Limiting In-Rush Current - CNC Power Supply

I am having a problem powering my new power supply reliably. I am using a 1.5 kVA dual-coil transformer; which was initially tripping my 20A single-pole circuit breaker. I have since upgraded my circuit breaker to a high magnetics version; which is designed for starting motors, large appliances, e.t.c. This resolved the breaker issue. However, now I am blowing in-line 20A time-delay fuses in my controls box. I am considering installing a 20A thermistor directly after the fuse-block to slow the in-rush current. I know the in-rush is the problem, because I have had the system power-up a couple of times without blowing fuses. The transformer coil is HUGE, and I am guessing it is pulling some serious current at start-up to build the magnetic field. Has anybody used a thermistor to limit current on their power supply inputs?? I searched the site, and found very little information.

Thanks in advance,
Wayne
Reply With Quote

  #2  
Old 12-21-2006, 03:50 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,543
Al_The_Man is on a distinguished road
Buy me a Beer?

One simple thing you could try is power the Transformer first, and get over that inrush, then power the output of the bridge, This way you do not get the double whammy of Transformer and Electrolytic inrush.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 12-21-2006, 06:11 PM
 
Join Date: Sep 2004
Location: U.S.A.
Age: 40
Posts: 160
snakebit95 is on a distinguished road

Hey Al,
Thanks for that suggestion. That is the way I already have it wired. I have the transformer in-front of a contactor, which is activated through the E-Stop reset button. I plan to power the transformer first, and then charge the capacitor by resetting the E-Stop. Just the transformer alone is killing the 20A fuses. I thought about installing a larger fuse........but then what good is the fuse when I am running #12 wire for standard 20A service?

Theoretically, a single 20A service line should be good for roughly 2.4 kW; which is well above the transformer rating. If I can just get past the in-rush. During my research, I found that my transformer could be pulling as much as 4X its rating at start-up; which equates to about 50A......albeit for less than 1 second. Any other ideas??

Thanks again!!
Reply With Quote

  #4  
Old 12-21-2006, 06:24 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,543
Al_The_Man is on a distinguished road
Buy me a Beer?

I would think there is some other issues there, there is no way a 1.5kva transformer should trip a 20amp breaker on its own, unloaded.
Transformer inrush is not 1 sec, more like 1/2 a cycle.
Check the transformer current when running, unloaded.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 12-21-2006, 06:28 PM
pminmo's Avatar  
Join Date: Jun 2003
Location: St. Peters, Mo USA
Age: 59
Posts: 3,325
pminmo is on a distinguished road

You probably could help yourself by using a zero-crossing switching arangement. http://www.futurlec.com/Relays/SSR80A.shtml while I haven't switched 20a, I suspect it could help. The beauty of zero crossing ssr's is you are always starting at zero crossing, where a mechnical switch you can start at the phase peak or anywhere in the phase cycle, plus the mechanical contacts bounce.

But, I can't say I think it's wise to run your load on a 12ga, 20a circuit. A 30A circuit with 10ga wiring and devices is probably the real solution.
__________________
Phil, Still too many interests, too many projects, and not enough time!!!!!!!!
Vist my websites - http://pminmo.com & http://millpcbs.com
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-21-2006, 06:38 PM
 
Join Date: Jun 2005
Location: UK
Posts: 180
Haydn is on a distinguished road

I used an NTC thermistor in my supply to limit inrush and it seems fine. In my circuit I put the thermistor across a time delay relay (rated 30A), when I power on the thermistor is in the circuit for about 1 sec or less, the thermistor is then removed from the circuit when the relay switches over. If I hit e-stop the thermistor will be cold and will work properly when I restart the system. This can be done using a high wattage resistor as well, I have seen people do this but if the relay fails the resistor stays in the circuit and messes with the supply before eventually going pop or catching fire (unless you use a resistor about the size of a brick).

Here is a pick of the ntc in my controller.
Attached Thumbnails
Click image for larger version

Name:	controller.jpg‎
Views:	166
Size:	147.3 KB
ID:	27687   Click image for larger version

Name:	thermistor.jpg‎
Views:	144
Size:	158.3 KB
ID:	27688  
Reply With Quote

  #7   Ban this user!
Old 12-21-2006, 08:56 PM
 
Join Date: Sep 2004
Location: U.S.A.
Age: 40
Posts: 160
snakebit95 is on a distinguished road

Al,
Are you sure only 1/2 a cycle on the in-rush? The couple of times I did get the transformer to power-up without blowing a fuse, I could hear a very faint high-pitched hum that quickly faded-out (maybe 2 seconds long). I am guessing this could be the wires/coils resonating while the field was building? I did check the output when it powered-up, and it checked within a volt or so of the advertised output (40V @ 37.5A)......so I know it works. If it is of any help, I have a Hammond transformer part #182V40. Please let me know what you think.

Phil,
When I started this project, I would have never guessed that I would have needed more than a 20A circuit to run this power-supply. The general calculations just did not show it. Of course, I had no idea that the in-rush would be so large. You know what they say about hind-sight. Going to a 30A circuit creates other problems, such as finding electrical plugs and receptacles that are adequately rated to handle 120V @ 30A.

Haydn,
That is one very nice looking layout!! That is also a great idea on the time-delayed relay. I ordered some thermistors today to try, and may go the same route you did to allow time for the thermistor to cool.....and to also eliminate the slight voltage-drop. I want to see that the thermistor will resolve my problem before I throw any more money at it.

Thanks for everybody's feedback!! I am ready to get this machine cutting chips!!!
Reply With Quote

  #8   Ban this user!
Old 12-22-2006, 12:33 PM
 
Join Date: Jun 2005
Location: UK
Posts: 180
Haydn is on a distinguished road

Thanks for the comment Snake, I don't think i'd try and fit it all in a 4U rack case again! Good luck.
Reply With Quote

  #9  
Old 12-22-2006, 01:44 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,543
Al_The_Man is on a distinguished road
Buy me a Beer?

This is a fix from PowerTronix, I would imagine if you put the relay on the secondary instead, it should provide a bit more delay, it looks like the delay is the pick up time of the relay.
So far I haven't had this problem to worry about, I mainly use Plitron, I don't know wether they have slightly different characteristics.
http://powertronix.com/html/in-rush-protection.html
2 secs. seems a heck of a long time.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 12-22-2006, 02:10 PM
 
Join Date: Aug 2004
Location: US
Posts: 2,786
ViperTX is on a distinguished road

SSR's are not the answer.....most are not true zero crossing.....they are basically triacs....so, they will be turning on and off at near every AC crossing cycle.

It is not the transformer that's causing the problem....it is most likely the capacitors on the output.....when discharged they look like almost a dead short....that is the reason that you are sometimes able to power up without any problem....the cap's are partially charged.
Reply With Quote

Sponsored Links
  #11  
Old 12-22-2006, 02:34 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,543
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by ViperTX View Post
It is not the transformer that's causing the problem....it is most likely the capacitors on the output.....when discharged they look like almost a dead short....that is the reason that you are sometimes able to power up without any problem....the cap's are partially charged.
Post #3 says it is on transformer power up only.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 12-22-2006, 03:17 PM
 
Join Date: Jun 2005
Location: UK
Posts: 180
Haydn is on a distinguished road

Originally Posted by ViperTX View Post
SSR's are not the answer.....most are not true zero crossing.....they are basically triacs....so, they will be turning on and off at near every AC crossing cycle.

It is not the transformer that's causing the problem....it is most likely the capacitors on the output.....when discharged they look like almost a dead short....that is the reason that you are sometimes able to power up without any problem....the cap's are partially charged.
The relay I used is not an SSR and it is on the secondary, reason being as Viper says, the inrush is almost all caused by the dead short of the filter cap when its discharged. I know inrush is a short lived affair but setting my time delay relay to 1sec isnt a problem for me, switch on, blink and everythings fine (it may be set lower I cant remember).

Looking at the pic it looks like its set to about 0.6s
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 09:19 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361