Inductive proximity switches

I have a few basic questions. as far as the most commonly used inductive limit switches.

1. Do all DC limit switches have 3 wires and what is the 3rd wire for? Acording to the schematic you have +,- but then there is the 3rd that looks like it is wire in parralell to the + lead and has a load symbol on it which I assumed was the led?



2. Do AC limit switches only have 2 wires? This confuses me because Usually its the opposite on pneumatic valve solenoids. Usually the DC solenoids have 2 wires and the AC solenoids have the 3rd ground.

3. Lastly is there a way to test the limit switches with a multimeter? What should they read in ohms?


Here is the prox switch

McMaster-Carr
Reply With Quote

  #2  
Old 05-27-2011, 08:01 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

I assume you are talking electronic limit switches? You can get 2 wire or 3 wire AC or DC.
The 3 wire are generally used for a load such as a relay etc, 2 wire have lower current capacity and can be used for PLC inputs etc.
The 3 DC wire can be N.O. or N.C. NPN or PNP.
Not a really conclusive test to use a ohm meter, except test for short circuit maybe.
The link shows various types.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 05-27-2011, 09:42 PM
 
Join Date: May 2011
Location: us
Posts: 99
Skiroy is on a distinguished road

These are DC 3 wires going to a PLC.

The reason I ask about testing them is because. I have a Japanese Tube bender which uses a 3 wire DC prox switch. It lights up. And when I bring it to a Machine with a PLC to test it, triggers a input light. But for somereason its not working in the Japanese machine. We traded it for another prox switch and it works fine. Same wiring,same prox switch but the one that works has a smaller diameter. So this raises a few more questions.

1. Does a smaller diameter prox switch mean a further projected magnetic field to catch a metal object entering the field further away or faster or does the size have nothing to do with it? What specs would indicate this. They both say 200ma?

2. Can a switch led light up and not send an output? And if it does send an output strong enough to trigger a PLC input light can the signal still be too weak for other controller devices, such as the Japanese machine?

3. What signal does the prox switch output ma or Voltage? Whats the PLC looking for, from a prox switch?

4. And finally is there any risk with using a PLC as a testing device for Bad prox switches? I mean if they are bad there is just no connection right?
Reply With Quote

  #4  
Old 05-27-2011, 10:13 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

Smaller diameter generally means closer detection gap.
With different 3 wire Prox, you need to know whether it is NPN or PNP, gnerally the 3 wire are open collector transistor, with most the LED will normally light though, even if a load is not connected.
See the PDF for sink source, NPN/PNP. input to a PLC.
Al.
Attached Files
File Type: pdf sinksource.pdf‎ (257.6 KB, 128 views)
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 06-04-2011, 04:11 PM
 
Join Date: May 2011
Location: us
Posts: 99
Skiroy is on a distinguished road

Originally Posted by Al_The_Man View Post
Smaller diameter generally means closer detection gap.
With different 3 wire Prox, you need to know whether it is NPN or PNP, gnerally the 3 wire are open collector transistor, with most the LED will normally light though, even if a load is not connected.
See the PDF for sink source, NPN/PNP. input to a PLC.
Al.
I always thought PNP vs NPN was the difference between NO vs NC.

I was reading the PDF but it seems a little complicated for my level at this point. Could you maybe give a situation why you would choose a PNP vs NPN limit switch in a real world situation?
Reply With Quote

Sponsored Links
  #6  
Old 06-04-2011, 05:07 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

NPN and PNP can both be either N.O. or N.C.
Usually the selection of PNP or NPN is when interfacing with the like of a PLC etc that has either a Source or Sink input, see the PDF for an example, if the Prox is operating a device such as a relay, or similar physical device, it does not really matter, as it can be set up either way.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.

Last edited by Al_The_Man; 06-04-2011 at 06:22 PM.
Reply With Quote

  #7   Ban this user!
Old 06-04-2011, 06:25 PM
 
Join Date: May 2011
Location: us
Posts: 99
Skiroy is on a distinguished road

Originally Posted by Al_The_Man View Post
NPN and PNP can both be either N.O. or N.C.
Usually the selection of PNP or NPN is when interfacing with the like of a PLC etc that has either a Source or Sink input, see the PDF for an example, if the Prox is operating a device such as a relay, or physical device, it does not really matter, as it can be set up either way.
Al.
Okay thank You. Last 3 questions on this topic.

1. So PNP vs NPN is only a option for DC switches which explains 3 wires on DC switches or 4 wires on DC switches that allow the option to wire as PNP or NPN,right?

2. So for a typical say PNP Prox limit switch that has 3 wires, is it one wire for +, one wire for - and the 3rd for the PNP lead?


3. Finally I have the following phoyo sensor I want to wire to a timer relay so the timer receives the control voltage when the photo sensor's beam is not being broken.

Allen Bradley (AB) Photoswitch 42GRU-92LO | eBay

The documentation says the 4 leads are as follows:
Pin 3 = (+)
Pin 4 = (NPN)
Pin 1 = (PNP)
Pin 2 = (-)

The sensor outputs voltage when the beam is unbroken with a mode switch, but how would I wire the photo sensor to the control input of the timer and the 24VDC PSU?
Reply With Quote

  #8  
Old 06-04-2011, 06:42 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

You show a rather specialized universal item, the run of the mill prox or photo switches generally only have NPN or PNP and are ordered as such as you usually only use one or the other.
But if you can set it as you say so it is operate on light or operate on dark, then what are the spec's of the timer relay you intend using?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #9   Ban this user!
Old 06-04-2011, 10:50 PM
 
Join Date: May 2011
Location: us
Posts: 99
Skiroy is on a distinguished road

Originally Posted by Al_The_Man View Post
You show a rather specialized universal item, the run of the mill prox or photo switches generally only have NPN or PNP and are ordered as such as you usually only use one or the other.
But if you can set it as you say so it is operate on light or operate on dark, then what are the spec's of the timer relay you intend using?
Al.
Just a standard repeat cycle timer with control voltage of 24VDC. Just uses a typical 2 contact 24VDC coil to trigger the timer.
Reply With Quote

  #10  
Old 06-04-2011, 11:03 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

You should probably be able to use either of the PNP/NPN outputs, more details of a model number of the timer would help to confirm it.
A load resistor in the collector may be needed depending on the characteristics of the contact input.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 06-22-2011, 10:07 PM
 
Join Date: May 2011
Location: us
Posts: 99
Skiroy is on a distinguished road
what does the PLC look for

I want to make a limit switch tester. I have had situations where the limit switch LED lights but still doesnt get signal.

Im going to make a little box that has a 24vdc and 120VAC output leads. Then I can hook up the limit sxwsitch and look for the voltage or current output. I could also use this PSU box to test solenoids easily as well.



1. Okay what does the PLC look from a limit switch, current or voltage?

2. When the limit switch has a current rating of 3-300ma does that mean thats how much current it can accept before malfunctioning or is that the amount of current it passes to the PLC? What determines this current amount? I would think the limit switch has a set resistance so if you apply 24VDC to it,it should have the same current everytime?

3. How do you tell if the PLC inputs require PNP vs NPN limit switches?
Reply With Quote

  #12  
Old 06-22-2011, 10:13 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

The input impedance of the PLC decides the current, as to the type of solid state switch needed, the pdf in post #4 will tell you, you need to know the configuration of the PLC, i.e. sink input or source input.
If rigging up a stand-alone tester you need to provide a series resistor that limits the current to less than the current rating of the switch.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need Help!- Inductive Switches jjacstcy DIY-CNC Router Table Machines 31 05-04-2011 09:37 PM
PROXIMITY SWITCHES CHANDRU General Electronics Discussion 1 12-12-2007 07:33 AM
Inductive Proximity Sensors nickfox General Electronics Discussion 3 09-06-2006 09:15 PM
proximity switches woodguy7777 Commercial CNC Wood Routers 4 04-29-2006 04:17 PM
Inductive Proximity Sensors-what are they? Splint General Electronics Discussion 3 08-01-2004 05:24 PM




All times are GMT -5. The time now is 10:35 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361