Good earth ground, what is your definition?

050601-1325 EST USA

I do not expect that all of you are able to answer all of these questions. But answer those that you can.

How do you define a good earth ground?

What resistance do you measure at 60 Hz and 100 kiloHz?

How would you measure the resistance?

Do you know what the NEC ( National Electrical Code ) requires for equipment grounding?

.
Reply With Quote

  #2  
Old 06-01-2005, 02:14 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

It is usually the resposiblility of whoever installs the supply into a building to connect up to the earth conductor provided by the Electric Service provider, which originates from the grounded star point of the three phase supply, this should be carried through and connected to all electrical equipment in the building, some manufacturers also recommend a ground rod or stake be driven in at each machine location and bonded to the incoming service ground.
To measure the actual value of the ground at a building with respect to the actual star point, (never often done), the resistance by current drop and is measured from the incoming point to a ground rod or good source of ground as far as practically possible at least 5 times the depth of the test ground rod etc, The (Planet) Earth is considered to be zero resistance, the code I believe says anything above 25ohms is not passable, recommended 2 to 3 ohms tops.
If an incoming ground is not available, Ground rods or electrodes are allowed.
Now there is available sophisticated equipment that is used to measure the GR.
There is probabally a more definitive explanation if you google.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 06-01-2005, 08:52 PM
ghyman's Avatar  
Join Date: Feb 2005
Location: USA
Posts: 214
ghyman is on a distinguished road

Originally Posted by rc-cellar
Once again... "THE MAN" spouts off on a subject he knows absolutely nothing about.
Bad form, pal.

This is an adults-only forum. Please try to act like one.

Furthermore, if the answer that was offered is incorrect, or if you have a different solution, then please share it with the rest of us.
Reply With Quote

  #4   Ban this user!
Old 06-01-2005, 09:24 PM
Karl_T's Avatar  
Join Date: Mar 2004
Location: Dassel,MN,USA
Posts: 1,318
Karl_T is on a distinguished road

When I was an engineer (3M) one great fear was ground loops. Really does weird things to control equipment. All ground and sheild wires in a machine were bonded at only one point, other end of wire left free. The bond point was attached to the machine case and a ground went back to the main ground point at the building electrical entrance. Other ground rods, tying to other ground points was a HUGE NO NO.

I'm not the expert here, but the control guys were adment about this.

Karl
Reply With Quote

  #5   Ban this user!
Old 06-01-2005, 09:47 PM
 
Join Date: Jan 2005
Location: Missouri
Posts: 746
2muchstuff is on a distinguished road

ghyman,

Well put, I second it.
__________________
If it's not nailed down, it's mine.
If I can pry it loose, it's not nailed down.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 06-01-2005, 11:15 PM
 
Join Date: Oct 2004
Location: USA
Posts: 395
OCNC is on a distinguished road

Originally Posted by Karl_T
When I was an engineer (3M) one great fear was ground loops. Really does weird things to control equipment. All ground and sheild wires in a machine were bonded at only one point, other end of wire left free. The bond point was attached to the machine case and a ground went back to the main ground point at the building electrical entrance. Other ground rods, tying to other ground points was a HUGE NO NO.

I'm not the expert here, but the control guys were adment about this.

Karl
Did this apply to control wiring and power wiring or only control wiring? It seems like you would want to protect the control wiring from small potentials that could develop between points in a ground loop and cause false triggering but that power wiring might be safer with 'local' grounds in the event of short circuits.

Chris
Reply With Quote

  #7  
Old 06-01-2005, 11:21 PM
miljnor's Avatar
S.N.A.F.U.
 
Join Date: Jan 2005
Location: usa
Posts: 1,844
miljnor is on a distinguished road

i have the benefit of having this explained to me recently. (still means i don't know what i am talking about. ) but if you connect the ground rod to the incoming ground wire there is no "Loop" thus still "bonded at one point".

and i think if you read the post by AL he says that. So.....
__________________
thanks
Michael T.
"If you don't stand for something, chances are, you'll fall for anything!"
Reply With Quote

  #8   Ban this user!
Old 06-02-2005, 05:50 AM
gar gar is offline
 
Join Date: Mar 2005
Location: USA
Posts: 1,498
gar is on a distinguished road

050602-0524 EST USA

Thanks folks:

I am glad to see some response on this subject.

I would like to see more quantitive data from all of you on ground resistance.

Al did provide some values, his NEC 25 ohms is correct. But I would like to know the construction of the ground system and soil conditions that produced 2 to 3 ohms ground resistance.

Al I know of one large plant ( million sq-ft ) where their primary 480 delta was completely floated from ground except for leakage impedance, of which there would be considerable. How the code reads on this I do not know. I also do not know if they had large capacitors to ground. Their building structure and safety ground wiring provided for personnel safety.

In general the code requires a protective earth ground at the service entrance.

More input please.

.
Reply With Quote

  #9   Ban this user!
Old 06-02-2005, 08:20 AM
 
Join Date: Nov 2004
Location: USA
Posts: 138
trilect is on a distinguished road

Ground needs depend on what your protecting the equipment from.

Medical grounds would be hated by the audiophile where ground loop avoidence would be unacceptable to medical and industrial applications (where copper data control wiring is present)


Lighting protection is also a different monster and can cause ground loop problems when machinery on a roof is electrically grounded and also has the metal case tied to the lighting protection ground.


also depends on the electrical code of the state where the ground in question is located and how the inspector interprets that code.
Reply With Quote

  #10  
Old 06-02-2005, 09:34 AM
Scott_bob's Avatar
Mfg Engineer
 
Join Date: Nov 2003
Location: United States
Posts: 458
Scott_bob is on a distinguished road

Interesting,

Personally, I know enough about electrical to stay away from it...
From experience though, the ground issue has been very problematic for reliable CNC controls. Of the CNC machines I have worked on the Fanuc has been the most susceptible to damage due to spikes, feed back, surges what ever they are, I don't know. By ensuring that a good low resistance ground rod is provided at "each" CNC, reliability has been improved.
The ohms resistance that I remember was to no more than 9 ohms...
In Colorado where the soil is mostly decomposed granite, the ground rod had to be 6 feet deep minimum, and the hole thru the concrete slab had to be kept wet in order to enhance the conductivity of the ground rod. No small task considering what it takes to get a copper rod driven into 6 feet of dg. In that part of the country, electrical storms are a serious issue. We had to shut down in the afternoons or risk major disasters with sensitive CNC equipment. They do go haywire when voltage comes in where output should be going.
This really is a serious problem for a lot of folks, I'm glad to see some informed discussion...
__________________
Scott_bob
Reply With Quote

Sponsored Links
  #11   Ban this user!
Old 06-02-2005, 12:49 PM
gar gar is offline
 
Join Date: Mar 2005
Location: USA
Posts: 1,498
gar is on a distinguished road

050602-1232 EST USA

Scott_bob:

Can you clarify the wiring of the separate ground rod.

When a separate ground rod was used at each machine was there still a heavy safety ground wire running back to the service entrance, or was the machine isolated and solely dependent upon the ground rod for grounding?

Do you know how the ground rod resistance to ground was measured?

How often did you pour water into the ground rod hole?

What resistance values were obtained with and without added water?

When you speak of problems from electrical storms, what were the specific problems? Were these mostly momentary loss of power, or large voltage transients, or close by lightening strikes ( very large transient, maybe a million volts or more )?

.
Reply With Quote

  #12  
Old 06-02-2005, 03:49 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by trilect
Medical grounds would be hated by the audiophile where ground loop avoidence would be unacceptable
THATs why the audiophile wasn't in today, he was off due to Medical Grounds.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ballscrew Basics Swede Linear and Rotary Motion 101 04-16-2012 08:09 PM
Motor supply ground vs Logic ground? Gashmore General Electronics Discussion 11 06-07-2005 05:21 PM
Power Supply ground question chas Gecko Drives 5 04-16-2005 06:48 AM
Please help find good CNC... dino-new General Metalwork Discussion 11 01-13-2005 05:24 AM
Ground Ballscrew - No nut! Swede General Metal Working Machines 4 11-20-2004 02:42 PM




All times are GMT -5. The time now is 06:48 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361