Power Setup for Home Shop

Howdy,

I'm sorry if this is a stupid question... here we go...

I'm shopping for a new home and one of my concerns is to have a nice space for the workshop and adequate power. I'll probably have 1/2 a full walkout basement which should be enough to (after the finances get back on track) get a full size used mill, lathe, and a 60-Amp plasma cutter and eventually DIY CNC them.

I figure I would plan ahead and see if I can get 3-phase in there, but since I never messed with it before I'm unsure if I should ask for 3-phase 230V or 460V. Not even sure if 460V is available in residential areas Would have 3-phase 230V give me a leg up when it comes to running used machinery I may pick up at auction or some other place later or is it a waste? What amperage would be good for a couple of beefy machines?

I'll try to get a couple of 240V circuits and one or two 120V circuits as well. I figure 20 Amps for the 120V. What amperage should I go for the 240V?

Do I need to get a 60-Amp 240V line for the cutter which is rated at 60 Amps... not sure... that sounds like a lot!

Thanks!

Reply With Quote

  #2   Ban this user!
Old 10-07-2006, 04:35 AM
Karl_T's Avatar  
Join Date: Mar 2004
Location: Dassel,MN,USA
Posts: 1,318
Karl_T is on a distinguished road

You're extremely unlikely to find 3 phase in a residential area.

Just make sure you have a 200 amp sevice (standard) and an electrical box with a huge area for adding more circuit breakers.

Tell the electrician you want a 60 amp welder here, a 50 amp air compressor there, and a 50 amp ? there, etc. Put in plenty, very hard to wire after sheetrock is up.

You'll end up running 3 phase equipment off a three phase motor/converter. You can build it yourself. My shop is the baesment and tuck under garage - sounds about like what you're doing. I only run one 3 phase machine at a time ( out of 8) off a 220 V 30 amp circuit.

Karl
Reply With Quote

  #3  
Old 10-07-2006, 05:35 AM
diarmaid's Avatar
*Registered*
 
Join Date: Apr 2006
Location: Alaska
Age: 35
Posts: 1,257
diarmaid is on a distinguished road

I contacted my electricity supplier last year about getting a 3 phase connection in my house for a workshop (Residential area) and they said that it was no problem, and sent me the form. The cost was €800 (About $1000). Of course this is Ireland, so it may be different where you are, and Im near the capital city so the necessary networks were probably already in place in the area. I ended up not getting it done because we were going to move house and didn't want someone else to have the luxury of my €800 expense!!
Reply With Quote

  #4   Ban this user!
Old 10-07-2006, 07:12 AM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

Speaking as a sparky, although your system is different to what we have here, maybe consider getting a sub board installed in the workshop area, makes for easier additions later on, closer to reset tripped breakers without affecting the rest of the house... just a thought.

Russell.
Reply With Quote

  #5  
Old 10-07-2006, 10:11 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,543
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by diarmaid View Post
I contacted my electricity supplier last year about getting a 3 phase connection in my house for a workshop (Residential area) and they said that it was no problem, and sent me the form.
Yeah, your fortunate that probabally like the UK, residential areas have three phase distrubution, (one phase per dwelling), so it is relatively easy to bring in three phase, unlike N. America that uses single phase only for residential areas.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 10-07-2006, 06:19 PM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

Originally Posted by Al_The_Man View Post
Yeah, your fortunate that probabally like the UK, residential areas have three phase distrubution, (one phase per dwelling), so it is relatively easy to bring in three phase, unlike N. America that uses single phase only for residential areas.
Al.
So your residential distribution uses one phase ? How big an area are we talking (on average) per phase, seems like that would make it hard to get even distribution of load using that approach (from a supply point of view).

Do you have floating neutral problems often by any chance ?

Russell.
Reply With Quote

  #7   Ban this user!
Old 10-07-2006, 08:00 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,565
Geof will become famous soon enough

Originally Posted by epineh View Post
So your residential distribution uses one phase ? How big an area are we talking (on average) per phase, seems like that would make it hard to get even distribution of load using that approach (from a supply point of view). Do you have floating neutral problems often by any chance ? Russell.
I don't know how they work it in Al's area but we have three phase 7200volts running down the street. Every so often a domestic supply 50kva transformer is tapped between one phase and ground. The transformer secondary is center tapped to give 240/120 with the neutral again at ground. It seems four or five houses are supplied by each transformer with a typical house supply in our area 100amps; newer houses are normally 200amps.

So I have three phase about 180 feet from my home workshop but the last time I enquired about getting a three phase supply I was told that mixed service; single phase and three phase is not provided to a single location and three phase is not supplied to a residential address.

What's a floating neutral? Our neutral is obviously the ground and considering I live on an island in a river delta about 10 inches above high tide I am almost floating but I don't think that is what you mean
Reply With Quote

  #8   Ban this user!
Old 10-07-2006, 11:13 PM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

Originally Posted by Geof View Post
What's a floating neutral? Our neutral is obviously the ground and considering I live on an island in a river delta about 10 inches above high tide I am almost floating but I don't think that is what you mean

Lol yeah that isn't what I meant, sounds like your distribution is "same but different" to what we have. Transmission is usually done at higher voltages (here street HV is 22 000 Volts) to cut down on losses caused by conductors carrying current, basically the higher the voltage the lower the current for the same given power.

Our setup is generally 3 phase HV (22000) using three phase Trannies (not the cross dressing type ) of whatever size 50-500 KVA and 3 phase and neutral LV (415 between phases, 240 between phase/neutral) distribution along the streets, be it domestic or industrial.

By floating neutral I meant that sometimes when a supply grid or large installation has a major imbalance on one or two phases (usually overloaded) the neutral point can tend to "float", causes havoc with 3 phase and single phase equipment, in worst case neutral can burn away, causing all sorts of fun stuff, water pipes becoming "live", anything metallic and previously grounded is at line potential.

Happened at my sisters place recently after our last cyclone (google cyclone Larry), combination of neutral burning out and 300km/hr winds disconnected the neutral to the house (overhead connection), as she had 2 phases coming in to the house with no neutral, when power was restored (1 week later), she noticed something strange going on with the power, went to check breakers and got booted from the metallic switchboard. Blew 2 computers, air conditioners and so on, basically they were on something between 240 and 415 volts, not good.

That is the basic version of what I meant, I could go on but I think I have hijacked Ed's thread enough, sorry bout that Ed...

Russell.
Reply With Quote

  #9  
Old 10-08-2006, 09:32 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,543
Al_The_Man is on a distinguished road
Buy me a Beer?

Russell , As you are an Electrician from down under, out of curiosity I have a question regarding Grounding there for you.
In Australia does the service company provide a Ground conductor, or do you have to set a local one up, isolated from the neutral?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.

Last edited by Al_The_Man; 10-08-2006 at 10:23 AM.
Reply With Quote

  #10  
Old 10-08-2006, 10:10 AM
Gold Member
 
Join Date: Nov 2005
Location: USA
Age: 69
Posts: 440
Adobe Machine is on a distinguished road

Most residential in the Southwest "bond " the neutral to the ground, and on new housing, the ground can be attached to rebar in the slab.
There can be a situation where a neutral floats if there is poor bonding, or the neutral is lost to the power company ( wind etc ) and as stated pure havoc ...will go through water heaters, pipes , even water..happened to me years ago in the shower..still carry scars.
For a price ($12000.00), plus the cost of wiring from the transformer to the home shop, about another $3500.00 we could have 3 phase in our new home. Those VFD and phase converters work real well for a home shop !

Adobe (old as dirt)
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 10-08-2006, 05:16 PM
 
Join Date: May 2006
Location: Australia
Age: 40
Posts: 2,205
epineh is on a distinguished road
Buy me a Beer?

Originally Posted by Al_The_Man View Post
In Australia does the service company provide a Ground conductor, or do you have to set a local one up, isolated from the neutral?
Al.
Hi Al, we have a system called MEN or multiple earth/neutral. Basically an active and neutral comes in off the street overhead or underground, there is an earth stake usually at or near the switchboard installed by the installing electrician, the conductor from this connects directly to the neutral at the MEN point. Usually we have a equipotential bond to the incoming water service, at the hot water system, though plastic pipes are taking over...

Russell.
Reply With Quote

  #12  
Old 10-08-2006, 05:31 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,543
Al_The_Man is on a distinguished road
Buy me a Beer?

Russel, Thanks, I presume the star point (neutral) at the distribution transformer is grounded?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 09:11 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361