Differential vs Earth Leakage Detector

Hi everyone,
I do my own electrics and just finished wiring my own house including the switchboard so in general I am quite comfortable with electrics but I am not an electrician. I do however, have a doubt regarding the operating principles of electrical safety devices.
(a) In Australia we used to use (and imagine they still do) a device called an Earth Leakage Detector. If I understand correctly, when a device has a fault there can be but not always, electricity flowing back along the earth wire which is detected by the earth leakage detector and this trips the system telling you there is a fault. Is this how it functions?
(b) Here in Europe they use a device called a Differential. If I understand correctly, AC current comes along the active wire enters into the appliance and completes the circuit via the neutral wire and no matter what happens to the appliance (no load or heavy load), there is always an equal relationship between the active and neutral wires. If there is a problem such as current going to ground (returning back along the earth wire) then this will create a difference between the active and the neutral wires which then gets detected by the Differential which trips the circuit. Is my understanding of this one correct?
I am assuming that a Differential and an Earth Leakage Detector are two different things. Can someone please put me straight on these points?
Thanks
Reply With Quote

  #2  
Old 09-06-2007, 08:23 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by skippy View Post
(b) Here in Europe they use a device called a Differential. If I understand correctly, AC current comes along the active wire enters into the appliance and completes the circuit via the neutral wire and no matter what happens to the appliance (no load or heavy load), there is always an equal relationship between the active and neutral wires. If there is a problem such as current going to ground (returning back along the earth wire) then this will create a difference between the active and the neutral wires which then gets detected by the Differential which trips the circuit. Is my understanding of this one correct?
I am assuming that a Differential and an Earth Leakage Detector are two different things.
The Differential works the way you surmised, Although you could also make an earth leakage detector that did not operate on the differential method, I don't think it would be as practical as you would probabally have to monitor ground current which may difficult to do, my guess is they are the same thing.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 09-06-2007, 08:27 AM
 
Join Date: May 2004
Location: Australia
Posts: 541
skippy is on a distinguished road

Thanks Al !
Reply With Quote

  #4   Ban this user!
Old 09-12-2007, 05:24 AM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

The Earth leakage devices were the older style of protection, as you mentioned they measured the current in the earth conductor and once it was over a certain level (generally 30 mAmps) it would trip. This is fine but in most installations the earth conductors are bonded at various points to things like water pipes, steel frames whatever, which can have harmless circulating currents causing nuisance trips, which is what used to happen (yes I am an electrician).

The newer style is what we (in Australia at least) call an RCD or residual current device, or what you are calling a differential device, as you mentioned the neutral and active of a circuit are monitored and any difference between the two over the trip point (still usually 30 mAmps) and the device trips. These are much more reliable and in fact I think you would be (un)lucky to get one of the original style earth leakage devices, though a lot of people, including electricians still refer to them as such.

If you are doing your own wiring, (not that I condone this in any way...end disclaimer), please be familiar with your earthing system, I don't know what system is used where you are but there are a few different types in use around the world, we use the MEN system here, if that is the system used there please make sure you know what you are doing, if it isn't setup correctly and with certain fault conditions you can get situations where everything metallic in your house is at mains potential !!! This can also happen with other earthing systems, even with RCD's installed.

Cheers.

Russell.
Reply With Quote

  #5   Ban this user!
Old 09-17-2007, 05:13 PM
 
Join Date: May 2004
Location: Australia
Posts: 541
skippy is on a distinguished road

Hey Russell,
thanks for putting me straight on this on. With regards to Earthing systems, here I have all the earths collecting in one point above the switchboard using a bridge type contraption (don't know the name in English) so that each earth wire can be easily disconnected to see where a problem is (measure current going to ground) and from there the main earthing cable is connected to: (a) a 1.5m copper spike in the garden (yard) and (b) the reinforcing bar within the concrete walls. Sounds very good but in saying that we got a new washing machine some weeks ago and when I installed it I was sitting on the floor with my sweaty legs touching the tile floor, I plugged it in and each time I touched the back panel of the washing machine (galvanised steel panel) I would get a decent tingle. Touching the earth pin of any of the electrical sockets in the same circuit with the washing machine plugged in and a moist finger would also give me a small boot. Unplug the washing machine and no shock could be felt. I then put an extra cable between the washing machine cable and the wall socket and disconnected the earth wire and ran it through my multimeter (amperage) but didn’t discover anything of substance. When standing (instead of sitting on floor) no shock could be felt either. I know my earth system is working and has continuity and the right size cable, etc. and I have a 30mA Differential and that doesn’t trip even though it’s wired correctly and tests correctly. Conclusion: Don’t know but just don’t sit on the floor with sweaty legs and touch the washing machine body when it’s plugged in.

“If you are doing your own wiring, (not that I condone this in any way...end disclaimer),.....”

It was funny when I first came to Europe (Belgium) from Australia and we rented an unfurnished apartment but unfurnished means no curtains, no light fittings (just a screw connector at the end of the two wires coming out of the ceiling). In fact in Germany it generally means no kitchen either, I kid you not! So I turn off the light switch, climb up the ladder and go to fit a socket and bulb and end up getting a decent boot. Ah, the switch is the other direction so I change it, BAM, another boot. What the hell? Turns out that instead of having an active and a neutral, the majority of the houses there (anything more than 20 years old) use a wire from each of two phases (out of the three phases in the street) and difference between them is 220v therefore when you turn off the switch, one wire of the wires in any appliance is still live. For bathrooms they use double pole switches but everything else is single pole.

I was also amazed to go into any hardware shop and see non-electricians buying three phase circuit breakers. I guess with mostly concrete and brick buildings the worst that can go wrong (apart from electrocution) is a burnt cable.... This isn’t a criticism against Belgium (or Europe) as it’s a great place. Just wanted to point out the difference in attitudes towards working with electricity. I know in Australia most people just call an electrician and are fearful of electricity whereas here most (or at least lots) would have a go themselves. In my case I’ve learned what I need to know in order to do what I have to do and I respect electricity, but by the same token I couldn’t tell you if a motor had star or delta windings.

I've been following your router build, keep up the good work!
cheers
Phil

Last edited by skippy; 09-17-2007 at 05:28 PM.
Reply With Quote

Sponsored Links
  #6  
Old 09-17-2007, 05:52 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by skippy View Post
when I installed it I was sitting on the floor with my sweaty legs touching the tile floor, I plugged it in and each time I touched the back panel of the washing machine (galvanised steel panel) I would get a decent tingle. Touching the earth pin of any of the electrical sockets in the same circuit with the washing machine plugged in and a moist finger would also give me a small boot.
Regardless of how much current you can measure, what this means is there is a potential between the Ground conductor feeding the W/M. and Earth ground.
Essentially it means that the power feeding the machine has some kind of leakage to the frame. if the frame had exactly the same potential as Earth ground, you should not experience any sensation as you are sitting on earth ground.
I would say that, either your W/M ground path has a higher than acceptable resistance back to the trip or the Earth leakage trip is not that sensitive or the ground path back to the grounded neutral has higher resistance than it should.
Does the service company provide a ground? I suspect not, in that case the ground path would be through ground back to the grounded star point of the 3 phase supply transformer, where ever that is located.
Hypothetically, think of this, if the supply transformer grounded star point was open or high resistance, sinking any amount of ground rods would be of no avail.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 09-17-2007, 09:48 PM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

Hey Phil, as Al mentioned there must be some kind of potential difference from the floor to the WM, also most people don't realise, you can still get a sizeable boot from a protected circuit - without tripping (you don't need to ask me how I know this). It is these sort of problems that can be tricky to diagnose. Also I am not familiar with the type of grounding system used there and in any case there are too many variables to help via forum...things that are unrelated may be to blame, broken neutrals can play havoc with earthing systems, and the fault may not even be with your wiring, possibly next door may have a fault, it can happen.

As a rule electricians will use a "Megger" which does two things, measure continuity (low ohms) and insulation. It does a better job than a multimeter for earth cont. and for insulation will test using up to 1000Volts (typically, they do go higher), this makes finding faults a lot quicker/accurately.

Cheers.

Russell.
Reply With Quote

  #8  
Old 09-17-2007, 09:59 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Many years ago in the UK, using a low resistance Megger we had to measure the complete ground loop resistance using the neutral back to the star point back through ground to the ground conductor, whether Ground rod or metalic water supply pipe.
With the common use of non-metalic water supplies, E.L. Trips became more common.
The system here in N.America is slightly different, as to ground conductor supply.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #9   Ban this user!
Old 09-27-2007, 04:52 AM
 
Join Date: May 2004
Location: Australia
Posts: 541
skippy is on a distinguished road

Sorry I didn't get back here to reply in the last two weeks and thanks for your answers. Just to recap on what you're saying. I should call an electrician who is equipped with a Megger and he should be able to tell me if I have a problem or not and what exactly it is? I have to be very choosy about who I call here. An electrician came to my neighbour's house last week and had to borrow my step ladder as he didn't own one. The week before that I had to lend my 3 section ladder to a tree lopper as he only had a 2 section one and one month ago I diagnosed why my other neighbour's new electric water heater didn't work properly. (The plumber had fitted a vertical model in horizontal position therefore it never filled up with water properly due to different positioning of the inlet/outlet pipes on horizontal and vertical models). I guess you get the point!
Reply With Quote

  #10   Ban this user!
Old 09-27-2007, 05:18 AM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

It might be a good idea, I would suspect both a minor fault with the washing machine and a fault with your earthing system. Some people are a little more prone to get little tingles as well, you mentioned a moist finger, small cuts and grazes will also increase your susceptibility to getting a boot, skin acts a little like an insulator, but not a very good one.

Good luck, and you better ask when you ring if the sparky has his own tools, including a megger . I guess an electrician without a ladder is fine if he is REALLY tall ... lol

Russell.
Reply With Quote

Sponsored Links
  #11  
Old 09-27-2007, 08:00 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by skippy;
347458. An electrician came to my neighbour's house last week and had to borrow my step ladder as he didn't own one.
If he can't afford a ladder, what are the chances of him owning a Megger
Ideally he would need both types or the combined high voltage insulation type and the low resistance reading type.
One to check the WM insulation and the other the ground path resistance.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 09-27-2007, 09:17 PM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

Just about all meggers we use do both, high voltage insulation testing and low impedance testing. Also set on 500 Volts good for waking up any apprentices sleeping on the job
Russell.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Earth Ground LYN BYRD Milltronics 5 06-20-2007 11:39 AM
Red Earth,trouble With New Plasma DISCONNECTED CNC Plasma and Waterjet Machines 2 02-06-2007 09:00 PM
How on earth do I make this!!! disinformation G-Code Programing 14 10-11-2006 07:53 AM
Differential threads... Chuck Pressure General Metalwork Discussion 7 09-24-2005 11:01 AM
Google Earth ( You'll love it) ynneb CNCzone Club House 28 08-05-2005 01:13 PM




All times are GMT -5. The time now is 09:00 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361