    Hello all, I am starting a project...putting motors onto my manual router table. I am going to use a hobby cnc driver and someone gave me a transformer to use but I can't find any information on it and am wondering if it is going to work. I will post links to some pictures of it...or maybe put them here if I can figure out how to do that!

    Thanks,

    Dave
    Oh yea, I am doing three motors probably under 200 oz.
    http://metalshop.homestead.com


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    19112
    Downloads
    0
    Uploads
    0
    First you need to find the primary winding, probably the two black wires, the winding should be the innermost one.
    Do a continuity test to see which windings are connected or separate from each other.
    Apply 120v to it and check the voltage on all the other windings.
    The VA rating of the transformer is basically a result of total core size of the transformer and the current capability of the windings.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered
    Join Date
    Aug 2007
    Location
    usa
    Posts
    65
    Downloads
    0
    Uploads
    0
    Thanks for that. Is there a way to measure what the amps are on this transformer?

    Dave
    http://metalshop.homestead.com


  4. #4
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    19112
    Downloads
    0
    Uploads
    0
    No definitive means, you can generally go by the physical size to get an idea of the VA.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #5
    Registered KOC62's Avatar
    Join Date
    Mar 2009
    Location
    Canada
    Posts
    277
    Downloads
    0
    Uploads
    0
    To further what Al said, the VA is also related to the temperature rise of the transformer. This has to do with the maximum internal core temperature.

    One could arrive at a reasonable current rating based on the maximum core temperature, but this would assume one has the proper equipment and transformer knowledge to make a test setup.


  • #6
    Registered
    Join Date
    Aug 2007
    Location
    usa
    Posts
    65
    Downloads
    0
    Uploads
    0
    OK, I think I got my power supply up and running. This transformer actually had 5 secondary coils. the voltages were:
    3.7
    9.3
    12.0
    18.9
    35.4

    I went with the 18.9 and after running it through the capacitors, it came out to 25.1 Volts.

    The store where I got my capacitors didn't have too much selection so I put two 4700 uF capacitors together. That was the largest they had...I feel like I should have gone with three though??

    Here is a picture of what I set up:




    Oh yea...one other question. I decided to try it out immediately so I hooked it up to my 24 volt computer cooling fan. It instantly fried it. Think that shows something wrong with my setup, or are their tolerances that tight...or maybe I shouldn't have had the two wires together...I have run that fan on 12 volts before?

    I am afraid I know just enough electric to get me in trouble!

    Dave
    Last edited by drescher3; 04-20-2012 at 08:08 PM.
    http://metalshop.homestead.com


  • #7
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    19112
    Downloads
    0
    Uploads
    0
    Computer fans are usually 12vdc, if ran off the PC P.S.?
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #8
    Registered
    Join Date
    Aug 2007
    Location
    usa
    Posts
    65
    Downloads
    0
    Uploads
    0
    well, it said 24 vdc on it...so I thought one more volt wouldn't hurt it! I am not sure where it came from...
    Last edited by drescher3; 04-20-2012 at 01:01 AM.
    http://metalshop.homestead.com


  • #9
    Registered KOC62's Avatar
    Join Date
    Mar 2009
    Location
    Canada
    Posts
    277
    Downloads
    0
    Uploads
    0
    I couldn't fully follow your transformer wiring.

    From your photo I count 9 secondary wires (some hidden?);
    2 blue, 2 grey, 2 red, 2 brown and one black, and two primary wires - black.

    You list 7 secondary voltages.

    Any of the wires a center tap?
    Are all secondary wires the same wire gauge?
    Any idea which equipment the transformer might have come from?


  • #10
    Registered
    Join Date
    Aug 2007
    Location
    usa
    Posts
    65
    Downloads
    0
    Uploads
    0
    Sorry about that...the 25.1 I had listed there was the final voltage...so I edited the post. Yes all the secondary wires are the same gauge. The black one formed a circuit with the orange ones...does that mean it is a center tap?

    I believe it came out of a stereo system.

    Dave D
    http://metalshop.homestead.com


  • #11
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    19112
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by drescher3 View Post
    The black one formed a circuit with the orange ones...does that mean it is a center tap?
    Dave D
    Measure the AC between the ones that have continuity and you can tell the centre taps from this.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #12
    Registered
    Join Date
    Aug 2007
    Location
    usa
    Posts
    65
    Downloads
    0
    Uploads
    0

    Smile

    It was very late when I posted the transformer voltages I went back and edited them to be right! Here are the values before and after the rectifier and capacitors:

    Grey-grey 3.7 4.4
    orange-black 9.3 12.0
    red-red 12.1 15.9
    orange-orange 18.9 25.1
    blue-blue 35.4 47.4

    Dave D
    http://metalshop.homestead.com


  • Page 1 of 2 12 LastLast

    Similar Threads

    1. Ferroresonant transformer for power supply?
      By DennisCNC in forum General Electronics Discussion
      Replies: 3
      Last Post: 09-04-2012, 11:22 AM
    2. Transformer for servo motor power supply
      By robhrzic in forum Servo Motors and Drives
      Replies: 2
      Last Post: 08-17-2007, 01:04 PM
    3. Power Supply Transformer Question
      By snooper in forum General Electronics Discussion
      Replies: 4
      Last Post: 07-30-2006, 05:38 AM
    4. control transformer to power supply?
      By bobleecnc in forum General Electronics Discussion
      Replies: 8
      Last Post: 05-19-2006, 09:42 PM
    5. Microwave transformer built power supply
      By TinkerDJ in forum General Electronics Discussion
      Replies: 64
      Last Post: 08-13-2005, 07:19 AM

    Posting Permissions



    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.