Limit Swithces NO or NC????

Ok I thought I new what I was doing but now I'm not sure. I have all my limits wired in with 2 wires to a set of NC contacts. How are they suppose to be? I was watching a Mach 3 video and they talked about using a common ground and NO contacts?? I'm confused!!

Dan
Tweet this Post!Share on Facebook
Reply With Quote

  #2   Ban this user!
Old 10-30-2007, 06:54 PM
 
Join Date: Aug 2007
Location: united states
Posts: 4
lowelife is on a distinguished road
Limit switches

NO- stands for normally open, allowing the circuit to close when tripped, and NC - normally closed will complete circuit when activated. Depending on how you want to machine to react is how you would set those up.
Tweet this Post!Share on Facebook
Reply With Quote

  #3   Ban this user!
Old 10-30-2007, 08:35 PM
gar gar is offline
 
Join Date: Mar 2005
Location: USA
Posts: 1,498
gar is on a distinguished road

071030-1912 EST USA

An unactuated NO contact is an open circuit. When actuated it closes. A limit switch with a lever will be actuated when you move the lever far enough to change the switch's state.

An unactuated NC contact is a closed circuit until actuated.

If you combine a number of limit switches to produce a single ouput, then by connecting:

NO switches in parallel any one or more actuated produces a closed output state. Depending upon what you do with this circuit will determine the resultant operation of your system. Suppose the switch parallel network is connected between a +5 V source and a pull down resistor. Then activation of any one or more switches will produce 5 V across the pull down resistor. This circuit is not as noise immune when you really want that immunity as is the NC type circuit. This is described as positive logic inclusive OR circuit.

NC switches in series can achieve the same logical inclusive OR as the above parallel NO switches. Here the noise immunity is much better because the low impedance of a closed contact circuit until you exceed a limit. Here we would connect one end of the series switches to common (ground) and the other end to a pull up resistor. We still have 0 V output until at least one switch is activated. Activation any one or more switches will open the circuit causing the output to go high.

Use the series connection of the NC switches.

.
Tweet this Post!Share on Facebook
Reply With Quote

  #4   Ban this user!
Old 10-30-2007, 08:39 PM
 
Join Date: Jan 2006
Location: USA
Age: 45
Posts: 596
stevespo is on a distinguished road

Either method (NC or NO) will do the job for you. One advantage of running your switches NC is that in the event of a damaged wire (or other problem), your circuit will "open", triggering your software that some type of event has occured. You can then troubleshoot and fix it before it becomes a real problem.

This happened to me recently, when I got a spurious eStop in the middle of a job. I tracked it down to a loose connection. Since I had it wired NC, I knew I had a problem and fixed it immediately. If I had wired it NO, I would not have known - until I had actually tried to use my eStop switch - and it wouldn't have worked.

Steve

Last edited by stevespo; 10-30-2007 at 11:00 PM. Reason: fix typo
Tweet this Post!Share on Facebook
Reply With Quote

  #5   Ban this user!
Old 10-30-2007, 10:13 PM
teamtexas's Avatar  
Join Date: Aug 2007
Location: USA
Posts: 268
teamtexas is on a distinguished road

Gar, would the NC switches in series be considered "active low" until they are tripped?
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 10-30-2007, 10:42 PM
acondit's Avatar  
Join Date: Apr 2005
Location: USA
Posts: 1,774
acondit is on a distinguished road

Dan,

It would seem to me that you would want "active high" until tripped. Otherwise, if power connection to the circuit fails, you have the same problem as a NO switch. You can't tell until the switch is tripped that it is not working. You don't know whether it is "low" because the switch is closed or "low" because power to the circuit has failed.

Alan
__________________
http://www.alansmachineworks.com
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 10-31-2007, 09:38 AM
 
Join Date: May 2004
Location: United States
Posts: 455
JRoque is on a distinguished road

Hi. Use NC limit switches. That means that there's normally a voltage present in the circuit and there's no action during that state. When the switch opens, the voltage goes to zero and the limit action is triggered. That's called an active-low switch.

NC switches are preferred because they fair better in electrically noisy environments. If you use NO switch a voltage spike caused by noise can trigger the limit switch action (which would be active-high for NO).

JR
Tweet this Post!Share on Facebook
Reply With Quote

  #8   Ban this user!
Old 10-31-2007, 12:40 PM
gar gar is offline
 
Join Date: Mar 2005
Location: USA
Posts: 1,498
gar is on a distinguished road

071031-1104 EST USA

teamtexas:

http://en.wikipedia.org/wiki/Active_low

My interpretation of this definition is that "active low" means that a logic 1 or TRUE is represented by a lower voltage than a logic 0. So in a 5 V system near 0 volts is a logic 1, and towards +5 is a logic 0. In an RS232 system -10 V is a logic 1 and +10 V is a logic 0. The rest state in RS232 is -10 V.

Whether a NC contact is active low or high is dependent upon the definition of the actuator of the switch and how the switch is wired.

Suppose the switch function made is to be treated as a logical 1 and that when made the contact closes, and the switch is connected between +5 V and a gate input, then the signal at the gate input is "active high". Connect the same switch to 0 V, then its output is "active low". As needed you have a pull up or down resistor.

Change the name "made" to "not made" and you reverse the above meanings.

Logically if I put several NO contacts in series, and closed represents a TRUE input, then this series connection performs the logical AND operation and a TRUE output occurs only when all inputs are TRUE (closed) and a closed circuit is logic TRUE.

Logically if I put several NC contacts in parallel, and open represents a TRUE input, then this parallel connection performs the logical AND operation and a TRUE output occurs only when all inputs are TRUE (open) and an open circuit is logic TRUE. If you redefine open circuit as FALSE, then this is the logical INCLUSIVE OR.

Note we can have multiple input AND and OR circuits, but only two input EXCLUSIVE OR circuits.

Fundamentally in the multiple limit switch application the activation of any one or more limit switches should produce a stop action, and I would classify this as an INCLUSIVE OR function. So no matter how I wire the switches what I want is any one or more switches to perform the desired action.

Clear? NO.

Probably not a good idea to get hung up on whether it is active low or high.

.
Tweet this Post!Share on Facebook
Reply With Quote

  #9  
Old 10-31-2007, 01:55 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

In the realm of PLC inputs etc, the term Active Low or High, usually means what the status has to be to activate the named Function of the input.
Take for example over travel switches used in systems like Fanuc or Mitsubishi etc, these are usually dedicated inputs that have to have 24vdc to disable the OT condition, the OT occurs when the NC switch opens and the input goes to a logic 0, This is then Active Low for the assigned condition to occur.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #10   Ban this user!
Old 10-31-2007, 03:06 PM
acondit's Avatar  
Join Date: Apr 2005
Location: USA
Posts: 1,774
acondit is on a distinguished road

Originally Posted by Al_The_Man View Post
In the realm of PLC inputs etc, the term Active Low or High, usually means what the status has to be to activate the named Function of the input.
Take for example over travel switches used in systems like Fanuc or Mitsubishi etc, these are usually dedicated inputs that have to have 24vdc to disable the OT condition, the OT occurs when the NC switch opens and the input goes to a logic 0, This is then Active Low for the assigned condition to occur.
Al.
Al,

Then the issue is what is the signal you are tracking. Given a NC limit switch that is high when closed, one could say that it is "active high" for the condition - "within limits" (i.e., the limit switch is closed and powered) but if you are considering the condition to be "over travel" the signal is "active low" when you trip the limit switch (or power to the switch fails).

Alan
__________________
http://www.alansmachineworks.com
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11  
Old 10-31-2007, 03:57 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

That is what I meant by my first sentence, maybe not very clearly, What I meant was it is the condition that it is in when it performs the function of its description, as in the example, the name of the switch or input is Over Travel Switch.
So if I describe the machine over travels as being active low, it usually means that the logic is looking for a 0 when the overtravel occurs.
Probabally a case of semantics, but it can be important if you are writing the logic for the function.
Some Manuf. indicate a active low input required by placing an Asterisk in front of the input descriptions and designated input number .
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #12   Ban this user!
Old 10-31-2007, 05:25 PM
teamtexas's Avatar  
Join Date: Aug 2007
Location: USA
Posts: 268
teamtexas is on a distinguished road

Wow, there's alot more to these then I every would have thought. Maybe I need to ask the question in a simpler way (so I can understand). I want to wire up limits for the x, y & Z axis. I will be purchasing Gecko G203v drivers and a CNC4PC- C1G Parallel port interface card. I plan to control all of this with Mach 3.

1. Should I use NO or NC contacts on the limits?

2. Should I run a pair of wires to each (axis) set of of limits. I assume each (axis) set of limits should be connected in series, however I would like to use one limit on each axis as my home switches also.

3. Should the wires be shielded?

4. Should all the limits share a common GND? If so, should this GND be bonded to the metal frame of the machine?

5. Can I use proximity switches on one of the axis?

Thanks in advance for all your help!
Dan
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
SX3 CNC Limit Switches Babba Syil Products 5 09-23-2007 02:44 PM
Limit Switches Drakkn DIY-CNC Router Table Machines 1 08-10-2007 05:57 PM
TM1-P, limit switch jheyliger Haas Mills 10 06-29-2007 09:08 PM
limit problems rboeser Mach Plasma / Laser 0 04-01-2007 01:45 PM
Limit switches itsme General Electronics Discussion 5 05-01-2005 06:02 PM




All times are GMT -5. The time now is 12:29 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353