedure and a good multi-meter should do the trick. Most likely L5 & L7 are single phase 120v or 220vac.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  4. #4
    Registered
    Join Date
    May 2005
    Location
    usa
    Posts
    56
    Downloads
    0
    Uploads
    0
    i unhooked L7 and the breaker stayed on, L7 goes to each of the two tranformers to the right of the breaker, and there is a l7 wire on the bottom of a relay labeled CR1AP, i have a elementary diagram book that i am looking thru, should i look for the wire number or the relay number


  5. #5
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,925
    Downloads
    0
    Uploads
    0
    Either wire number or relay number will identify the circuit, The circuits and/or transformers should be disconnected one at a time. In other words you have to identify everything that is principally fed by L5 - L7, one of these circuits is providing the overload.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


Posting Permissions


 


About CNCzone.com

    We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

Follow us on

Facebook Dribbble RSS Feed


Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.