Power Supply/Power Cord Sizing for Four 850 oz-in Servos, One is Slaved

Power Supply/Power Cord Sizing for Four 850 oz-in Servos, One is Slaved

Could someone please give me feedback on power supply and power cord sizing? This is an aluminum machine made to cut aluminum plate. It is in a residential building connecting to 240VAC but will be moved to “light industrial” commercial space in the future. Here are some details:

I have four 850 oz-in Keiling servos.
Continuous current: 7.5 amps
Peak current: 33.5 amps

I also have
Spindle: 15 amps (3-1/4 hp router)

My gantry is 3 ft. wide weighing 215 lbs. with two servos driving it. A servo is on each side with one slaved to the other. Calculated servo inertia ratio was less than 10, with a 2:1 toothed belt reduction.

Servo cable is rated at 41 amps.

Power Supply Sizing Problem:
For a 3-servo machine, I believe a general rule of thumb that others have used is to take the peak current draw, multiply it by 3 servos and take 66% of that.

My 4-servo total current calculation for power supply sizing is:
(66% x 33.5 amps x 4 servos) + ( 15 amp spindle motor) = 104 amps

I took 12 amps off because one servo is slaved. So, 92 amps still seems like way too much for a machine with a 200 lb gantry. Life experience is telling me it’s a 65 amp machine. I don’t think it will be stiff enough to handle deeper cuts anyway. Am I off track?

In any case, I have one 1500W, 19.5 amp Toroidal power supply. The data sheet states that it can easily handle 200% overload for a few minutes. I don’t know how they come up with the 19.5 amps since it varies inversely with the voltage. So, I was planning to run it with just one power supply while checking the toroid for heat buildup. I think two of these should be enough. That will be 39 amps continuous with 78 amps for a few minutes. What do you think?

Power cord sizing should then be 78 amps + 15 amp spindle = 93 amps. In my residence, I can only get 240VAC ,50 amps. So, I’ll be limited on depth of cut until I move it to a “light industrial” commercial space. Does this sound like I’m in the ballpark and like it's going to work okay for now?

Thanks!
Reply With Quote

  #2  
Old 01-24-2012, 12:03 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

I think you are way over with your numbers, care should be taken not to run at the peak servo current, as this approaches the destruction point of the servo.
Your Toroidal P.S. will not be 19.5 amps even on 120v, even less on 240v.
It is extremely rare for all 3 motor to run all at once in continuous current mode, never mind peak current.
I think you need to revise those numbers some otherwise your cabling and fusing is going to be way over sized.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 01-24-2012, 05:49 AM
 
Join Date: Sep 2010
Location: usa
Posts: 838
mike_Kilroy is on a distinguished road
Buy me a Beer?

I'm with Al; your numbers are way way way hi.

To your question will it work with the one power supply to start - yep.

I cannot say anything about your ps being rated different at different voltages; but assuming it is 19amp cont, sounds prob ok for this machine - or maybe one more.

here is how I would add it up:

case 1
-----------
4x 7.5a*50% = 15amps for all servos
10 amps for the spindle

so 25 amps total rms required - probably worst case in the real world.

keep in mind u prob will not be running spindle at 100% load most of the time - so say 10amps for 50-70% typical load.

u do not size servos for peak; just make sure ur ps can handle the peak short term, and not all at the same time.

no one runs all 4 motors at full rms load long term at the same time so dont size to that either.

no one machines at full speed! remember ur servo drive is a dc-dc converter -- ie., power in = power out. so if you run at full amps cutting - at what, 1/4 top speed typically, then since rpm = volts, motor volts =1/4 rated. so power in is 1/4 so your 7.5amps into motor comes from only 1.8amp in! THIS is the number you should consider for sizing. so 2a*4+10spindle=18amps typical case!

this is why i say one ps is prob fine - try it.
__________________
Mike (at) KilroyWasHere.com -- machine tool servo repair, retrofit
Reply With Quote

  #4  
Old 01-24-2012, 01:49 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

You mention everything is running off of 240v?
You rate the power devices by the primary current, on 240v the 1500va transformers will not consume half of 19.5 amps, I would allow 10a delay fuse on the primaries.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 01-25-2012, 02:25 PM
 
Join Date: Mar 2010
Location: USA
Posts: 33
Plugger is on a distinguished road
Design Revision

Thanks Al and Mike!! My stress level just went down a few notches!!

Correction to previous postings: The spindle is *not* running off the power supply. (See attached Electrical Schematic in next post.) As a result, it seems the power supply should now be large enough. Also, I modified the suggested fuse values due to this and incorporated them into my schematic.

Here's my logic:
The power supply is 240VAC 1500W with 200% overload for a few minutes. Therefore, the amperage contribution of the power supply to each main is:
(1500W x 200% / 240VAC) / 2 mains = 6.25 amp

I would not normally use a 10amp delay fuse to run a 15amp spindle, but if that has been the experience of others, then I’ll give it a try. Did I interpret that right?

Further, this machine is going to be moved to a commercial space in the near future. So, I am trying to comply with NFPA 79. I believe that is the standard and the classification is “industrial machine” for use in light industrial space. If anyone with experience can check my schematic for errors, I’d appreciate it! I am trying to be error free and also use industry best practices. I don’t want an electrical inspector to shut me down or a future employee to get hurt.

I plan to use MTW (Machine Tool Wire) for the black and white conductors. Home Depot has it by the foot. If small quantities of other colors can't be found, I don’t think I am allowed to recode the termination points. I already have flexible, shielded cable for the spindle and servos. So, I really want these cables to enter the machine electrical enclosure, but I believe they will not meet color code standards either. How are others solving this problem?

Thanks!

Last edited by Plugger; 01-25-2012 at 02:43 PM. Reason: Image was too large and not uploaded by the web site.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 01-25-2012, 02:45 PM
 
Join Date: Mar 2010
Location: USA
Posts: 33
Plugger is on a distinguished road
Schematic is here.

Right click on it/ save target as and then view it. Otherwise it's too small. Sorry!
Attached Thumbnails
Click image for larger version

Name:	Electrical Layout.jpg‎
Views:	26
Size:	65.4 KB
ID:	151036  
Reply With Quote

  #7  
Old 01-25-2012, 03:00 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

You normally would have a disconnect or fused disconnect, the fusing here would be for the total panel, you would then set up subsidiary fusing from this for each of the other devices.
Attached is a typical schematic from NFPA79.
It shows 3ph set up, but the same applies for 1 ph.
You are allowed to run one colour wiring if the colour is identified at every termination point, you could use various colours of electrical tape if you wished.
The shielded cable colours will not be a problem when it is part of a jacketed cable.
If going this route for colour coding, it is best to ensure proper wire marking and documentation (control panel schematic) placed in the enclosure Document pocket or equivalent.
It also pays to follow Earth Grounding and particularly earth bonding conductors to all motor frames and metal parts of the machine Gantry etc.
The 10amp furs was for the PS not the spindle.
Al.
Attached Files
File Type: pdf NFPA79.pdf‎ (576.9 KB, 16 views)
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 03-10-2012, 10:52 PM
 
Join Date: Mar 2010
Location: USA
Posts: 33
Plugger is on a distinguished road
Safety Corrections To Previous Posts

Excellent post Al!! The information is much appreciated!!

To anyone who views this, my schematic in post #6 is NOT correct!! I cannot seem to edit or remove it. So, corrections are below. In any case, I highly recommend reading NFPA 79 to figure out how to safely build your system. It’s free to read at NFPA if you give them your e-mail. Otherwise, it’s $43 to buy. It’s great guide.

Corrections to post #5 and #6:

What I said…

“Therefore, the amperage contribution of the power supply to each main is:
(1500W x 200% / 240VAC) / 2 mains = 6.25 amp”

What I should have said or drawn in the schematic…
(1500W x 200% / 240VAC) = 12.5 amp
So a time delay fuse of 10amp in L1 and L2 should be enough. The fuses should be located just before the power supply. Additional fusing of a larger value should also be just after the disconnect in both L1 and L2.

Correction to schematic in post #6:
Neutral should not have a fuse. Neutral should not be disconnected by the main disconnect. Neutral should not be disconnected in the contactor. This is a safety issue!!
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Capacitor sizing on power supply Jackal66 General Electronics Discussion 4 05-15-2011 07:22 PM
Power supply sizing and source GWB32119 General Electronics Discussion 1 06-25-2009 03:58 PM
Sizing a power supply smoothing capacitor Monte General Electronics Discussion 2 03-09-2008 10:12 AM
power supply sizing vs. servo rating Erick Davidson General Electronics Discussion 1 06-06-2006 03:08 PM
Sizing servo power supply? bsc52001 DIY-CNC Router Table Machines 2 01-30-2004 11:20 PM




All times are GMT -5. The time now is 10:50 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361