Power supply help

Hi,
I need help in determing the power supply for the following DC servo motor.

nominal terminal volt = 120

Max continous current = 4 amps
Max Peak current = 20 amps

I looked at various threads and am able to inderstand some of the terms, but I am not a electrical guy. If I am provided with the diagram then I can solder and assemble it together.

everybody suggests torodial transformer (What specs? I am using 4 motors so 120X4 = 860 VA. On Plitron website I can see one at 1500 VA with 117 volts output, does that means 1150/117 = 12.82 amps. Is this amps enough?)

Also what else do I need to construct the power supply. What kind of bridge rectifier, capacitor etc, wire gauge etc. Your input is appreciated

thanks
Onkar
Reply With Quote

  #2  
Old 06-01-2005, 09:49 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Are these 120v DC motors? you could probabally get away with that VA as allowing for average duty cycle, you will probabally never pull 4 amps on each motor at once, the 20 amps is the peak rating of the motor which you should never see if the amplifiers are capable of current limiting to 4 amps. You will need around a 85vac secondary to give you the 120vdc. The Capacitor size will depend on what your required DC voltage will be.
You can use a 12,000µfd capacitor to give you 2.5% ripple at 12a 120vdc.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 06-01-2005, 10:00 AM
 
Join Date: Jan 2005
Location: canada
Posts: 55
osdhillon is on a distinguished road

Al
Yeah These are 120v DC motor. The transformer I specified, Is it the right one? What kind of brige rectifier and capacitor I need. What else do I need. I already built one using the kit fron Dan. That one is running is fine (36 vDC 25 A). Does somebody have schematic for torodial one. Thanks
Onkar
Reply With Quote

  #4  
Old 06-01-2005, 10:20 AM
Cyclone's Avatar
*Registered User*
 
Join Date: Mar 2004
Location: Florida
Posts: 60
Cyclone is on a distinguished road

you might want to pick one up like this...toroidal ...Can't beat the $15.00 price considering that they sell between $100 - $200..unwrap the outer primaries (easy job) and rewind with 12 or 14gauge wire to up the amps(16gauge now) I also used the help from this forum and the great guys here. I posted this schematic a few days ago on another thread but here it is anyhow, hope it helps.
Attached Thumbnails
Click image for larger version

Name:	schematic.jpg‎
Views:	115
Size:	259.9 KB
ID:	7954  
Reply With Quote

  #5  
Old 06-01-2005, 10:42 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by osdhillon
Al
Yeah These are 120v DC motor. The transformer I specified, Is it the right one? What kind of brige rectifier and capacitor I need. What else do I need. I already built one using the kit fron Dan. That one is running is fine (36 vDC 25 A). Does somebody have schematic for torodial one. Thanks
Onkar
The one you indicated in your first post was 117vac, this would give you around 165 VDC when rectified and smoothed, Take the desired DC voltage that you want to end up with and multiply by .707 +2 equals the secondary AC voltage of the transfomer you need.
These motors ideally should be run at 100 to 120vdc, otherwise you will not get the maximum power out.
A torioid is wired exactly the same as a common square type as far as primary and secondary connections are concerned.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 06-01-2005, 10:57 AM
 
Join Date: Jan 2005
Location: canada
Posts: 55
osdhillon is on a distinguished road

Al
thanks for clearing things up. I was under impression that the volts specifed are DC (I wasn't aware of the rectifier converting AC to DC) Does the DC amps remain the same as AC amps. To run motors fully at 120 vDC I figured 120*.707+2 = 86.9 vAC
I am getting one from "avellindberg", the specs are 1000VA (secondary volt = 45+45)
ie 90 volts (which gives 125v DC output, 11.11 amps) the other one is (Secondary volt =40 +40) which gives 110 vDC,12 apms. Which one do you recomend? how about the amps. This is part I am having hard time to understand. Do I need total of 16 apms (4 motors at 4 amps each) or less?

cyclone , your schematic is great, thanks, I have to modify it to my specs. Any suggestions?

Thanks
Onkar
Reply With Quote

  #7   Ban this user!
Old 06-01-2005, 11:59 AM
 
Join Date: Aug 2004
Location: US
Posts: 2,786
ViperTX is on a distinguished road

You should be fine with either toroidal transformer...but before you proceed....which driver are you using to drive the servos?
Reply With Quote

  #8   Ban this user!
Old 06-01-2005, 12:23 PM
 
Join Date: Jan 2005
Location: canada
Posts: 55
osdhillon is on a distinguished road

I am using MACH3 controller and probably Rutex drives. I am very comfortable with Gecko, due to voltage limitation I have to go to other source.

How can I convert 12 amp into 20 or 30 amp. What is the real purpose of the capaitor? Does it do more that just storing the power? Does it increases the amps too ?

If I cannot increase the amps, then should I connect two transformer in parallel to get the desired amps. What safe amps should I looking at (4 motor 4 amps each at full load)

thanks
Onkar

Last edited by osdhillon; 06-01-2005 at 12:41 PM.
Reply With Quote

  #9   Ban this user!
Old 06-01-2005, 12:50 PM
DieGuy's Avatar  
Join Date: Apr 2005
Location: USA
Posts: 420
DieGuy is on a distinguished road

The general rule of thumb for transformer sizing is about 2/3 total load. It is unlikely that you will be drawing full load on all 4 motors at the same time.
Reply With Quote

  #10   Ban this user!
Old 06-01-2005, 12:52 PM
 
Join Date: Jan 2005
Location: canada
Posts: 55
osdhillon is on a distinguished road

Originally Posted by Cyclone
you might want to pick one up like this...toroidal ...Can't beat the $15.00 price considering that they sell between $100 - $200..unwrap the outer primaries (easy job) and rewind with 12 or 14gauge wire to up the amps(16gauge now) I also used the help from this forum and the great guys here. I posted this schematic a few days ago on another thread but here it is anyhow, hope it helps.
What is the max amps I can get out of it ans using what gauge of which wire. Sorry to ask so many questions at once but I am trying to learn
Thanks
Onkar
Reply With Quote

Sponsored Links
  #11  
Old 06-01-2005, 01:23 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Originally Posted by osdhillon
I am getting one from "avellindberg", the specs are 1000VA (secondary volt = 45+45)
ie 90 volts (which gives 125v DC output, 11.11 amps) the other one is (Secondary volt =40 +40) which gives 110 vDC,12 apms. Which one do you recomend? how about the amps. This is part I am having hard time to understand. Do I need total of 16 apms (4 motors at 4 amps each) or less?
I would go with the 40+40.
As two of us have pointed out you probabally will not be drawing full load at any given time, theoretically the full load would be 4x4=16amps only if the motors were all in a full load state, in normal use any motor can be anywhere from 0 to 4 amps at any given time so a duty cycle factor is used to give you an average.
The output of the rectifier is a 120 cycle ripple so the capacitor is used in order to provide steady state DC as near as possible under all loads.
There is plenty of information in previous posts as this subject has been covered many times.
Al
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #12   Ban this user!
Old 06-01-2005, 01:28 PM
 
Join Date: Jan 2005
Location: canada
Posts: 55
osdhillon is on a distinguished road

AL

Thanks
Looks like I am on the track. Once I get my parts in, Probably I will help again (Wnat to do it right the first time). I was recommend from the guy selling me motor to use 750 VA each axis along with recifier and capacitor for each axis and the price near to $ 200 each axis.
Thanks
Onkar
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How does a power supply work. ynneb DIY-CNC Router Table Machines 1 07-27-2011 09:40 AM
Diy Power Supply Choices berin DIY-CNC Router Table Machines 11 07-13-2005 03:47 PM
5 Volt Power Supply Tripping murphy625 General Electronics Discussion 13 02-27-2005 09:05 PM
Is this power supply rating adequate? jerryrigge General Electronics Discussion 3 11-25-2004 10:06 AM
Choosing a Power Supply for Retrofit? pfeist General Metal Working Machines 4 05-23-2004 10:36 PM




All times are GMT -5. The time now is 06:48 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361