How do I remove windings from this transformer?

Hello,

Al mentioned the other day that he has successfully removed windings from a laminated transformer.

I would appreciate it if you would coach me on how to do this.

Here is some pics of the transformer. I carefully removed the outer protective film and some of the fabric wrap.

For this I used a Popsicle stick, wooden paint stirring stick, and a plastic putty knife.

The varnish is critical and you need to be careful not to nick it.

It appears the power in (primary) is the outer winding. It has (2) coils connected to it shown in the picture. There is plenty of room for careful work.
The wire gauge looks about .090 thou diameter. The varnish is too thick to measure.

Click image for larger version

Name:	Transf 1.JPG
Views:	46
Size:	170.3 KB
ID:	133611

Click image for larger version

Name:	Transf 2.JPG
Views:	48
Size:	196.3 KB
ID:	133612

Click image for larger version

Name:	Transf 3.JPG
Views:	55
Size:	176.1 KB
ID:	133613

Click image for larger version

Name:	Transf 4.JPG
Views:	52
Size:	161.7 KB
ID:	133614

Click image for larger version

Name:	Transf 5.JPG
Views:	44
Size:	195.9 KB
ID:	133615

Click image for larger version

Name:	Transf 6.JPG
Views:	56
Size:	160.1 KB
ID:	133616
__________________
Everything is bio-degradable, if you run over it enough times with the lawnmower.
Reply With Quote

  #2   Ban this user!
Old 05-08-2011, 06:23 PM
 
Join Date: Sep 2006
Location: US
Posts: 285
Jackal66 is on a distinguished road

Here is the rest of the pics.

The dollar bill shows the physical size of the transformer.

No wonder they charge $100 to ship one of these across the US.

Thanks for your help,
JAckal
Attached Thumbnails
Click image for larger version

Name:	Transf 7.JPG‎
Views:	44
Size:	168.9 KB
ID:	133617   Click image for larger version

Name:	Transf 8.JPG‎
Views:	28
Size:	170.3 KB
ID:	133618  
__________________
Everything is bio-degradable, if you run over it enough times with the lawnmower.
Reply With Quote

  #3   Ban this user!
Old 05-08-2011, 07:18 PM
 
Join Date: Sep 2010
Location: usa
Posts: 838
mike_Kilroy is on a distinguished road
Buy me a Beer?

u seem on the right track. as Al has removed windings, I have added windings to a xfmr to get more voltage for my 2 meter 120 watt amplifier. I wound 3 more turns of couple #12 wires in parallel (I didnt have any thicker wire at the time) around my 1 ph xfmr and IIRC increased output voltage from 12v to 13.5v. be carefull and go for it!
Reply With Quote

  #4  
Old 05-08-2011, 07:57 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by Jackal66 View Post
Hello,

Al mentioned the other day that he has successfully removed windings from a laminated transformer.

I would appreciate it if you would coach me on how to do this.

Here is some pics of the transformer. I carefully removed the outer protective film and some of the fabric wrap.

It appears the power in (primary) is the outer winding. It has (2) coils connected to it shown in the picture. There is plenty of room for careful work.
The wire gauge looks about .090 thou diameter. The varnish is too thick to measure.
I believe you mean the secondary is the outer winding, this is usually the case and appears so in the one you show.
Hopefully the varnish or shellac is not too thick and the idea is to take the outer turns off as carefully as possible.
It is hard to do on a square laminated, but if you first wind ON say 10 turns of small gauge wire on as a means to determine the turns/volt, power up the transformer and measure the voltage on the 10t. it will get you a fairly accurate idea of how many to take off of the secondary.
If you want to re-coat the winding when you are done, you can use Conformal Coating available by the 1 litre can.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 05-08-2011, 08:42 PM
 
Join Date: Sep 2006
Location: US
Posts: 285
Jackal66 is on a distinguished road

Thanks guys,

Al,

I see what you, mean. The H1- H4 are the inputs ( Primary).

The secondary is the outer windings that are connected to the lead , in the close up pic.

It just threw me at first, because the lead wire that goes to the double wire on the coils, is thicker than the H1-H4 wires.

For adding the new wraps, can I use solid household wire?

Maybe strip the sheath on some Romex type 14 ga.and take out one wire. Then use about 4+ wraps and leave the insulation on the wire for protection??


Thanks,

JAckal
__________________
Everything is bio-degradable, if you run over it enough times with the lawnmower.
Reply With Quote

Sponsored Links
  #6  
Old 05-08-2011, 10:06 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

You need insulated wire, and #14 is a bit larger than you need just to get the T/V.
It can be small gauge stranded if necessary as there will not be a load present on the winding.
A stripped multi conductor cable will service.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #7   Ban this user!
Old 05-09-2011, 07:06 AM
vger's Avatar  
Join Date: Jan 2006
Location: usa
Posts: 664
vger is on a distinguished road

If you would rather use enameled magnet wire (like the wire on the transformer now) you might try getting some from a local electrical motor repair shop. They use a lot of it and will probably sell / give you enough to do your rewind. Just be carefull not to scrape the insulation off as you are winding. Give yourself lots of room and cover the inner lamination edges (sharp) with a couple of layers of masking tape that can be removed when you are done winding. You might also ask at the motor shop for some of the stuff they use to coat the windings. This keeps the windings from vibrating, making noise, and heating up from the friction created from movement.

Steve
Reply With Quote

  #8  
Old 05-09-2011, 09:07 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

The alternative to the T/V winding is to simply take off a small number of turns to begin with and then power up and measure the difference, this will tell you the T/V with probably less work.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #9   Ban this user!
Old 05-09-2011, 02:05 PM
 
Join Date: Sep 2006
Location: US
Posts: 285
Jackal66 is on a distinguished road

I found some #10 gauge stranded wire. It was long enough to get (5) turns wrapped real tight on the transformer.

Before it put out 64.9 VAC, now it puts out 75.0 VAC.

So that means each wrap is 2 volts?

On removing the wire to get lower voltage, would removing 5 wraps to lower -10 volts= 55volts x 1.414 rectifier=77.77 new voltage.

My concern is the coil is double wire until it get to the lead wire where both are soldered to the lead.

Since You can't remove 2.5 turns, should I just remove 3 wraps and check it?

Here is a pic of my added wraps:

Click image for larger version

Name:	Transformer add wrap 1.JPG
Views:	26
Size:	133.5 KB
ID:	133717


This pic shows the lead where it connects to the dual wire of the coil. covered in electrical tape.
Click image for larger version

Name:	transformer wrap 2.JPG
Views:	26
Size:	161.1 KB
ID:	133718

Thanks,
JAckal
__________________
Everything is bio-degradable, if you run over it enough times with the lawnmower.
Reply With Quote

  #10  
Old 05-09-2011, 02:31 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,540
Al_The_Man is on a distinguished road
Buy me a Beer?

That's odd, I have seen 2t/V but not the reverse, 2V/t?
I really meant to just wind on the test winding as a separate winding, not put it in series, although that should work, it is usually easier to keep them separate..
At this point, I would take say 5 full turns off the existing secondary and measure the new difference on the old secondary.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 05-09-2011, 03:13 PM
 
Join Date: May 2007
Location: US
Posts: 779
Andre' B is on a distinguished road

Some times it is easier to add turns then to take them off.
In which case you can add the turns but wire them in series but reverse polarity with the existing winding to knock the voltage down.
Reply With Quote

  #12   Ban this user!
Old 05-09-2011, 04:02 PM
 
Join Date: Sep 2006
Location: US
Posts: 285
Jackal66 is on a distinguished road

Al,

I figured if you put on 5 turns and it adds X amount of volts, you know the value of each turn at that diameter.

After removing 3 wraps I checked and it had dropped to only 58V.

Removed 4 & 5 and stayed at 58V

By removing the 6th wrap, it now fluctuates from 56.4 to 57.1 volts.

That would give me from 79.7 to 80.7 DC volts.

That should be close enough for the 80V Geckos shouldn't it?

Marcus at Geckodrives told me :

The G320X will work at 80VDC just fine; we use very robust MOSFETs in our drives and de-rate them to 80VDC from about 110VDC to ensure that they will not blow because of an over-voltage.
It's doubtful that my meter is exactly right on anyway.

I may take off another wrap to be safe.

JAckal

Al,

Here's you a beer.

I owe you a keg after all of the help you've given me.

Thanks!!!!!!!
__________________
Everything is bio-degradable, if you run over it enough times with the lawnmower.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Boss 5 stepper: Which windings in parallel? cabledude Gecko Drives 12 04-26-2012 02:12 PM
Need Help!- Remove M06 oxton Bridgeport and Hardinge Mills 1 09-30-2010 12:54 PM
Butt connector in my motor windings? ZipSnipe General Electronics Discussion 7 02-15-2009 05:37 PM
Different resistance readings in an eight wire stepper windings miro Stepper Motors and Drives 6 12-16-2008 08:44 AM
small engine windings midnite2336 General Electronics Discussion 3 10-08-2007 09:50 AM




All times are GMT -5. The time now is 10:33 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361