3 Phase Motor Wiring Trouble

I am having trouble wiring a 3 phase motor properly.

The motor is the type with different jumpers to connect to adapt it to different voltages. I have 208V 3-phase power.

Here is the wiring diagram that came with machine:


When I hooked it up for the 220V option, the motor seemed to be running way way faster than it should have and the high pitched whining noise coming from it just seemed unhealthy.

So, I hooked it up for the 440V option, and it seemed to work normally. However, when a serious load is put on the machine (well within the limits of what the machine is supposed to be capable of), the motor bogs down and doesn't have enough power.


I noticed the diagram shows a Delta (triangle) sign above the 440V option, and TWO Deltas above the 220V option. Does anybody know what these symbols mean and does it explain why the motor didn't run normally when jumpered for 220V?

Is there some special way I need to wire the motor up to get it to work properly?

Any help would be greatly appreciated. Thanks!
Reply With Quote

  #2  
Old 12-08-2008, 06:33 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Is this a 2 pole or 4 pole motor? it should say the rpm on the motor plate.
It should not be able to run any faster than it is capable of on 60hz, this is what decided the rpm, not the connection.
Hook it up to 220 the way the digram shows and check the off load current.
The symbols are star (wye) and delta for the triangle.
The 220 appears to be both delta windings in parallel.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 12-08-2008, 07:40 PM
 
Join Date: Mar 2007
Location: USA
Posts: 143
PhoenixMetal is on a distinguished road

Originally Posted by Al_The_Man View Post
Is this a 2 pole or 4 pole motor? it should say the rpm on the motor plate.
It should not be able to run any faster than it is capable of on 60hz, this is what decided the rpm, not the connection.
Hook it up to 220 the way the digram shows and check the off load current.
The symbols are star (wye) and delta for the triangle.
The 220 appears to be both delta windings in parallel.
Al.
Hi Al,

I'll check in the morning as to the 2 or 4 poles, run the current test that you reccommended and will get back to you.

By the way, when I said it was running way faster than normal, that statement was really based mostly on the sound it was making - so it is possible that it was still running its normal speed. The motor is running a hydraulic pump, so its not as if I was able to clearly view things moving faster or slower. However I really do think it was running way fast. But faster or not, the motor definitiely was not making happy noises when I had it jumpered for 220!

What does it mean to have the delta windings in parallel? Is this perhaps specifying a certain type of power supply that is different from what I have?
Reply With Quote

  #4  
Old 12-08-2008, 07:50 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

If the motor was connected to the hydraulic pump, it is most likely the whine you heard is from the pump.
The Delta in parallel connection is what appears to be the designated connection for 220.
Your voltage is the lowest of any of the designated connections, so anything but the correct connection is going to be underpowered.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 12-10-2008, 04:44 PM
 
Join Date: Mar 2007
Location: USA
Posts: 143
PhoenixMetal is on a distinguished road

Ok, I have checked the faceplate on the motor to determine whether it is a 2 or 4 pole motor, and unfortunately it doesn't say. However perhaps its model number (FC112MT/4) gives a clue (the 4) suggesting that it is a 4 pole motor.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-10-2008, 06:43 PM
 
Join Date: Mar 2008
Location: us
Posts: 90
rlabonte18 is on a distinguished road

2 pole will have an rpm around 3000 and a 4 pole will have an rpm around 1700. Yours is probably a 2 pole motor.
Reply With Quote

  #7  
Old 12-10-2008, 06:43 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Doesn't it mention rpm on the plate?
If the pump is connected and the current is within the FLA which hopefully it also mentions, then it should be OK.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 12-12-2008, 12:00 PM
 
Join Date: Mar 2007
Location: USA
Posts: 143
PhoenixMetal is on a distinguished road

Originally Posted by Al_The_Man View Post
Doesn't it mention rpm on the plate?
If the pump is connected and the current is within the FLA which hopefully it also mentions, then it should be OK.
Al.
The plate says 1704 RPM. I have found some literature online from the motor manufacturer and it looks like this is in fact a 4 pole motor.

OK, but now what does this tell you?
Reply With Quote

  #9  
Old 12-12-2008, 12:18 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by PhoenixMetal View Post
The plate says 1704 RPM. I have found some literature online from the motor manufacturer and it looks like this is in fact a 4 pole motor.
OK, but now what does this tell you?
The 1704rpm confirms it is a 4 pole motor.
I was just trying to get an idea of what rpm you should be getting.
You need to confirm the running current, that will tell you if you have the hook up wrong.
Hopefully the motor plate shows FLA's or the H.P. at least.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 12-12-2008, 12:29 PM
 
Join Date: Mar 2007
Location: USA
Posts: 143
PhoenixMetal is on a distinguished road

Hi Al,

The motor lists 4.8kw as its power.

I was going to do the current test that you requested, but then realized I have no idea how to do this on a 3 phase motor!

I can imagine how to do this on a normal AC or DC motor, with only 2 wires, but how do I do I measure current on a motor that has 3 leads?
Reply With Quote

Sponsored Links
  #11  
Old 12-12-2008, 01:36 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

That is around a 6HP motor so you most likely would draw ~18amps max. at full load on 220v.
The easiest way to measure the current is to borrow a clamp-on ammeter, this clamps over each conductor in turn, no contact is necessary with any conductor directly.
If you are running under 18amp on each conductor, you should be OK.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 12-12-2008, 02:49 PM
 
Join Date: Jul 2005
Location: USA
Posts: 100
jpgdesigns is on a distinguished road

Just a thought... you said this motor is running a hydraulic pump... some hydraulic pumps do not like to be run in reverse... so be sure of your rotation.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 3 (0 members and 3 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Can I convert single phase motor to three phase? Jim Estes Phase Converters and VFD 30 01-24-2009 02:41 AM
Wiring trouble Smackre General Electronics Discussion 25 06-23-2007 03:32 AM
help wiring 1 phase motor ezland00 General Electronics Discussion 7 05-15-2006 04:23 PM
Wiring a relay into my 3 phase motor Bass_Player General Electronics Discussion 6 05-24-2005 09:50 AM
4-phase motor and wiring questions DmitryZ General Electronics Discussion 10 04-13-2004 11:14 PM




All times are GMT -5. The time now is 04:35 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361