Needs some wiring help... please

Hi all,

I'm building a new controller and figured I'd get some expert advice before I blow something up.

If you'd be so kind as to take a look at the schematic and let me know if I have the wiring correct or if there's a better way of doing things.

Here's the parts I'm dealing with.

PARTS:
24V Xylotex power supply
Xylotex 4th axis driver board
Campbell design Combo board (with spindle relay)
two 110V receptacles
one 24V DC lamp
one e-stop switch with four NC contacts
one 110V power switch
one 10Amp fuse holder (not sure if I really need one of these)

Here's what I'm trying to accomplish.

1. I want to have one of the receptacle always powered up when I hit the main switch

2. The second receptacle will only be powered up via the onboard relay (controlled through Mach3)

3. When the E-stop is hit I want to kill power to the 24V DC line that feeds the Xylotex controller. It will also send a signal to the comboboard with will in turn drop the relay and cut 110VAC to the receptacle (Mach3 handles this)

4. When the E-stop is pressed it will also power off the 24V DC lamp

I believe that I have the E-stop shown wired correctly, it's mainly the AC stuff I'm not too sure about. Robert Campbell from Campbell Design told me how the E-stop and Relay works in conjunction with Mach3.

One concern I have is killing power to the 24V DC line that feeds to the Xylotex card. If I reset the E-stop; therfore, creating the 24V circuit, will this damage the card?

All bold lines are the AC lines (hopefully it makes sense).

Please forgive my ignorance, it's been a while since I've messed with circuitry and don't want to go more in debt if I wire things wrong.

I also left out the details on the board, if you need more info, please holler.

Thanks!
-Ed

Reply With Quote

  #2   Ban this user!
Old 02-07-2008, 06:40 AM
vger's Avatar  
Join Date: Jan 2006
Location: usa
Posts: 664
vger is on a distinguished road
Just one questionable

You have both L1 and L2 going to the combo board. Are you using 2 of the relays on the combo board to control the 110 outlet?
If not:

1. Disconnect the line from L2 to the combo board and connect it to the outlet's L2 side (if the outlet is a duplex with the jumper tabs still in place, L2 is already connected there).

2. Ensure L1 is connected to the COM terminal of the relay you are using (J16 if you are using the run relay).

3. Connect the NO relay contactof the relay (J16 if you are using the run realy) to the L1 side of the controlled outlet (if the outlet is a duplex, ensure the jumper tab on the L1 side is removed).

I'm assuming your EPO is a DPST normaly closed switch. Mushroom head pushbutton?
Everything else looks OK.
The users manual PDF that's online has several typo's in the J connector pinout area.
On the first page it says "J18-20 PCgnd"
(picture shows J18 and J19 as relay connections)

On the second page the relay connections show:

NC Normally closed correct
Com is the center terminal correct
NO Normally closed INCORRECT, should be "NO Normally Open"

I think they could use a new tech writer (or tech proof reader)

Best of luck

Steve
Reply With Quote

  #3   Ban this user!
Old 02-08-2008, 01:00 AM
nosplinters's Avatar  
Join Date: Jul 2006
Location: USA
Posts: 64
nosplinters is on a distinguished road

Hi Steve,

Thanks a lot for your input.

I'm a bit confused about the AC going to the combo board. I see on the combo board that J21 is a two terminal block that is labeled 115/220 on it.

Don't I need one of those with L1 and the other L2? I'm using the new Rev 5 Comboboard (if that matters).

My Run relay is labeled J17 with the following order

NO | RUN | NC


Is the RUN terminal what you're considering the COM terminal?

The two receptacles that I'm using are individual 15AMP 120V. They're the type that lock into a front panel, not like the standard house hold type outlet.

The e-stop is one of the big red mushroom types DPST (NC).

Please let me know your thoughts.

Thanks again!
-Ed
Reply With Quote

  #4   Ban this user!
Old 02-09-2008, 08:12 AM
vger's Avatar  
Join Date: Jan 2006
Location: usa
Posts: 664
vger is on a distinguished road
clarification

Yes, you will need L1 and L2 going to the combo board for it's power supply. And the jumpers installed to set the voltage for 110.

The run relay connections are only the contacts of the relay. There is no power available there. In order to switch L1 on and off to your spindle motor, you would need to wire the L1 coming from the main power switch to the COM (center connection) probably labeled "RUN" and wire the "NO" connector to the L1 side of your spindle motor outlet. The L2 side of the spindle motor outlet would go to the L2 wire (bold green in your drawing)

Hope that clarifies..

Steve
Reply With Quote

  #5   Ban this user!
Old 02-09-2008, 12:05 PM
nosplinters's Avatar  
Join Date: Jul 2006
Location: USA
Posts: 64
nosplinters is on a distinguished road

Hi Steve,

I updated the main circuit that I originally posted. You should see the changes to the schematic in my first post. I added the terminal numbers and cleaned things up a bit as well as the AC lamp that I was missing.

Am I closer now?

Thanks
-Ed
Reply With Quote

Sponsored Links
  #6  
Old 02-09-2008, 01:18 PM
ger21's Avatar
Community Moderator
 
Join Date: Mar 2003
Location: Shelby Twp, MI....USA
Posts: 20,455
ger21 is on a distinguished road
Buy me a Beer?

Originally Posted by nosplinters View Post
One concern I have is killing power to the 24V DC line that feeds to the Xylotex card. If I reset the E-stop; therfore, creating the 24V circuit, will this damage the card?
Someone recently asked this on the Xylotex support group. Xylotex said to cut the power to the power supply, don't cut the DC power. He didn't say if it would cause damage or not.
__________________
Gerry

Mach3 2010 Screenset
http://home.comcast.net/~cncwoodworker/2010.html

(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Reply With Quote

  #7   Ban this user!
Old 02-09-2008, 02:25 PM
nosplinters's Avatar  
Join Date: Jul 2006
Location: USA
Posts: 64
nosplinters is on a distinguished road

Hi Gerry,

Initially I was thinking about cutting the AC power; however, I didn't want to kill the secondary AC receptacle at the same time as well as having basically two power switches. I think what I might try first is to eliminate the second contacts on the EPO alltogether. When Mach3 and the combo board sense the open circuit the combo board will open the 110VAC Run relay; thereby killing power to the spindle receptacle. The killing of the 24V line was mainly as a precautionary step to make sure the steppers no longer move. I'm pretty confident the combo board will handle this.

Thanks
-Ed
Reply With Quote

  #8  
Old 02-09-2008, 02:59 PM
ger21's Avatar
Community Moderator
 
Join Date: Mar 2003
Location: Shelby Twp, MI....USA
Posts: 20,455
ger21 is on a distinguished road
Buy me a Beer?

Originally Posted by nosplinters View Post
The killing of the 24V line was mainly as a precautionary step to make sure the steppers no longer move. I'm pretty confident the combo board will handle this.

Thanks
-Ed
You could use the enable pins on the Xylotex.
__________________
Gerry

Mach3 2010 Screenset
http://home.comcast.net/~cncwoodworker/2010.html

(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Reply With Quote

  #9   Ban this user!
Old 02-11-2008, 04:05 AM
vger's Avatar  
Join Date: Jan 2006
Location: usa
Posts: 664
vger is on a distinguished road

Ed,

What you have there will work. However you are turning the spindle motor off and on by switching the L2 line (neutral). The L1 (hot) side of the line is always connected to the spindle motor outlet.

Here is the reccommended change

Steve
Attached Thumbnails
Click image for larger version

Name:	circuit[2].jpeg‎
Views:	109
Size:	83.5 KB
ID:	53019  
Reply With Quote

  #10   Ban this user!
Old 02-11-2008, 09:29 PM
nosplinters's Avatar  
Join Date: Jul 2006
Location: USA
Posts: 64
nosplinters is on a distinguished road

Good deal!

Thanks Steve.

Now I just need the rest of the parts and I'll be good to go.

-Ed
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 02-29-2008, 01:36 AM
nosplinters's Avatar  
Join Date: Jul 2006
Location: USA
Posts: 64
nosplinters is on a distinguished road

Hi all,

I thought I'd give you a peek at what the wiring was for.
So far no smoke.

Big thanks goes out to Steve for his wiring modification.

-Ed



Reply With Quote

  #12   Ban this user!
Old 02-29-2008, 06:00 AM
vger's Avatar  
Join Date: Jan 2006
Location: usa
Posts: 664
vger is on a distinguished road

Ed,

Very nice ! Always great to see it all come together.

Steve
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
G-REX wiring Lost Tourist G-REX 24 07-30-2008 05:15 PM
425 wiring cueshark Automation Technology Products 6 02-27-2008 04:20 AM
Wiring help..... fineartlig Industrial Hobbies (Support forum) 1 09-24-2007 11:21 AM
need help wiring dtman CNC Plasma and Waterjet Machines 11 02-19-2007 07:55 AM
P5 Wiring tintruder Servo Drives 2 02-03-2006 11:13 AM




All times are GMT -5. The time now is 11:00 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361