3 PH AC motor starter question

I have an air compressor that we are hooking up. It runs on 460 3 ph power. The motor starter that I have is rated for 460 on the input/output and the low voltage(on/off) side is rated at 208. I have 240 in the shop, both single and 3 phase. Can I use 240 with this device for the low voltage on off side?
__________________
www.machmachine.com
Reply With Quote

  #2  
Old 12-02-2010, 08:19 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

Please clarify? What do you mean by 'low voltage on/off side'?
Is this a simple 3 phase contactor?
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 12-02-2010, 08:36 PM
 
Join Date: Apr 2010
Location: USA
Posts: 231
dingo0722 is on a distinguished road

the way it is set up is to use a normal 20Amp switch to activate the relay with the 460 voltage. The relay is alo connected to the air compressor pressure switch. They relay say 208V 60Cy. I was wondering if the relay could operate by using a 240 volt source instead of a 208 volt source. If not I could always by a small 150VA step down transformer
__________________
www.machmachine.com
Reply With Quote

  #4  
Old 12-02-2010, 08:56 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

I am assuming you mean the coil voltage?
If it is presently a 208 coil, you should be OK with 240, if it runs hot, it might be wiser to get the right coil, they can be purchased from any electrical supplier.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 12-02-2010, 09:00 PM
 
Join Date: Apr 2010
Location: USA
Posts: 231
dingo0722 is on a distinguished road

thats what I thought. Any idea what the coil goes for. The unit is an allen bradley. Does the brand matter or are they standardized
__________________
www.machmachine.com
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 12-02-2010, 10:11 PM
lgalla's Avatar  
Join Date: Jul 2006
Location: canada
Posts: 1,250
lgalla is on a distinguished road
Buy me a Beer?

You should post a picture orf the rating plate on the motor.You cannot run a 460 volt 3ph motor on your 240 shop voltage.Perhaps the motor has lower voltage taps?
Yes you could run the coil of the starter off your shop 220,but you still need the 480 for the motor.Al could explain much better than I.
Larry
__________________
L GALILEO THE EPOXY SURFACE PLATE IS FLAT
Reply With Quote

  #7  
Old 12-02-2010, 10:23 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

Larry is correct, the plate may show if it is possible change the motor to 240.
Most motor bring all 6 ends out and can be connected star/delta for 220/480.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8   Ban this user!
Old 12-03-2010, 06:23 AM
 
Join Date: Apr 2010
Location: USA
Posts: 231
dingo0722 is on a distinguished road

I should have mentioned tha I have a step up transformer going from 240 3ph to 460 3ph just for the compressor. The compressor motor, a Baldor, has duel voltage listed on the plate,230/460. When I opened up the box on the motor there were only 3 wires. The previous owner had the unit running on 460V. Dont know if the plate is in error or someone removed the other 3 wires.

So for the high voltage power, I will bringing 460 into the starter and then to the motor. From your comments below, I should be able to use my 240 single phase to power the coil even though the coil has a plate on it that says 208V.

I found coils on McMaster for about $56. But I am unsure if they are the same form factor: McMaster-Carr
listed on the bottom of the page. I can then select 110/240 voltage range

thanks
__________________
www.machmachine.com
Reply With Quote

  #9  
Old 12-03-2010, 09:30 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,538
Al_The_Man is on a distinguished road
Buy me a Beer?

AB like many manuf make NEMA and IEC style, the coil has to be for the same frame size of contactor.
You could run the 208 coil for a while on 240 and monitor the temperature.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 12-14-2010, 05:50 AM
 
Join Date: Dec 2010
Location: South Africa
Posts: 21
vanjast is on a distinguished road

Dingo, try get hold of either a users or technical manual on the compressor.

What you're probably currently looking at is the compressor motor connected for 'Star' 3-phase (you mention only 3 wires and it was set up for 3-phase operation). There are probably configuration links with 6 bolts to connect to. Get hold of a manual before you wire up and switch on power.

Secondly, get hold of a multimeter and measure the voltages across the wires. If they're all in the range of 400+ volts (AC) you're looking at 3-phase power. If it's 3-phase you're missing an earth wire, and possibly a neutral wire as well.

If 2 wires are at 220V(110) AC and one pair around 0V (should be close to 0V otherwise there's a earth problem), then you have 1-phase 220V(110v).

If you get other voltages there's a power/wiring problem
It's advisable to call in a qualified electrician to do a basic checkup as this is cheap compared to a blown motor and possibly a fire, which the insurance will refuse to payout.
Reply With Quote

Sponsored Links
Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Quick Starter Relay Question for regular motor Cartierusm General Electronics Discussion 4 01-13-2009 12:38 PM
Humming noise in Car Starter motor ramee20374 General Electronics Discussion 0 10-25-2008 11:08 AM
Starter Bit Set Recommendations 3D Robotica General Material Machining Solutions 0 07-23-2007 02:18 PM
New starter to CNC Simon_18 General Metal Working Machines 5 06-09-2006 11:09 AM
Starter motor as servo? wile_e Servo Motors and Drives 10 01-10-2005 05:57 PM




All times are GMT -5. The time now is 03:28 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361