Electrical service/build-out leased space

I need some electrical info. Maybe someone can illuminate.

I'm currently working with the landlord of my space to get the electrical wired. The space doesn't have anything right now. The building has 3 phase 4 wire 120/208 service.

I will have a cnc mill using 3 phase, woodworking equipment, and computers. So it would be ideal to have 120, 240, and 3 phase service int he space.

Here is what the landlord is offering/suggesting and I need to know if it is possible/good idea:

He will run 3 phase from an existing breaker box to a breaker box in my space. He wants us to purchase a 3 phase watt meter to put inline in between the two breaker boxes to measure our usage. He bought a 3 phase box and put in breakers for 3 phase, 240, and 120. Then I would pay for surface mounting conduit and outlets where I need them.

Can 3 phase be run from one box to another?

Can a 3 phase meter be used to measure usage when the box in our space will be using 3 phase, 240, and 120?

What don't I know that I should know about this?


I have contacted some electricians to see if they can consult on the landlords end, he will use an in-house guy that is not licensed. Then the electrician could do the rest of the work for me.
Reply With Quote

  #2   Ban this user!
Old 09-17-2011, 12:45 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,564
Geof will become famous soon enough

Al the Man is the one for a definitive answer but what you are describing is the way my building is wired. Three phase 120/208 is pretty much the standard up here.

Because you have 208 not 240 you should check that your motors can run on 208. Most can but if you have older motors you may have a small problem with reduced power and overheating.

You don't mention amperage. What size breaker and wire is the Landlord using to supply your space? A 60 amp supply would probably be adequate but 100 amp would give you the capacity for getting more machines. Less than 60 amps may give you problems with the starting surge on motors tripping the breaker on the Landlord's side.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Reply With Quote

  #3  
Old 09-17-2011, 01:41 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

As Geof suggests, I would look at the 3ph issue first and see what you can run on 208 3ph.
Some machines have an internal transformer with adjustable taps.
If you can get away with using the 208, then that leaves 120/240, you already have the 120v.
See what single phase loads are critical on 208 instead of 240v 1ph, how many do you have at 240?
If the 240v loads are not that high then a 208/240v 1ph transformer may be a possibility.
It all comes down to your power demand for any particular voltages.
The landlords way is viable, but I would also opt for the 100a service while you are at it if you go that route.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #4   Ban this user!
Old 09-17-2011, 08:37 PM
 
Join Date: Aug 2010
Location: USA
Posts: 79
curriergroh is on a distinguished road

The box he is going to mount in the space is 100A. Is the box the relevant item or is it at the other box where he is going to source ours from that matters?

I am waiting to buy a Hitachi X200 vfd (X200-022NFU) until the power is sorted. That will be paired with a Keling 2.2kw spindle that is already purchased. The spec sheet for the spindle says 220v. Is the X200 going to work on 208 3 phase?

There is currently no equipment needing 240 single phase.
I am planning for 3 20A breakers for the 120 service.

Is it possible to wire the breaker box to have 120 if its source is 3 phase?
Is a transformer needed or is it just a matter of wiring inside the box?

If you need more information let me know. Thanks for the help.
Reply With Quote

  #5   Ban this user!
Old 09-17-2011, 09:07 PM
 
Join Date: Jul 2005
Location: Canada
Posts: 11,564
Geof will become famous soon enough

The 100 amp rating is the maximum that may be fed into your box. What matters is the breaker rating on his side that is supplying your box.

Yes you can get 120 from 208 three phase. You get 208 single phase between any two lines of the three phase supply and 120 single phase between any line and the neutral.
__________________
An open mind is a virtue...so long as all the common sense has not leaked out.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 09-21-2011, 11:20 AM
 
Join Date: Aug 2010
Location: USA
Posts: 79
curriergroh is on a distinguished road

He is planning on using a 150A breaker on his end and our box is rated for 100A. Is that a problem?

I have contacted an electrician to come out and check things after the landlord has done his bit.
Reply With Quote

  #7  
Old 09-21-2011, 11:59 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

As long as there is current protection in the box your end for 100A, especially if it is going to be wired for this capacity.
Although the conductor size from his 150a to the 100A should be capable of carrying 150A.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
CNC Service manager & service positions available - Schaumburg IL Chris D Employment Opportunity 0 08-29-2011 02:02 PM
Space in Frederick MD dgapilot Mentors & Apprentice Locator 0 02-25-2008 06:58 PM
Anyone else have space issues? cxixer DIY-CNC Router Table Machines 6 10-14-2007 10:37 PM
Sub- Space Annomaly ImanCarrot General Metalwork Discussion 33 03-09-2007 07:17 AM
Paper space Model space ?? CNCadmin Autodesk Software (Autocad, Inventor etc) 10 05-29-2003 06:07 AM




All times are GMT -5. The time now is 10:42 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361