Question WATERPROOF Extension Cord to Shed

Hi folks,

I haven't been on cnczone in a while.....haven't been on the tinternet in a while, been very busy with work.....now its time to get back to the real work of cnc'ing!!

Background: Anyway, Im about to buy a shed to relocate my tools and have some sort of temporary proper workshop. Unfortunately, right now at least, I can't really get an electrician to put in permanent power since the shed will be in the in-laws house, and the shed itself I think is enough to annoy them with for one day!

Problem:
So, obviously I need power, and running an extension cord or cord's from the house is the order of the day. Sounds simple! Ok, so its September right now, and in about a month god will unleash raining fury on Ireland as per his usual routine . Now Im thinking I dont want some crappy extension cord electrocuting me when it's lying in a pool of water from the house to the shed. So I searched the internet, and there doesn't seem to be much in 220V outdoor cords out there, I only found this one on amazon but its not long enough: http://www.amazon.co.uk/Waterproof-o.../dp/B000R2SFF8

So Im thinking I'll make two of my own as follows:

RCD plugged into mains in house.
Extension cord plug connected to RCD.
15Amp (Or higher) cord connected from the plug and run out to shed, where it will have 4 sockets at that end.

I figure I can use two of these giving me 8 power points in the shed. Four points always being used for the cnc machine, and the others only being used one or two at a time as I'm working. I can also connect the cord above gnd level outside to the house wall wherever possible to minimise the amount its physically sitting in water.

So what do you all think in general?

Am I missing any safety devices I can add into the circuit?

Do you think 15Amp cable is enough or should I use a different amperage, the mains is 13Amps I think?

Thanks all. Hope everyone's being keeping well while I was gone.
Reply With Quote

  #2   Ban this user!
Old 09-09-2007, 03:02 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,563
Geof will become famous soon enough

Possibly you should find out what the rules and regulations say and the fine print in your in-law's insurance policy. You may rig something up that is safe and works but if it contravenes regulations and then something bad happens, that may be entirely independent of your electrical cord, things can get nasty.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Reply With Quote

  #3   Ban this user!
Old 09-09-2007, 03:23 PM
thkoutsidthebox's Avatar  
Join Date: Nov 2006
Location: Ireland
Posts: 1,698
thkoutsidthebox is on a distinguished road

Thats a good point Geof, maybe I should insist on getting an electrician to run a cable...I just thought that extension cords are used all the time for the lawnmower/strimmer etc, the only differance is that mine has to be able to be used in the rain...
Reply With Quote

  #4   Ban this user!
Old 09-09-2007, 04:14 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,563
Geof will become famous soon enough

Where the distinction is made over here in the regulations is that the cord is to be used in a temporary manner. As soon as you clip it up on a wall you are making it non-temporary.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Reply With Quote

  #5   Ban this user!
Old 09-09-2007, 05:18 PM
 
Join Date: Dec 2005
Location: UK
Posts: 1,407
martinw is on a distinguished road

Originally Posted by thkoutsidthebox View Post
Thats a good point Geof, maybe I should insist on getting an electrician to run a cable...I just thought that extension cords are used all the time for the lawnmower/strimmer etc, the only differance is that mine has to be able to be used in the rain...
Dear thkoutsidthebox,

I do not know if you are in Eire or the UK, but here is an IEE article that explains the way to do a fixed installation "properly".

http://www.iee.org/Publish/WireRegs/...s_outdoors.pdf

The underground cable would most likely be SWA (steel wire armoured). The alternative would be to run the cable overhead on a catenary wire. I think the rule is that the cable should be at least 3.5 metres above ground, if no vehicles are about. Obviously, the sheath of any overhead cable needs to be UV resistant. Cables laid on the ground are not an option for a fixed installation, simply because, even in the case of SWA cable, mechanical damage is still a possibility.

Personally, I'd probably take the risk of your RCD/extension lead scheme, and ensure it was disconnected when not in use. I would not suggest others do however. Your risk, your decision..

Best wishes,

Martin
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 09-09-2007, 05:43 PM
 
Join Date: Nov 2006
Location: New Zealand
Posts: 4
Foils is on a distinguished road

My old man has an extension cord that runs inside a hose pipe - he just threaded the cable down the hose and then put plugs on the end after. That makes the cable 'water proof' and offers some degree of protection from being mechanically damaged as well. Building inspectors just thought it was a water hose and didn't ask any questions.
Reply With Quote

  #7   Ban this user!
Old 09-09-2007, 07:15 PM
 
Join Date: Dec 2005
Location: UK
Posts: 1,407
martinw is on a distinguished road

If you go the extension lead way, I wouldn't worry too much about having to protect the cable from water if you choose the right one. Flexible cables snake round building sites all the time, (yes they tend to be 110v not 230v, but they can take the environmental conditions).

Something like

H07RN-F Harsh Environment flexible cable might do.

3 core
1.5 mm2
22 amps
about 11mm OD
about £1.50 per metre

Best wishes

Martin
Reply With Quote

  #8   Ban this user!
Old 09-10-2007, 08:50 AM
thkoutsidthebox's Avatar  
Join Date: Nov 2006
Location: Ireland
Posts: 1,698
thkoutsidthebox is on a distinguished road

Thanks folks.
Martin, I can get that cable you mentioned locally in Radionics, so that'll do fine. I'll make my own extension lead and run it inside some hose pipe for extra protection, and I'll roll it up and leave it in the shed when I'm not using it. It says it's rated for 40 Amps, so more than enough there, the house board will trip before the cable is overloaded. Not cheap though is it?

http://www.radionics.ie/electronic-c...-4MM2-50M.html
Reply With Quote

  #9   Ban this user!
Old 09-10-2007, 09:16 AM
 
Join Date: Dec 2005
Location: UK
Posts: 1,407
martinw is on a distinguished road

Originally Posted by thkoutsidthebox View Post
Thanks folks.
Martin, I can get that cable you mentioned locally in Radionics, so that'll do fine. I'll make my own extension lead and run it inside some hose pipe for extra protection, and I'll roll it up and leave it in the shed when I'm not using it. It says it's rated for 40 Amps, so more than enough there, the house board will trip before the cable is overloaded. Not cheap though is it?

http://www.radionics.ie/electronic-c...-4MM2-50M.html
Dear thkoutsidethebox,

I have no idea how long this extension lead is going to be, or what size load you will have in your shed. As a result, I do not know if voltage drop might be a problem. The temporary arrangement you described was going to connect via a plug-in RCD to a 13 amp socket in the house. If your total load is greater than 13 amps per extension lead, the fuse in the plug is going to trip. If you wire directly into the ring main, you will fall foul of the regs. because it is a fixed installation IMVVHO.

Why choose a 40 amp cable when you only need to carry 13 amps (unless voltage drop is problem) ???

Best wishes

Martin
Reply With Quote

  #10   Ban this user!
Old 09-10-2007, 01:44 PM
thkoutsidthebox's Avatar  
Join Date: Nov 2006
Location: Ireland
Posts: 1,698
thkoutsidthebox is on a distinguished road

Originally Posted by martinw View Post
Dear thkoutsidethebox,
I have no idea how long this extension lead is going to be, or what size load you will have in your shed. As a result, I do not know if voltage drop might be a problem. The temporary arrangement you described was going to connect via a plug-in RCD to a 13 amp socket in the house. If your total load is greater than 13 amps per extension lead, the fuse in the plug is going to trip. If you wire directly into the ring main, you will fall foul of the regs. because it is a fixed installation IMVVHO.

Why choose a 40 amp cable when you only need to carry 13 amps (unless voltage drop is problem) ???
Best wishes
Martin
Hi again,

We're talking MAX 40 feet, probably shorter depending upon which window I bring it into the house.

Regarding load, I will have two (2) extension leads, each plugged into a seperate socket in the house, and each lead will have a 4 gang socket set at the shed end. Giving me total 8 sockets in the shed.

The first set of 4 sockets will always be used for the cnc machine. i.e: Computer, Monitor, Spindle & Controller. I have been using a 4 gang extension cord from a single plug for this now for months, so I know they're allright on a 4 gang socket set to a 13amp mains.

The second set will be used for whatever tool Im working with at the time, the most power hungry of which I believe to be my 3HP Router. At most two of these sockets will be used at once. i.e One tool, and one shop-vac connected to tool. Shouldn't ever exceed 13 Amps.

So, If I could find the same cable as the one you mentioned in 15Amp or similar, it'd be great, but when I did a google search for the designation number you mentioned above, the hit I got in Radionics says 40Amp. Too much, and probably more expensive than necessary, but what you gonna do, Im not an electrician, and don't know what to search for.

Any help finding the same cable with a smaller amperage is appreciated.

All I need is it to take 13Amps and be fine sitting on the ground in the rain.

Neither end will be in the rain, just a length in the middle from house to shed.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 09-10-2007, 01:54 PM
thkoutsidthebox's Avatar  
Join Date: Nov 2006
Location: Ireland
Posts: 1,698
thkoutsidthebox is on a distinguished road

CANCEL MY LAST!

I just found this:

http://www.radionics.ie/cgi-bin/bv/r...eID=ienetscape
Reply With Quote

  #12  
Old 09-10-2007, 02:28 PM
DareBee's Avatar
Monkeywrench Technician
 
Join Date: Jan 2004
Location: Stratford, Ont. Canada
Posts: 2,783
DareBee is on a distinguished road

It is highly recomended that you use some sort of GFCI device on each socket at the house that you will be plugging into. You can get in-line units such as these http://www.danielwoodhead.com/pdf/ne...s/saftchek.pdf rated for 220V.
__________________
www.integratedmechanical.ca
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
3-Axis Machine tension cord freddean2006 DIY-CNC Router Table Machines 8 06-18-2007 10:52 PM
Storing a K2 Out in the Shed.. GuitarEng Commercial CNC Wood Routers 5 12-09-2006 01:38 PM
Anyone own a waterproof caliper carbidecraters Calibration & Measurement 11 10-24-2006 05:46 PM
Extension Cord dneisler Welding, Brazing, Soldering, Sealing 4 01-13-2006 07:29 PM
Rc stuff for sale, cleaning out my shed!!! Apples Hobby Discussion 0 08-25-2005 04:05 PM




All times are GMT -5. The time now is 09:01 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361