Old 09-11-2011, 10:52 PM
draughted's Avatar  
Join Date: Sep 2007
Location: australia
Posts: 206
draughted is on a distinguished road
hair stands on end when i touch the case!!!

hi guys, i have recently re-wired the control box for my machine and found once again that the hair on my arm stands on end with a very definite tickle sensation. it was one of the reasons that i re-wired so i am a little worried it is my fault in wiring.

does anyone know this to be normal. what fixes do you know of.
i have used both torroidial power-supples with full-bridge rectification as well as
switch mode supplies, and they both seem to have the same effect.
is my earthing inadaquate.

i don't want to electricute myself any more than i have to.
Reply With Quote

  #2   Ban this user!
Old 09-12-2011, 04:15 AM
 
Join Date: Apr 2011
Location: Australia
Posts: 232
aussiegazza is on a distinguished road

Try earthing the case as well.

If you must use an earth leakage detector (ELT) where you are located, a leak to earth should blow the ELT and you will know you have a short from either active or neutral.
Reply With Quote

  #3   Ban this user!
Old 09-12-2011, 04:36 AM
 
Join Date: Dec 2007
Location: Australia
Posts: 364
aarggh is on a distinguished road

This is really dangerous, if your actually getting a tickle have you inadvertantly crossed the active with the neutral? You should be able to check this with an ohmmeter from either one to the ground connection.

Have you also done a proper star earth layout (everything should be earthed!), this is critical to stop multiple earth paths and voltage differentials.

cheers,
Ian
__________________
My blog on the Jinan JCut 6090 CNC Router - http://www.cnczone.com/forums/blogs/aarggh/
Reply With Quote

  #4   Ban this user!
Old 09-12-2011, 07:55 AM
draughted's Avatar  
Join Date: Sep 2007
Location: australia
Posts: 206
draughted is on a distinguished road

yeah thanks for your concern. i go to great lenghts to star earth every thing i wire up.

with the case in question i have an earth coming from the plug socket, pop riveted to the chassis along with the earths for the three switch modes present in the case.
it could be something i have missed but i can't put my finger on it.

what was that you said about swapping live and neutral?
Reply With Quote

  #5   Ban this user!
Old 09-12-2011, 08:01 AM
 
Join Date: Apr 2011
Location: Australia
Posts: 232
aussiegazza is on a distinguished road

Originally Posted by draughted View Post
yeah thanks for your concern. i go to great lenghts to star earth every thing i wire up.

what was that you said about swapping live and neutral?
Check your wiring VERY carefully. All the way from the wall plug (check it too) to the machine's connections.

I will not tell you colours etc as they can vary (Update your OZ) over the last few decades or so.

In Oz, Neutral is connected to earth at the distribution box, and earth is run to an earth post. If you have active and neutral wrong, you can be making anything earthed LIVE. An earth leakage detector should stop this happening though. You may not have one.

Check it visually before you turn it on again.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 09-12-2011, 08:36 AM
 
Join Date: Dec 2007
Location: Australia
Posts: 364
aarggh is on a distinguished road

Originally Posted by draughted View Post
what was that you said about swapping live and neutral?
In the place we bought some time ago, we used to get a very slight "tingle" when we touched the electric kettle and the sink. It took a lengthy hot spell for it to go from a slight "static" kind of feel to a genuine shock, due to the ground drying up, as the earth wasn't properly connected to that socket, but while the ground was moist, it was enough.

I put a meter on it and it measured 125 volts roughly. The power point feeding the kettle had been wired by the previous owner, and i'm guessing he made the classic mistake of live/neutral connections relative to male/female sockets/plugs, and had transposed the active and neutral on a power point. This meant whenever the kettle was on, it was fed from neutral, while the active was connected to the earth, hence the shock!

Very simple mistake, and no doubt common, but I really can't underscore just how dangerous it is! It can put you and anyone else you care about in danger.

If you have ANY confusion at all about wiring, please ensure you google as much as you can, especially regarding earthing, and earthing stakes and their roles, as you may only get one chance. Electrical wiring really isn't hard at all, you just need a basic but good understanding of it. Also think of how others may be at risk. For example, if you'd transposed the active/neutral, and someone were walking around barefoot on a humid day, the risk of being electrocuted could be quite high. Rubber soled boots, dry air/ground, and many other factors can all mask a potentially lethal situation, that may only manifest one day when its been really hot, the earth stake may need replacing, etc, etc.

For a few bucks you can little electrical testers that plug into your socket and will light up according to whether the the cables are shorted, crossed, correct, etc. While not infallible, I would highly recommend them as a first point of helping to determine if there is a problem.

Good luck chasing it!

cheers,
Ian
__________________
My blog on the Jinan JCut 6090 CNC Router - http://www.cnczone.com/forums/blogs/aarggh/
Reply With Quote

  #7  
Old 09-12-2011, 09:21 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

You either have improperly grounded system at the machine or your supply panel system ground is defective, i.e. one side of the supply is not grounded.
It should not matter how your connections are made, a properly grounded system you should not have any potential to ground from any metallic part of the machine.
This is normally qualified by an electrician using a resistance Megger, (not a high voltage insulation type), the resistance type is used to measure earth ground path resistance.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 09-13-2011, 03:54 AM
draughted's Avatar  
Join Date: Sep 2007
Location: australia
Posts: 206
draughted is on a distinguished road

well thanks guys, i think i will be getting the electrician neighbour around to check the earthing points.

i'll keep you posted.

Last edited by draughted; 09-13-2011 at 04:35 AM.
Reply With Quote

  #9   Ban this user!
Old 09-13-2011, 07:43 AM
john_100's Avatar  
Join Date: Mar 2007
Location: uk
Posts: 413
john_100 is on a distinguished road

in water heaters and kettles its normal to have some leakage current to earth !

so the electric shocks are a warning !

are both the kettle and your machine plugged into sockets installed by the previous handy man ?
the earth connection could be missing

even when wires are in metal conduit ,an earth wire should be installed
you can have high resistance at the conduit joints

the neutral cable is connected to earth at the supply transformer
( usually the star point of a 3 phase transformer)


if your earth and neutral terminals are only connected at the transformer

the earth connection can be either a wire in the cable or the steel armour
in which case you can measure a small voltage between them
( ie the volt drop in the neutral supply cable)


earth leakage / residual current breakers monitor the difference between the live and neutral currents , usually tripping at 30mA

the mains filters inside switch mode power supplies also leak to earth
and supplies without an earth like those used with I.T. equipment
leak to the output !!!!

when you use several together its enough to feel (got the T- shirt)

John
Attached Thumbnails
Click image for larger version

Name:	mains supply.jpg‎
Views:	33
Size:	52.6 KB
ID:	141869  
Reply With Quote

  #10   Ban this user!
Old 09-14-2011, 07:01 PM
 
Join Date: Sep 2010
Location: usa
Posts: 838
mike_Kilroy is on a distinguished road
Buy me a Beer?

nobody has stated the obvious probably because it is obvious: have you put a voltmeter from that case and the other lead to a good known ground and MEASURED it? Do both AC and Dc scales.
__________________
Mike (at) KilroyWasHere.com -- machine tool servo repair, retrofit
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 09-15-2011, 08:03 AM
draughted's Avatar  
Join Date: Sep 2007
Location: australia
Posts: 206
draughted is on a distinguished road

it would seem i am in ignorance.
i asked you to elaborate on active and neutral swapping purely because i over looked the significance of it when i did the thing.

i have now taken the internal wiring back to basics and i can confirm that active and neutral were wrong at the socket and the significance is now sinking in. my basic knowledge of AC current defied the fact i don't know everything and lead me to believe the two could be switched.
Reply With Quote

  #12   Ban this user!
Old 09-15-2011, 08:33 AM
 
Join Date: Dec 2007
Location: Australia
Posts: 364
aarggh is on a distinguished road

Originally Posted by draughted View Post
it would seem i am in ignorance.
i asked you to elaborate on active and neutral swapping purely because i over looked the significance of it when i did the thing.

i have now taken the internal wiring back to basics and i can confirm that active and neutral were wrong at the socket and the significance is now sinking in. my basic knowledge of AC current defied the fact i don't know everything and lead me to believe the two could be switched.
This is a surprisingly common mistake as I mentioned in my post with our power socket, it's good you found it as it can be very, very dangerous. I've also seen this happen heaps with home made power cords over the years, as people when making extensions visually get the perspective of the pins messed up and transpose active/nuetral on one end.

cheers,
Ian
__________________
My blog on the Jinan JCut 6090 CNC Router - http://www.cnczone.com/forums/blogs/aarggh/
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Just IN- Bolt together stands for router gio666 Product Announcements & Manufacturer News 3 06-03-2011 09:22 PM
Stands for heavy benchtops ?? cyclestart Benchtop Machines 3 05-18-2011 10:36 PM
pulling hair out radioman DIY-CNC Router Table Machines 15 01-05-2010 03:16 PM
New Machine Build- some x7 series inside photos,like casting,solid stands,and linear. syil Syil Products 22 10-07-2009 09:57 PM
X-3 Stands jjh122 Benchtop Machines 3 09-29-2007 12:21 PM




All times are GMT -5. The time now is 10:41 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361