    wiring contactor

    help needed to wire a contactor with an on and off switch have tried different combinations but cannot seem to get it to latch and stay on .Any help would be much appreciated.


  2. #2
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    If you are using a momentary P.B. to pick the contactor up, you need a N.O. aux contact on the contactor that is wired in parallel with the P.B.
    If you have a latch type E-stop button or similar, you do not need a latch contact.
    For the first example you would also need a stop or N.C. Stop P.B.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  3. #3
    Registered
    Join Date
    Jan 2006
    Location
    uk
    Posts
    12
    Downloads
    0
    Uploads
    0
    hi al
    my contactor has L1 L2 L3 20NC and A1 on top T1 T2 T3 22NC and A2
    any chance you could do me a small diagram of conections thanks

    John


  4. #4
    Registered
    Join Date
    Jan 2006
    Location
    uk
    Posts
    12
    Downloads
    0
    Uploads
    0
    forgot to add my switch has pb start and pb stop also has a light in centre .

    john


  • #5
    Tinkerer
    Join Date
    Nov 2009
    Location
    USA
    Posts
    2,310
    Downloads
    0
    Uploads
    0
    L1, L2, & L3 tie directly across to T1, T2 & T3. A1 & A2 are for locking the coil therefore completing the circuits. What is the voltage of the coil/contactor? Are you using it for 220V or 120v or something else? Is your PB start momentary? Do you have a latching Estop?


  • #6
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    If you have a dual stop/start PB station then you need to wire a N.O. aux latching contact on the contactor in parallel with the start P.B.
    See CRM example in the PDF.
    Al.
    Attached Thumbnails Attached Thumbnails wiring contactor-controlexample.pdf  
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #7
    Tinkerer
    Join Date
    Nov 2009
    Location
    USA
    Posts
    2,310
    Downloads
    0
    Uploads
    0
    This was a picture of me during the set up of mine. It now functions in this sequence. Flip on power (energizes the incoming side of the contactor, if the E Stop is out it also enables power to the momentary switch) upon pressing the momentary switch the contacts are closed allowing power thru all L1-T1 connections etc. A2 gets fed off of the T side thru the E stop switch. Press the E Stop no power to the coils, all power is off.
    Attached Thumbnails Attached Thumbnails wiring contactor-imageuploadedbytapatalk1329928110.983648.jpg  


  • #8
    Registered
    Join Date
    Jan 2006
    Location
    uk
    Posts
    12
    Downloads
    0
    Uploads
    0
    dont have a no on my contactor it is nc which is connecter 21 top and 22 on the bottom


  • #9
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    What make of contactor? many of the DIN style have the option of clipping N.O./N.C. auxiliary contacts on the front.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #10
    Registered
    Join Date
    Jan 2006
    Location
    uk
    Posts
    12
    Downloads
    0
    Uploads
    0
    coil is 220 vlts and pb start is momentary.


  • #11
    Community Moderator Al_The_Man's Avatar
    Join Date
    Dec 2003
    Location
    Canada
    Posts
    18,930
    Downloads
    0
    Uploads
    0
    Quote Originally Posted by johnmb View Post
    pb start is momentary.
    Thats normal on a dual PB station.
    That is why you need the retaining contact.
    Al.
    CNC, Mechatronics Integration and Custom Machine Design (Skype Avail).

    “Logic will get you from A to B. Imagination will take you everywhere.”
    Albert E.


  • #12
    Registered
    Join Date
    Jan 2006
    Location
    uk
    Posts
    12
    Downloads
    0
    Uploads
    0
    schnieder contactor LC1K090107


  • Page 1 of 2 12 LastLast

    Similar Threads

    1. Huanyang VFD and magnetic contactor
      By X2cnc in forum Phase Converters and VFD
      Replies: 3
      Last Post: 02-19-2012, 11:08 PM
    2. Need Help!- Contactor Source wanted
      By capngene in forum Fanuc
      Replies: 2
      Last Post: 11-19-2011, 04:07 PM
    3. Need Help!- Fuji SRX3631-5-1/X Magnetic Contactor Wiring?
      By Fastest1 in forum General Electronics Discussion
      Replies: 2
      Last Post: 04-13-2011, 04:31 PM
    4. What's that gizmo across the contactor coil?
      By jrlandau in forum Bridgeport and Hardinge Mills
      Replies: 1
      Last Post: 01-21-2011, 12:53 PM
    5. Contactor help ????
      By Fabric8r in forum General Electronics Discussion
      Replies: 1
      Last Post: 05-26-2006, 06:27 PM

    Posting Permissions


     


    About CNCzone.com

      We are the largest and most active discussion forum from DIY CNC Machines to the Cad/Cam software to run them. The site is 100% free to join and use, so join today!

    Follow us on

    Facebook Dribbble RSS Feed


    Search Engine Friendly URLs by vBSEO ©2011, Crawlability, Inc.