Question Square D starter/contacter help needed

I am trying to wire a Hem metal saw that I got in pieces. I have a Square D nema size 1 contacter. The numbers on it are:
Type sc03
form s
series a


The problem is when I energize the 120v coil to start the motor I lose the 120v to my control.
Any help would be appreciated.
Thanks Mike.
Reply With Quote

  #2  
Old 12-01-2007, 03:37 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

The description of what is happening is too vague, is the contactor staying in but the control voltage disappears?
If so, the control may be going through NC contact on the SqD.
Did you wire it from the original or did you come up with the control circuit? What picks up the contactor?
I would imagine it is a standard push button start across a retaining contact on the SqD and a stop button in series?
Sometimes a trip switch drops out the motor when the saw is down.
More is required and preferably how you wired it.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 12-01-2007, 05:26 PM
 
Join Date: Aug 2005
Location: usa
Posts: 59
mt92 is on a distinguished road

The 120v is lost for the control when the blades comes on and then as soon as the blade stops the control voltage is there again. I think that it is the way I have the 120 coil on the starter wired?
Reply With Quote

  #4  
Old 12-01-2007, 06:26 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Unfortunately, without detail as to how you wired it it is sheer speculation.
If you can post the wiring connections then maybe help can be offered.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 12-01-2007, 09:44 PM
 
Join Date: Aug 2005
Location: USA
Posts: 1,622
One of Many is on a distinguished road

Here is a standard 3 wire motor control circuit that should work. The only difference would be the source of power, either direct from L1, L2, N or through a step down control transformer. The contactor itself for the most part makes no difference what it controls, with the exception of ratings and overload protection.

The type of contactor you have should include an auxiliary contact that is NORMALLY OPEN for the latching of the coil across the start button. Another one that is NORMALLY OPEN, but HELD CLOSED by the overload holding mechanism.

What you need to see, is that if any of the contacts that maintain the power to the coil is interrupted, the M1 coil drops out.

Compare this to what you have to see if it makes more sense or resolves your troubles.



DC
Attached Images
File Type: bmp Motorcontrol.bmp‎ (118.0 KB, 148 views)
__________________
Learn cause and effect through experience. Mastering those relationships is the "Common Sense" ability within the art of any trade.

Last edited by One of Many; 12-01-2007 at 09:59 PM.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-02-2007, 09:33 AM
 
Join Date: Nov 2005
Location: Alabama - USA
Posts: 252
Mike Nash is on a distinguished road

Not to be picky, but you're more likely to see it as below, simply because it's easier to tie the aux contact to the coil. In a multi starter situation, you don't have to tie L1 to the starters at all, just the pusbuttons.

And how did you get the thumbnail in your post?
Attached Images
File Type: bmp Motorcontrol.bmp‎ (118.0 KB, 131 views)
Reply With Quote

  #7  
Old 12-02-2007, 10:14 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Control wise, there also could be more going on here, depending on whether it is a simple reciprocating saw or a Hem Vertical band saw, where the contactor control is tied in to other control items.
Also, although for many years the OL has been wired this way, it is now considered safer to wire it in the 'Hot' side of the coil when a grounded neutral exists.
The old way, If a ground occurs between the coil & OL, the OL is defeated.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 12-02-2007, 02:01 PM
 
Join Date: Aug 2005
Location: USA
Posts: 1,622
One of Many is on a distinguished road

If it weren't for someone being picky, the rest of us would never know how fast posting mis-information can be corrected with better ways(with good reason) to do the same thing. Although I have seen it drawn both ways, I sincerely appreciate the reasoning behind why and how it is done otherwise.

To get an image inside the post. I right click the uploaded image attachment link to get an address. Copy that address, now click the mountain scene icon above this post reply window and paste the copied address into its pop-up address bar.

DC

__________________
Learn cause and effect through experience. Mastering those relationships is the "Common Sense" ability within the art of any trade.

Last edited by One of Many; 12-02-2007 at 02:22 PM.
Reply With Quote

  #9   Ban this user!
Old 12-02-2007, 05:37 PM
 
Join Date: Nov 2005
Location: Alabama - USA
Posts: 252
Mike Nash is on a distinguished road

Thanks DC. I tried that, but it wasn't showing up in the preview for me, so I figured I was doing it wrong.

And I agree Al on the O/L location. I've always hated the neutral side wiring. I wonder where that convention got started?

I've also run into situations where the stop pushbutton was in the seal in around the start pushbutton. This allows the contactor to be pulled in even while the stop is being held! Lawsuit waiting to happen.
Reply With Quote

  #10   Ban this user!
Old 12-02-2007, 07:49 PM
 
Join Date: Aug 2005
Location: USA
Posts: 1,622
One of Many is on a distinguished road

Originally Posted by Mike Nash View Post
I've also run into situations where the stop pushbutton was in the seal in around the start pushbutton. This allows the contactor to be pulled in even while the stop is being held! Lawsuit waiting to happen.
The OEM I used to work for did it this way in order to have a jog function. Several other machines I ran in the steel wire industry while in electronics Tech school, had this also. And I cannot tell you how many times the contacts welded on the main motor contactor with no way to shut it off on the operator side. The element of danger is ever present, but certain modes of failure may be unpreventable. Redundant contacts might be a fail safe?

DC
__________________
Learn cause and effect through experience. Mastering those relationships is the "Common Sense" ability within the art of any trade.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 12-04-2007, 08:07 AM
 
Join Date: Nov 2005
Location: Alabama - USA
Posts: 252
Mike Nash is on a distinguished road

You should look into safety relays and circuits. Dual contactors, in series, force operated contacts, redundant safety checks (that can't simply be duplicates.) It can get crazy.
Reply With Quote

  #12  
Old 12-04-2007, 09:10 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by Mike Nash View Post
You should look into safety relays and circuits.
They are slowly appearing in N American equipment, Europe has used them extensively for some years now.
I believe Piltz was one of the first producers of safety relays. There is quite a combination available that covers safety and internal controlled shut down timers etc.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Starter Set of End Mills Megaplow Benchtop Machines 1 11-13-2007 06:41 PM
would this be a good starter hutch08 Bridgeport and Hardinge Mills 1 10-12-2007 06:35 PM
New to CNC lathe and need starter projects? Rickady General Metal Working Machines 2 08-24-2007 05:53 PM
Starter Bit Set Recommendations 3D Robotica General Material Machining Solutions 0 07-23-2007 02:18 PM
New starter to CNC Simon_18 General Metal Working Machines 5 06-09-2006 11:09 AM




All times are GMT -5. The time now is 09:05 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361