The industry standard to conform to the code etc, is to physically disconnect by contactor etc the AC supply side to drives, VFD, AC motors etc.
The controller itself, and if desired, any I/O of an input nature can be left energized to allow ease of trouble shooting.
The control or E-stop relay that achieves this can also have a contact advising the CNC controller a E-stop has occurred.
It is also customary for a watch dog timer or charge pump to detect if the controller (PC) malfunctions, the output of which is usually placed in the E-stop relay series string.