Electronics are not my fortay, so I have a simple question for you guys. I have one Hitach VFD running off 220V and a power supply + CPU both running off 110V; all in the same control box. I would like to run one 220V cable to the control box for simplicity. Would there be a way to convert the 220V to 110V inside the cabinet so I can power all the components from the same line? Thanks ahead of time, MRM |
|
#2
| |||
| |||
Just a thought - 220v might be 3-phase? same applies - need to run the transformer off one phase thats all..
__________________ If you're in Europe why not come and visit the UK CNC Community at http://www.mycncuk.com |
|
#3
| |||
| |||
The way that 110v volt is brought in your fuse panel is 2, 220v legs and a neutral. At least in American homes with single phase service. One leg and the neutral give 110v. If you are adding a lot of 110v devices inside the cabinet, try to split them between legs to balance the load on the 220v legs. If you are running the 220v line yourself, make sure you use a 3 wire cable with ground, this was you get leg, leg, and neutral. Red and black are the 220v legs and the white is the neutral. If you are unsure, ask a licensed electrician. Disclaimer, I am not an electrician but I play one on the CNCzone. Mike
__________________ Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out. |
|
#5
| ||||
| ||||
| The method Mike mentioned is used on electric ovens and clothes dryers to provide both 110V and 220V. You can get the wire at home depot.
__________________ Gerry Mach3 2010 Screenset http://home.comcast.net/~cncwoodworker/2010.html (Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management) |
| Sponsored Links |
|
#6
| |||
| |||
| Thanks for the backup Gerry. Always nice to know I got it right. Mike
__________________ Warning: DIY CNC may cause extreme hair loss due to you pulling your hair out. |
|
#7
| |||
| |||
| INteresting about the split supply, didnt realise that was the case in US. UK homes have a 240 single phase supply on 3 wires , Line, Neutral and Earth. This is one phase of the 3-phase 415v transmission and the balancing is done at the local substation across streets, or even within a block of flats (apartments). Domestic 3-phase is generally not available unless you are lucky enough to live in a warehouse conversion or similar.
__________________ If you're in Europe why not come and visit the UK CNC Community at http://www.mycncuk.com |
|
#8
| |||
| |||
The chassis of your unit needs to be tied to safety ground (earth ground at the breaker box). Neutral is supposed to be bonded to earth ground at the main breaker but NEVER tie neutral to the chassis of connected electronics. If the neutral ground has been compromised the voltage between neutral and a real earth ground could cause a nasty shock. \ TOM Caudle www.CandCNC.com |
|
#9
| ||||
| ||||
| The 120/240 in N.A. is still single phase power, not two phase. In UK the ground and neutral were never connected at the incoming service point, in fact even if the service carried a ground, it could not be used as a system ground, a proper ground conductor had to be used (metal water supply etc) if this was not adequate an Earth Leakage trip had to be installed at the service entry. The neutral circuit was grounded at the service transformer star point ONLY. At least this was the case when I worked in the electrical industry in UK. In N.A. If fitting a 240v to 120v isolation transformer it is customary to set up a local grounded neutral as the original neutral/ground has been lost due to isolation. This is done by grounding one side of the secondary directly to chassis ground at the transformer and where the service ground enters the enclosure. Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. Last edited by Al_The_Man; 01-09-2010 at 10:31 AM. |
|
#10
| ||||
| ||||
| CNCZone rocks! |
| Sponsored Links |
|
#11
| |||
| |||
|
Ever looked at the waveform on a dual trace scope? It's two legs of 120VAC that are 180 deg out of phase. True, it's single phase going into the pole transformer in most residential locations, and the center tap of the secondary sets the neutral leg. The term two phase is not used (more commonly it's "split phase") probably because it's confusing, but electrically it's two phases of AC with neutral to ground as common. Any transformer can be designed to give opposite phases of AC out. I guess it's the term "phase" that makes it confusing. To me phase describes the waveform based on times (when) it crosses neutral (0 volts). In North America it crosses every 8ms. Phasing is relative. It's described in degrees of difference. (vector descriptions). Sorry, but I approach electricity as an engineer and I have to take into account the characteristics of the wave forms involved which includes the relative phase of more than one source to a common return. 3 phase has a different characteristic than single or two phase waveforms and cannot be generated/created from single phase with a transformer (sadly). TOM Caudle (Old burned-out EE ) |
|
#12
| ||||
| ||||
| I was always taught to use the terms to describe a centre tapped secondary of a single phase transformer as is described in Wikipedia
Al.
__________________ CNC, Mechatronics Integration and Machine Design. “Logic will get you from A to B. Imagination will take you everywhere.” Albert E. |
![]() |
| Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
| Thread Tools | Search this Thread |
| Display Modes | |
| |
Similar Threads | ||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Using USA 110V Equipment on Euro 220V Mains! | diarmaid | General Electronics Discussion | 120 | 01-18-2010 02:49 PM |
| fitting a 110v or 220v single phase spindle motor on a 3 phase machine | mwood3 | Benchtop Machines | 12 | 10-12-2009 09:53 PM |
| Need Help!- 220V europe to 120V US wiring | willy1067 | Laser Engraving & Cutting Machines | 35 | 02-24-2009 09:05 PM |
| Electronics cabinet | mcArch | General Electronics Discussion | 10 | 08-04-2008 10:02 PM |
| The wiring inside a control box... | MrWild | General Electronics Discussion | 2 | 06-02-2007 12:13 PM |