220 to 400 V Transformer

Is there a transformer available to step up from 220 to ~400V 3 phase? I got a plasma cutter and it uses 400V.
__________________
Dennis
Reply With Quote

  #2  
Old 11-10-2005, 01:47 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

First check if it runs 400 or is it 460? If made for the N.american market it is usuall 460.
Many Plasma cutters have voltage option taps, some even have automatic voltage selection (Hypertherm).
You can run a 460 to 220 transformer 'backwards' but most manufacturers have a de-rating factor if used this way.
Hammond Transformers could have what you are looking for.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 11-10-2005, 01:54 PM
DennisCNC's Avatar  
Join Date: Aug 2005
Location: Clearwater, FL US
Age: 29
Posts: 816
DennisCNC is on a distinguished road

It says 400-460 its either 400 to 460 / 400 or 460.

Al, thanks I will look in to Hammond
__________________
Dennis
Reply With Quote

  #4   Ban this user!
Old 12-10-2010, 07:38 PM
 
Join Date: Sep 2010
Location: Canada
Posts: 65
torinwalker is on a distinguished road
7.5kva 600 to 120/240 single phase in reverse?

I found a 7.5kva 600 --> 120/240V transformer for $80! A transformer of this size/type is just too sweet to pass up, and if I can run it in reverse, it'll be eactly what I need to run the 575V 1ph VFD that will run my 575V 3-ph mill (from my poorly endowed 240V 1ph garage)

Data on this tranformer is scarce; The manufacturer, Polygon, appears not to have a website, so I thought I might pose this question here in case anyone easily recognizes the specifications.

I've attached a picture of the unit and its specification placard. The placard shows a 600V primary and 120/240 secondary, and it shows... three taps on the primary?

Could someone confirm or deny my suspicions?

I think:

1. At 3HP max (the power of my new Ex-cell-o), I am well within the ratings of this transformer, even in reverse.
2. The secondary has two windings of 120V each that can be wired in parallel or series. (I would connect in series to use on my 240V 1ph service.)
3. The primary has three positions (taps?) of 627, 600, and 573. I would use the third tap as the output to get 575V out.

Ahh... if only I knew everything beforehand, my life would be much simpler.

Thanks (for the umpteenth time) everyone.


Torin...
Attached Thumbnails
Click image for larger version

Name:	7.5kva-single-phase-xformer.jpg‎
Views:	24
Size:	40.8 KB
ID:	121152   Click image for larger version

Name:	7.5kva-single-phase-xformer-spec.jpg‎
Views:	32
Size:	27.3 KB
ID:	121153  
Reply With Quote

  #5  
Old 12-10-2010, 07:55 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

I ran one for a tap dis-integrator that was about that size.
You should be OK with a 50amp breaker on 240.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-10-2010, 11:41 PM
 
Join Date: Sep 2010
Location: Canada
Posts: 65
torinwalker is on a distinguished road
Taps on the transformer

Al,

Tap disintegrator... funny.

And what about the positions of 627, 600, and 573 shown on the placard? Do you think they are taps on the primary?


Torin...
Reply With Quote

  #7   Ban this user!
Old 12-10-2010, 11:45 PM
 
Join Date: Feb 2007
Location: Singapore
Posts: 2
ashad is on a distinguished road

Please check the website

elabsp - elab Solution Provider
For
Power Electronics Tutorials
Reply With Quote

  #8   Ban this user!
Old 12-10-2010, 11:57 PM
 
Join Date: Sep 2010
Location: Canada
Posts: 65
torinwalker is on a distinguished road

ashad,

Thanks. I went through the transformer basics and, while I kinda knew all that stuff already, it did mention that mutliple taps to accomodate different voltages is a common design feature which reinforces my notion that those "positions" labeled on the placard are probably what I suspected they were: taps.

I just wanted to hear it from someone who actually knows, or at least, who knows more than I do. Electricians, particularly, probably have this stuff down pat.

I'll probably head out there on Sunday to pick up this little diamond in the rough and save myself nearly $200 on the purchase of a 5kva transformer I had originally intended to buy.

Thanks again.

Torin...
Reply With Quote

  #9   Ban this user!
Old 12-11-2010, 07:26 AM
 
Join Date: Sep 2010
Location: usa
Posts: 838
mike_Kilroy is on a distinguished road
Buy me a Beer?

You are correct; those are the 3 inputs possible; 600v nominal and +/- 5% taps around it. 600v was common for a while (not sure if it still is) in some parts of canada I think at automotive plants. we sold a lot of 600v transformers years ago to canada.
Reply With Quote

  #10   Ban this user!
Old 12-11-2010, 09:23 AM
 
Join Date: Sep 2010
Location: Canada
Posts: 65
torinwalker is on a distinguished road

Thank you, Mike.

I ran a manufacturing shop well over a decade ago and everything in that shop was 575 3-ph at least as far as the equipment was labelled. I had an electrician who would come in and drop new lines and so forth, so I never looked in the electrical room to see if it was 600V or 575V. I once wired a new 3-ph motor in delta instead of wye configuration - it only took a minute or two before it smoked and I had to have it rewound to the tune of $350. Needless to say, I'm a little more careful these days.


Torin...
Reply With Quote

Sponsored Links
  #11  
Old 12-11-2010, 10:59 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

Most machines are fairly tolerant of voltage level, ±10% is usually the accepted tolerance.
Is the VFD that you have, designed or accept the ability to run on 1 phase?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.

Last edited by Al_The_Man; 12-11-2010 at 01:52 PM.
Reply With Quote

  #12   Ban this user!
Old 12-11-2010, 07:04 PM
 
Join Date: Sep 2010
Location: usa
Posts: 838
mike_Kilroy is on a distinguished road
Buy me a Beer?

Originally Posted by torinwalker View Post
I found a 7.5kva 600 --> 120/240V transformer for $80! A transformer of this size/type is just too sweet to pass up, and if I can run it in reverse, it'll be eactly what I need to run the 575V 1ph VFD that will run my 575V 3-ph mill (from my poorly endowed 240V 1ph garage)
Torin...
Torin, you have a 1ph 575v input VFD that runs a 3ph 575V motor.... Who makes those nowadays for you guys up north? I haven.t paid attention to 575v drives for a long time!

BTW, IIRC the Ford motor company is the one who changed the 575v to 600v standard in some Canada locations and we had to change our transformers to this as the nominal with taps up/down around it for them. But they bought a hole lot of em so we didn't complain!
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On





All times are GMT -5. The time now is 10:52 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361