Power supply ground clarification.

In searching the forums for help on the possibility of hooking two PS together, there is the mention of;

1) Another thing to watch out for with separate supplies is if the commons are at ground potential

2) The fact is if you are working with supplies that have isolated grounds you can do it

The terms in bold are what I need clarification on and how can I determine what my PS have ?


Thanks
Ken
Tweet this Post!Share on Facebook
Reply With Quote

  #2  
Old 10-03-2007, 12:03 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

Simply measure continuity between the black wire in the HD connectors (power off) and the case of the supply, you should have very high resistance (meg-ohms) most are isolated here and the ground connection is made by at least on ground securing screw on the mother board.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #3  
Old 10-03-2007, 12:32 PM
Gold Member
 
Join Date: Apr 2003
Location: Ohio, USA
Posts: 1,734
Ken_Shea is on a distinguished road

AL,
I am getting no reading at all, and best I can see no ground connection on the MB.

http://cgi.ebay.com/Power-One-HD48-7...QQcmdZViewItem



Ken
Tweet this Post!Share on Facebook
Reply With Quote

  #4  
Old 10-03-2007, 01:16 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 15,714
Al_The_Man is on a distinguished road
Buy me a Beer?

I though you meant PC power supplies as some have done, these linear supplies do NOT usually come with ground connected and it is done at the discretion of the user.
Also I assumed you meant in series, I am not sure I would want to connect this type in parallel, as they each have electronic regulation circuitry, and some have over-voltage crow-bar, This is a SCR placed across the output, and if the voltage goes up by reason of PS defect or large back EMF the SCR fires, placing a high load on the DC output and causes the PS to shut down untill powered down and up again.
Some thing to look out for in Linear supplies of this type.
Al.
__________________
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Tweet this Post!Share on Facebook
Reply With Quote

  #5  
Old 10-03-2007, 09:13 PM
Gold Member
 
Join Date: Apr 2003
Location: Ohio, USA
Posts: 1,734
Ken_Shea is on a distinguished road

Thanks for the information Al.

Ken
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 10-15-2007, 02:26 AM
 
Join Date: May 2007
Location: Australia
Posts: 9
hixfixit is on a distinguished road

Running power supplies in parallel is not recommended at all for a situation where there current required is higher than the individual capacity of the power supplies. Some very expensive power supplies are actually designed for load sharing. Most are not.

If one power supply has a higher voltage than the other one (the difference does not need to be great), it will do all/most of the work, causing more strain on it and leading to earlier failure. Then you will have a situation where you have one power supply left trying to do work it was never intended to, which will cause overload protection to trip, power supply death or in the worst case scenario, a fire.

When you use diodes, that's normally for setting up an 'OR' type configuration. In other words, one fails, and the other one kicks in transparently, thus you have redundancy. It can also be used to protect one power supply from the other in the event of one failing in such a way that it causes current to flow into the working one, thus destroying both. It goes without saying that the diodes should be of sufficient rating to handle the current draw.

In summary, we should NOT recommend to dealers that they do this unless it's for redundancy. They should get a bigger power supply....end of story. In the event that they decide to parallel them anyway contrary to our advice, they don't blow up when you parallel them without diodes in place and are very unlikely to. The diodes however, should be in place nevertheless for some kind of protection in the event of failure of one of the power supplies.
Tweet this Post!Share on Facebook
Reply With Quote

  #7   Ban this user!
Old 10-15-2007, 08:13 AM
gar gar is offline
 
Join Date: Mar 2005
Location: USA
Posts: 1,498
gar is on a distinguished road

071015-0852 EST USA

Ken:

The power supply you referenced lists the input voltage as 100 - 240. My guess is that is an incorrect statement. More likely it should read
120 xor 240 +4%/-17%. I am guessing it should tolerate 125 V as a max.

Most commerical linear regulated supplies run very hot at maximum input voltage with maximum output load current. Basically marginal design. For good reliability you need to derate the output current rating. If enclosed it is worse.

.
Tweet this Post!Share on Facebook
Reply With Quote

  #8  
Old 10-15-2007, 08:34 AM
Gold Member
 
Join Date: Apr 2003
Location: Ohio, USA
Posts: 1,734
Ken_Shea is on a distinguished road

hixfixit,
Thanks for the additional information. these have an adjustable voltage up about 6V and down about 10V so they could be balanced if that was the only issues I guess.

Gar,
You are absolutely correct on both counts, the voltage and heat. A decal on the PS indicates a either or voltage and also indicates that a 15cfm air-flow is required if used at full load.


I have decide to build a single PS, was hoping to avoid this as the more I read the more confused I get on what specific components are needed.

Thanks
Ken
Tweet this Post!Share on Facebook
Reply With Quote

  #9   Ban this user!
Old 10-15-2007, 08:43 AM
gar gar is offline
 
Join Date: Mar 2005
Location: USA
Posts: 1,498
gar is on a distinguished road

071015-0739 EST USA

Ken:

If all you want is a power supply to supply motors, either stepper or servo, then generally there is no particular need for a regulated supply.

What is the power supply for and what voltage, current, and regulation do you need?

.
Tweet this Post!Share on Facebook
Reply With Quote

  #10  
Old 10-15-2007, 09:03 AM
Gold Member
 
Join Date: Apr 2003
Location: Ohio, USA
Posts: 1,734
Ken_Shea is on a distinguished road

Gar,

The voltage and current information I have is:
1) Servos are 36VDC
2) Maxium continuous current is 3amp
3) Power delivered to load is 86 watts
4) Was wanting to build a PS that will handle 3 of these servos at maximum load with some reserve.


Ken
Tweet this Post!Share on Facebook
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 10-15-2007, 09:20 AM
gar gar is offline
 
Join Date: Mar 2005
Location: USA
Posts: 1,498
gar is on a distinguished road

071015-0811 EST USA

Ken:

In all likelyhood you will not need a continuous steady state 9 A. But it may be useful to design for 12 A as your full continuous duty load. This will provide lots of margin.

The bigger question is what maximum voltage your servo drivers can tolerate and what minimum voltage can you work with.

Almost any power supply can be approximated as a constant voltage source, Vs, with a series internal resistance of Rs. Then your output voltage will be
Vo = Vs - (Il * Rs) where the load current is Il.

If you assume a 10% internal impedance, then your no load to full load output voltage will change by 10%.

.
Tweet this Post!Share on Facebook
Reply With Quote

  #12  
Old 10-15-2007, 09:35 AM
Gold Member
 
Join Date: Apr 2003
Location: Ohio, USA
Posts: 1,734
Ken_Shea is on a distinguished road

gar,
12amp sounds good.

The drivers are Rutex 2010 rated at 100V and 20 amp.

"what minimum voltage can you work with"
Not sure what you need to know here?


Ken
Tweet this Post!Share on Facebook
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How'd you supply your power supply? cnczane DIY-CNC Router Table Machines 12 08-28-2011 06:13 AM
More power from switching power supply R.thayer General Electronics Discussion 4 03-10-2007 08:03 PM
Power Supply from a computer power supply jmytyk General Electronics Discussion 21 01-11-2006 03:56 PM
Motor supply ground vs Logic ground? Gashmore General Electronics Discussion 11 06-07-2005 06:21 PM
Power Supply ground question chas Gecko Drives 5 04-16-2005 07:48 AM




All times are GMT -5. The time now is 02:29 AM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353