Question Voltage reduction

Hello all this is my first post so of course I have a question.

I have a LED being fed from a vfd controller, it is 120v and 6mA. The problem is my ssr is leaking at 62.2 volts and .062mA yes I have the formula and yes I can figure out what size resister to use (1003) at 4watts. thats not the problem , the problem is how do I make sure that once the relay fires
that I have not reduced the voltage so much that the light does not come on?????
Reply With Quote

  #2  
Old 08-26-2009, 12:30 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Explain a bit more what you are trying to do?
Where is the LED being fed from and why?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 08-26-2009, 12:38 PM
 
Join Date: Aug 2009
Location: USA
Posts: 9
ArlieD is on a distinguished road

I have a vfd with outputs for a fault light, this light comes on when the vfd is faulted , the led is slightly on all the time , I am trying to put the light out so to speak, but still be able to have it on at full voltage when/if the drive faults out. We seem to have a large number of brown outs here and the drive faults for undervoltage. I have installed a reset and an led the led will tell the operator that the drive is faulted and he can then reset it.
Reply With Quote

  #4  
Old 08-26-2009, 01:25 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

It sounds like you are taking a SSR off a high voltage output?
The majority of VFD's I have come across usually have a choice of N.O. or N.C. contact closure of the alarm output.
Some have low voltage open collector output, configurable.
This contact closure is the prefered way.
What make of VFD? is there an on line manual that shows where you are taking this output from?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 08-26-2009, 01:53 PM
 
Join Date: Aug 2009
Location: USA
Posts: 9
ArlieD is on a distinguished road

it is a A/B smc flex 150Ft08NBD I am taking the reset from terminal 15 configured to clear fault, the led comes from terminals 31 and 32 which is aux option # 3 and configured for "Fault" in its n/o state. I believe this is a low voltage open collecter output and it is configurable. it just leaks .... if it helps the light is a 800T-Qh10R 120 volts full voltage LED
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 08-26-2009, 01:56 PM
 
Join Date: Aug 2009
Location: USA
Posts: 9
ArlieD is on a distinguished road

unfortunatly my day is over I would really like to continue this but don't want to keep you hanging so I will check email at home if you reply other wise I thank you for y our time and I will check in the am.
Reply With Quote

  #7  
Old 08-26-2009, 02:01 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

If you are using a low voltage collector output, how are you using a 120v led?
I will see if I can look up the manual in the mean time.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8  
Old 08-26-2009, 02:42 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

If this is the correct unit
http://literature.rockwellautomation...m051_-en-p.pdf
This appears to be a soft starter?
The outputs on 31 32 look to be contact closure, so there should be no leakage.
You could confirm it with a meter on ohms range maybe.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #9   Ban this user!
Old 08-26-2009, 06:34 PM
 
Join Date: Oct 2008
Location: US
Posts: 115
bharbour is on a distinguished road

Originally Posted by ArlieD View Post
Hello all this is my first post so of course I have a question.

I have a LED being fed from a vfd controller, it is 120v and 6mA. The problem is my ssr is leaking at 62.2 volts and .062mA yes I have the formula and yes I can figure out what size resister to use (1003) at 4watts. thats not the problem , the problem is how do I make sure that once the relay fires
that I have not reduced the voltage so much that the light does not come on?????
Hi,
If I read your post correctly, you are switching a solid state relay from the VFD outputs and the solid state relay output is leaking a little.

That leakage is probably unavoidable - there is an RC snubber network in most AC output solid state relays that prevents noise triggered turn ons and the snubber leaks a little bit. Could you replace the LED on the relay output with an incandescent bulb that takes more current to light up?

BobH
Reply With Quote

  #10   Ban this user!
Old 08-26-2009, 07:44 PM
 
Join Date: Aug 2009
Location: USA
Posts: 9
ArlieD is on a distinguished road

Yes Al it is a soft start, and I am sure it should not leak but it does. On 31 I have 120v , on 32 is the wire to the lamp, the second terminal on the light is the N.

Bob ,

using a incandesant lamp is my last resort, all other lamps on this unit are led so am trying to keep them the same.

Thanks alot for all the help folks
Reply With Quote

Sponsored Links
  #11  
Old 08-26-2009, 08:33 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

The PDF definitely shows contact closure, are you sure the contacts are open in the non-alarm condition?
Measure the continuity 31 to 32 with a meter with no power to the unit and then when it is in operation, remove the power first.
BTW, are you using 120vAC or DC, if AC it should be a LED that is conditioned for AC use, you can exceed the reverse voltage rating if an ordinary LED with resistor.
In this case a series rectifier is needed.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 08-27-2009, 06:18 AM
 
Join Date: Aug 2009
Location: USA
Posts: 9
ArlieD is on a distinguished road

absolutly postive the contacts are open with no power.

The Led works as its supposed to when there is a fault it comes on at full power. When contacts are open there is still 62.2v across the terminals of the LED at .062mA so the light remains very dimley lit. I can size a resister to drain the voltage but want to be sure I am not reducing it by too much so that when the contacts close the light will still come on but that the residual voltage is gone and the led will be out.

The Led is rated for 120vac full voltage and yes I am using 120vac

Last edited by ArlieD; 08-27-2009 at 06:21 AM. Reason: more info
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need help with gear reduction IQChallenged Linear and Rotary Motion 21 04-15-2009 10:36 AM
Vibration reduction.. JerryFlyGuy Mechanical Calculations/Engineering Design 34 11-09-2008 08:33 AM
Help on Voltage Reduction Resistor foamcutter General Electronics Discussion 9 07-06-2008 08:19 PM
Help..Stuck at relay ext dc voltage missing but dc voltage OK ? Dirky Bridgeport and Hardinge Mills 24 11-27-2007 07:33 AM
2:1 or 3:1 reduction...I'm not sure? Bird_E General Metal Working Machines 5 08-18-2004 08:32 AM




All times are GMT -5. The time now is 04:50 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361