Need Help with Magnetic reversible Contactor

I'm a little frightened of the wiries going to this thing. This is an Allen Bradley 705X-BOD (with 2x 1401-N10 surge supressors) that is currently controlling my 3-ph spindle motor. I'm pulling it out to put it in a new smaller case (and new controller), but I'm frightened of all the control wires coming to and fro on this thing.

Anyone know how these are wired or know where I might find a wiring diagram? The main 3 ph wires seem simple enough, especially since there are basically 3 wires in (top), and then 3 out (bottom, under a mystery device, maybe a breaker?)

Any info or thoughts on this would be helpful. I found some newer contactors on ebay for around $50 that I can get wiring on. This one seems to be going for closr to $300 in most cases...that might be because it's good, or maybe just old and hard to get (probably).

Thanks
Attached Thumbnails
Click image for larger version

Name:	ab1.jpg‎
Views:	101
Size:	163.7 KB
ID:	49106  
Reply With Quote

  #2  
Old 12-21-2007, 11:59 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by Chris64 View Post
=
Anyone know how these are wired or know where I might find a wiring diagram? The main 3 ph wires seem simple enough, especially since there are basically 3 wires in (top), and then 3 out (bottom, under a mystery device, maybe a breaker?)
I guess the PDF I posted didn't do it
It is going to be wired up pretty much as the 3 phase reverser in the diagram.
Except it looks like you have 120v control voltage instead of 24v.
The control wiring is usually electrically interlocked through N.O. contacts on each side and also the N.C. motor over-loads (mystery device?).
If the wiring is in place, just reverse engineer it by tracing the wires and draw out the schematic.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3  
Old 12-22-2007, 09:24 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Just an after thought on the PDF diagram, whatever type of contactor you use try and get one with a N.O & a N.C. auxiliary contact on each contactor or one that can accept add-ons, most modern ones do, they just clip on the front actuator with the new DIN style.
The reason is, especially with manual P.B.s, is that without using the N.C. contacts to interlock the two fwd/rev PB's, it is possible to energise the opposite coils, although the second one would not pick up due to the mechanical interlock, if you are using AC and the contactor is unable to pick up due to this mechanical Interlock, you will burn the coil out, this doesn't happen with DC coils, however.
The PDF I posted on the other link does not show this.
The N.O. contacts are shown in the normal way as latching contacts across the start PB's.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #4   Ban this user!
Old 12-22-2007, 09:55 AM
 
Join Date: Aug 2006
Location: US
Posts: 281
Chris64 is on a distinguished road

Originally Posted by Al_The_Man View Post
I guess the PDF I posted didn't do it
It is going to be wired up pretty much as the 3 phase reverser in the diagram.
Except it looks like you have 120v control voltage instead of 24v.
The control wiring is usually electrically interlocked through N.O. contacts on each side and also the N.C. motor over-loads (mystery device?).
If the wiring is in place, just reverse engineer it by tracing the wires and draw out the schematic.
Al.
Your PDF was a great help. I drew up a schematic of how this is all going to go together with your PDF as the model. Then I started looking at how things were going to come apart and got a little overwhelmed. This just had way more control connections then your diagram.

Like you said, I'll probably have to reverse engineer it a bit. I should just power it up while it's open (i've been a little intimidated to do that) and measure the voltage with different actions. Tricky with AC since I'm not sure what is "neutral."

So, in your opinion, use what I have or ebay? It must be an OK contactor for this size machine.

While we're on that topic. For my circuit I'll probably need a 110 line for something. My Dad is an electrician and suggested I go from L1 or L2 to Neutral (and yes, I'll be putting him to work on it when he's down for Christmas ). It appears that this existing controller went 220 to a 1:2 transformer to bring it back down. Thoughts? 220 would probably be less likely to be affected by spikes caused by the motor starting...but maybe not.
Reply With Quote

  #5  
Old 12-22-2007, 09:59 AM
HuFlungDung's Avatar
Moderator
 
Join Date: Mar 2003
Location: Canada
Posts: 4,825
HuFlungDung is on a distinguished road

If you plan to go to a VFD someday (which is a practical necessity), you won't need that crap. You'll want to use the VFD to create the spindle motor control system. So don't waste more money buying yet more contactors. Those ones serve the same purpose as a brand new one.

For the VFD, all you will need is the mechanical disconnect to supply power to the VFD and anything else you might need to retain inside the cabinet. Estop and on, off, reverse must be handled within the VFD as you must not break the main power between the motor and the VFD output.

Each coil on the contactor relay has two contacts, an in and an out. Those will be interlocked through clever wiring methods so that both cannot engage simultaneously.

There is often an auxilary set of contacts there, which create a latched circuit after the coils have been momentarily energised by an external push button station (probably from the M function board, to a reed relay board, to an icecube relay to this contactor relay). So part of what the mess is, is the means of creating the latched condition of the coil so that current flows through an auxilary circuit after the pushbutton is released. Any interruption to that latched circuit (ie., spindle stop) breaks the current through the coil latched circuit causing it to drop out of contact when the springs open the contactor.

It can be tough to figure it out, I'll be the first to admit. But, if you're going to stick with contactors, you'll end up duplicating that 'mess' in your own way later on. You might even come to appreciate how well thought out it is
__________________
First you get good, then you get fast. Then grouchiness sets in.

(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-22-2007, 10:14 AM
 
Join Date: Aug 2006
Location: US
Posts: 281
Chris64 is on a distinguished road

I just relooked at it and I guess I'm throwing in the towel a little too quickly. I guess it just has 4 connection points per contactor (Like Al's PDF). The other connections are surge supressors and the overload thingamajig (it's already wired, don't mess with it, right?).

Hu, I totally understand what you're talking about with holding the contactor open...I'm guilty of making some low budget remote car starters with relay's using the same method. I guess I just wish I knew what did what so that I could be confident in my wiring. Al's PDF shows that one pair is a coil, and another is a capacitor (I think). I'm not sure if this is the same, and quite honestly I'm not sure why there would be a capacitor in there at all (I'm sure theres a good reason though).

With 12v I used to do a lot of bench playing with a makita battery...maybe I should do the same with this...just A LOT more carefully. (eek) After carefully documenting how this is connected that is.
Reply With Quote

  #7  
Old 12-22-2007, 10:15 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by Chris64 View Post
So, in your opinion, use what I have or ebay? It must be an OK contactor for this size machine.
As long as it is rated for the correct HP, but like I mentioned, you should ensure you have, or can add, a N.O & a N.C. aux contact to each contactor.

Originally Posted by Chris64 View Post
My Dad is an electrician and suggested I go from L1 or L2 to Neutral (and yes, I'll be putting him to work on it when he's down for Christmas ).
You have the answer right there, 'My Dads an Electrician'
I would use the live and neutral for 120v rather than fitting a transformer.
I think you are confusing the N.O. contact symbol with a capacitor
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 12-22-2007, 10:30 AM
 
Join Date: Aug 2006
Location: US
Posts: 281
Chris64 is on a distinguished road

Originally Posted by Al_The_Man View Post
I think you are confusing the N.O. contact symbol with a capacitor
Al.
oops!

the 220-110 transformer (it's in the pic on the left) I think might be dedicated to just controlling this contactor. Strange. Maybe it isolates the contactor from the rest of the circuit better this way.
Reply With Quote

  #9   Ban this user!
Old 12-22-2007, 10:34 AM
 
Join Date: Aug 2006
Location: US
Posts: 281
Chris64 is on a distinguished road

THAT MAKES SENSE NOW! You're right, I thought it was a cap (smaller then the other NO contacts)...I figured it cause some type of momentary surge so it wouldn't overwhel the coil or whatever, but with AC that was just not making sense...but basically just a little NO control circuit! Seriously, the light just went on here, thanks!
Reply With Quote

  #10  
Old 12-22-2007, 10:38 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Incidentally, to avoid confusion, ladder or schematic diagrams usually show a N.O. like -||- and a cap like -|(- .
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 12-22-2007, 08:11 PM
 
Join Date: Aug 2006
Location: US
Posts: 281
Chris64 is on a distinguished road

Just a funny update. In my efforts to reverse engineer everything, I flip on my controller and presto, it works again (should I be glad?). Well I saw this as an opportunity to machine all the brackets I would need for the new encoders etc. So I grab my computer to start sending the new programs and...nothing. It was dead again.

That was it! I had enough! I photgraphed and documented everything and just started cutting components out. No during back now! ha ha ha. When I'm done I'm going to take this bandit case out to a field and go all "office space" on it! Well, not really, cause this thing would win...I'm really going to go "ebay" on all the little parts though.

What I was really surprised about was how small the power wires were that went to the driver transformer (Heavy BTW, maybe 50 pounds). Just two little (maybe 18 guage) wires and that's it. Then 4 big 10 guage wire coming out of it. Seems a little out of wack, since it was running at 110 and only converting it down to 80V. It's not like the the v/a draw is that different.

And it barely fits in my new case (whew). The contactor is next...but it's riveted in so I couldn't yank that out as easily.

Do you think I should worry about EMI from this transformer to the Gecko components? I found an EMI filter in there and figured I could probably reuse it.
Reply With Quote

  #12   Ban this user!
Old 12-23-2007, 02:36 PM
 
Join Date: Aug 2006
Location: US
Posts: 281
Chris64 is on a distinguished road

Also, just to update what the connections are in case anyone else runs across this type of contactor.

The two terminals next to the red writing are for the coil, ac 120 (as it states right on it - it seems so obvious in retrospect)
The two top terminals (labeled 5/7 on the left) are NC
The two terminals below those are NO.
The Surge supressor just gets wired parallel to the coil.

So each coil power is routed through the opposite contactor NC switch. This way they both can't be powered simultaneously.

I'm still not entirely clear on what the overload device at the very bottom is for (besides dealing with overloads). It has two small red wires fed to it for something. Thoughts?
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
fanuc magnetic sensor keithmech Fanuc 11 05-04-2009 07:30 PM
magnetic sensor keithmech General Electronics Discussion 0 07-28-2007 06:04 PM
magnetic clamping dhiruj Work Fixtures and Hold-Down Solutions 1 04-28-2007 02:37 PM
Magnetic Chuck for Milling Machine...? tdfsu General Metal Working Machines 8 03-19-2007 02:41 PM
Contactor help ???? Fabric8r General Electronics Discussion 1 05-26-2006 05:27 PM




All times are GMT -5. The time now is 09:08 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361