three phase wiring with only a N for 120

So I am researching how to wire a warehouse that will be used with 3 phase machinery. A lot of it will be retrofitted or built from the ground up because its a maker space.

According to Wikipedia:
NEMA connector - Wikipedia, the free encyclopedia

NEMA L14 and NEMA L18 can be used with only a neutral and no ground; allowing both 3 phase 208 and 120 single phase to a machine with only 4 conductors. The problem is that while working on my mill I have had noise problems with limit switches and such.

The real question is can I get away with 4 conductors but wire the machines internally to avoid noise.

I'm aware that the are standards that include L-L-L-N-G. The reason for avoiding these is the extra cost and unavailability of 5 conductor wiring and connectors.

Also I'm not asking for safety reasons because this is a twist lock system and a NEMA standard.

Any insight is appreciated.

Thanks, Ben
Reply With Quote

  #2  
Old 08-28-2011, 09:43 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

Not sure of your final intentions, but most machinery that is three phase fed has a local 120v single phase transformer in the enclosure that has one side set up as a local grounded neutral, this must be referenced either to Earth Ground through ground rods or to the incoming service ground.
Or is this for general 120v outlets in the shop?
To avoid noise in control power, it is necessary to ground and bond all metallic parts of the system to an Earth Ground point.
http://www.automation.siemens.com/do.../emv_r.pdf?p=1
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 08-28-2011, 10:09 AM
 
Join Date: Aug 2007
Location: United States
Posts: 58
chimpera is on a distinguished road

Hi Al,I was hopping you would show up. Can I interpret your response to mean that its ok to have one conductor going to the machine act as both neutral and ground?

Thanks, Ben
Reply With Quote

  #4  
Old 08-28-2011, 11:30 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

NO NO, you will be contravening the code by using a neutral as ground, the neutral and ground can only come in contact with each other at either the service distribution point or at a local situation I mentioned earlier where a control transformer is set up in an enclosure etc.
In both instances at no point in an installation can you use ground as neutral and vice-versa.
In spite of technically being at the same potential.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 08-28-2011, 12:18 PM
 
Join Date: Aug 2007
Location: United States
Posts: 58
chimpera is on a distinguished road

So NEMA L18 connectors only have a neutral and no ground. If this is never permissible why does it exist? Basically I'm wondering if I can get away with 4 conductors on 3 phase equipment that have 120v controls as is suggested by the existence of the NEMA L18 standard. Thanks, Ben.
Reply With Quote

Sponsored Links
  #6  
Old 08-28-2011, 12:51 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

NEMA L18 is L-L-L-N where a circuit is used not requiring a ground, probably not used that often, or for devices that are double insulated as in portable power tools etc that do not require a ground conductor.
So if you require a neutral AND a ground for 120v outlets you cannot use L18.
If feeding some items such as a mill for e.g., to me the best and most common way is to feed it with 3 phase and ground and set up the local 120v 1ph grounded neutral via a 220/120v 1ph transformer as I mentioned earlier.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 08-28-2011, 04:30 PM
 
Join Date: Aug 2007
Location: United States
Posts: 58
chimpera is on a distinguished road
Red face

Is your proposed wiring
a.
L
L
L---\_1:1 transformer
G---/

b.
L
L---\_2:1transformer
L---/
G
what about the 120 deg phase difference. it seams like it would produce a very poor 120v supply.

Thanks for taking the time, Ben
Reply With Quote

  #8  
Old 08-28-2011, 05:33 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

Ans: B, There is not 120deg between two phases when there is no other reference it is 180deg , it is identical to 240v 1ph, So if you hook up a 240/120v transformer across 2 phases you end up with 120v 1ph which is no difference than your domestic 120v supply.
I have an example PDF control circuit from the code I will post when I get back to my other PC.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.

Last edited by Al_The_Man; 08-28-2011 at 10:14 PM. Reason: Clarify
Reply With Quote

  #9  
Old 08-28-2011, 06:30 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

Here is the PDF, ref transf 1T, notice how the secondary X2 is grounded right at the transformer and the neutral taken off at this point.
Al
Attached Files
File Type: pdf ControlExample.pdf‎ (491.3 KB, 15 views)
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 09-02-2011, 10:25 PM
 
Join Date: Aug 2007
Location: United States
Posts: 58
chimpera is on a distinguished road

Al, that diagram makes almost everything clear. The only thing left is that two legs of 240v three phase are supposed to only have a potential of 208v. If that's correct then I would need a transformer with a ratio of ~1.73:1.
Thanks again
Reply With Quote

Sponsored Links
  #11  
Old 09-04-2011, 12:08 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

You should be able to get 208-120v from one of your electrical supply houses.
Allen Bradley and I believe Hammond also make them.
The alternative is to buy a toroidal transformer and modify the 120v secondary winding to suit, very easy to do.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's the difference between 2 phase and 4 phase wiring? David Bord Gecko Drives 0 09-01-2010 03:37 PM
5 phase stepper wiring Bambang Otto Stepper Motors and Drives 0 10-27-2009 04:35 AM
3 Phase Converter Wiring ideffects Phase Converters and VFD 7 05-09-2008 06:59 PM
help wiring 1 phase motor ezland00 General Electronics Discussion 7 05-15-2006 04:23 PM
Phase Converter Wiring freak_brain General Electronics Discussion 2 03-15-2005 12:56 PM




All times are GMT -5. The time now is 10:40 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361