  #1   Ban this user!
Old 04-08-2004, 09:50 PM
Swede's Avatar  
Join Date: Dec 2003
Location: United States
Posts: 383
Swede is on a distinguished road
Determining VA load

Hi everyone! As part of my VFD upgrade project, I have purchased a neat "control" transformer. This xformer accepts my 240 volt line and has a 115V secondary and a 24V tap as well.

The transformer is rated 100VA. Stupid question time (I should know this), how do I determine the acceptable load for the secondary circuits? For example, let's say I have a contactor coil that must close, 115V and 100 mA. Also, a cooling fan, 115V 500 mA. What is the formula for determining the VA loading of this combo?

Any hints appreciated. Thanks.

Swede
Reply With Quote

  #2  
Old 04-08-2004, 10:46 PM
HuFlungDung's Avatar
Moderator
 
Join Date: Mar 2003
Location: Canada
Posts: 4,825
HuFlungDung is on a distinguished road

I would just add them together:

100mA = .1 A
500mA = .5 A

24V * .1A = 2.4 VA for the coil

115V * .5 A =57.5 VA for the cooling fan

Total load= 60VA
__________________
First you get good, then you get fast. Then grouchiness sets in.

(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Reply With Quote

  #3  
Old 04-08-2004, 10:59 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

VA for 100ma @115v & 500ma @ 115v = 600ma (.6 amps * 115 ) = 69VA.
Al
Although the total VA rating is 100VA, you also need to know what the individual winding are rated at , current wise.
Al
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #4  
Old 04-09-2004, 02:59 AM
*Registered*
 
Join Date: Apr 2004
Location: Norway
Posts: 678
ESjaavik is on a distinguished road

I'll vote for Al's version.
This means you have 31VA to go.
That leaves you with 1.3 A @ 24V.
And don't count on the 115V to be isolated from the grid! It may be just a midpoint tap on the primary (autotransformer). Check that with a VOM.
Reply With Quote

  #5  
Old 04-09-2004, 08:24 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

The only problem with a multi-secondary transformer is knowing what the VA rating is for each winding, for a single secondary transformer it can be assumed that the total VA value can be used to calculate the maximum current, but with a multi secondary type, it depends on what percentage of the VA value the windings are wound for, although the voltage is decided by the number of turns, the winding must be of a sufficient diameter for the intended current.
It's not always a choice of just divi-ing up the VA between the windings.
If you have just a 24v tap instead of a separate winding, I would guess that the secondary is wound in just one gauge, which probabally means that will restrict the 24v to fairly low current, In ESjaavik's example, I would guess it would handle the 1.3amp max.
Al
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 04-09-2004, 09:14 AM
Swede's Avatar  
Join Date: Dec 2003
Location: United States
Posts: 383
Swede is on a distinguished road

Hmmm. This transformer has a primary with connections for 208V, 240V, and 277V. Since I have 240V in my shop, I'll connect the 240 across the approprite leads. On the secondary side, the full winding is 120V, and it does have a 24V tap.

To be conservative, given that the wire guage is probably constant on the secondary side, I'll multiply the total secondary load current by 120 for the VA load. This is what I suspected but I did want to double check.

Einar, the 120 is truly isolated from the primary. I think this transformer was made specifically for this type of project... turning 240V into low-current, lower AC voltages for relay actuation, etc.

I really appreciate everyone's help, many thanks.
Reply With Quote

  #7   Ban this user!
Old 04-09-2004, 05:47 PM
DR-Motion's Avatar  
Join Date: Mar 2004
Location: Ontario,Canada
Posts: 120
DR-Motion is on a distinguished road

Swede, If the 24V is a tap off the 120V output then you can be sure that it VA rating is 24/120 of the full rating. This gives 20VA available for the 24V tap with 80VA remaining on the 120V tap.

20VA divided by 24V = 833mA; 80VA divided by 120V = 666mA

If you used just the 120V output you would have the full 100VA available or 833mA.

From your description it looks like you need 600mA at 120V so a full 833mA will still be available for your 24V supply.

Remember that the VA rating is for all practical purposes the same as it power rating in watts... this transformer has enough to drive a household 100W light bulb from a 240V source.

HTMTC Gary
__________________
embrace enthusiasm to accomplish the task
Gary Davies... www.durhamrobotics.com
Reply With Quote

  #8  
Old 04-09-2004, 06:23 PM
HuFlungDung's Avatar
Moderator
 
Join Date: Mar 2003
Location: Canada
Posts: 4,825
HuFlungDung is on a distinguished road

Whoops! I mistook that for a 24 volt coil. I agree with Al
__________________
First you get good, then you get fast. Then grouchiness sets in.

(Note: The opinions expressed in this post are my own and are not necessarily those of CNCzone and its management)
Reply With Quote

  #9   Ban this user!
Old 04-10-2004, 09:59 AM
Swede's Avatar  
Join Date: Dec 2003
Location: United States
Posts: 383
Swede is on a distinguished road

Update on the transformer issue - I made a nice eBay purchase which was delivered yesterday. It was an assembly consisting of 2 ea. 4-pole contactors rated at 25 amps, another control transformer, and a 115V mechanical solenoid.

After cleaning the contacts, the contactors worked great. I think it was scrapped because the internal contacts were dirty and the continuity intermittent. Some light polishing of the contacts (they looked like brazed silver pads) restored the contactors to full use.

This was some sort of 3-phase reversing setup, meaning it has an interlock between the contactors which mechanically prevents both from closing at the same time. The whole thing comes apart as it is DIN rail mounted.

The 30VA transformer doesn't even get slightly warm, with a 500mA load (24V contactor coil). Can the temperature of the transformer be a crude indicator of load? I would assume it would heat excessively as the load approaches the limit.
Attached Thumbnails
Click image for larger version

Name:	vfd003.jpg‎
Views:	131
Size:	64.3 KB
ID:	2010  
Reply With Quote

  #10   Ban this user!
Old 04-10-2004, 10:13 AM
DR-Motion's Avatar  
Join Date: Mar 2004
Location: Ontario,Canada
Posts: 120
DR-Motion is on a distinguished road

You got it Pontiac.

Your 30VA transformer at 24V gives you 1.25A to play with, since you only use 0.5 A you have plenty of headroom. The heating of the transformer is produced by both the current passing through the coils and the heating of the soft iron core induced by the magnetic field which is proportional to the current.
You have 12 W of power going through your transformer which would not produce much of a temperaturre rise in the fairly large heatsink mass of the transformer.

electrically yours, Gary
__________________
embrace enthusiasm to accomplish the task
Gary Davies... www.durhamrobotics.com
Reply With Quote

Sponsored Links
  #11  
Old 04-10-2004, 11:46 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Swede, The thing that happens to a transformer when the VA rating is exceeded, the magnetic core reaches saturation and it can no longer transfer the energy to the secondary and excessive heating occurs.
When operating magnetic/inductive devices such as contactors etc on AC, it is important to use some kind of fuse protection due to the fact that if devices such as contactors and solenoids etc ever jam or stick preventing the armature in the device able to operate, the current goes through the roof due to the device losing impedance.
This does not occcur when using DC operated devices as the resistance remains the same whether the device picks up or not.
Al
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 04-10-2004, 04:00 PM
Swede's Avatar  
Join Date: Dec 2003
Location: United States
Posts: 383
Swede is on a distinguished road

Thank you both Al and Gary, and everyone else. Al, I like your avatar. That guy is either getting shocked, or he's seen the price tag on the CNC machine he desperately wants!

I'll stop theorizing, and get into the shop now. The first project will be to install a fuse and contactor set in my rotary coverter safety switch box as a warm-up; then I'll tackle the VFD and the mill's electrical system.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
newbie Quest. Basic Static Load on Linear Bearing Block kNewton ? Calico Linear and Rotary Motion 4 06-27-2007 06:10 PM
stepper motor load resistor and figuring out phases? drtuto General Electronics Discussion 7 03-19-2005 02:53 PM
Actual load on Ball Screw? dmgdesigns DIY-CNC Router Table Machines 6 10-22-2004 11:05 AM
Axis load meters? DAB_Design General Electronics Discussion 3 10-13-2004 08:35 PM
Spindle load meter ? Ken_Shea Haas Mills 1 10-10-2004 10:21 PM




All times are GMT -5. The time now is 08:52 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361