Hello everyone,

I’m a long time lurker and have learned a great deal from this forum. I wish it has been available 22 years ago when I built my router. I’m hoping someone can explain why the following happened:

I had replaced my stepper cables with new shielded cables that had a drain wire. The old cables were not shielded and had no drain. I tied the drains on the new cables together and grounded them to the controller chassis.

After I powered up the motors I was hearing lots of clicks and squealing from the motors. Worse, my X axis would occasionally stutter and lose steps. I suspect noise was getting into the system but could not find any logical source.

When I disconnected the drain lug from the chassis I still had the problem, however; when I untied the drains from the common lug the problem went away.

While I can run this without the drains grounded I do wonder what caused the problem. The cables are all well separated. They are 22 gauge and attached to old chopper drivers that are set for 2 Amps/phase. The cables are about 12’ long.

Thanks,
Mark
Reply With Quote

  #2  
Old 03-21-2010, 01:12 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

With the three drain wires disconnected from the common lug, check for continuity from drain to ground also check continuity between the drain and the other conductors in the cable.
If OK, re-mount the ground and common lug and connect one drain at a time and then try each of the combination of pairs.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #3   Ban this user!
Old 03-21-2010, 04:16 PM
 
Join Date: Dec 2008
Location: USA
Posts: 13
mmcleod is on a distinguished road

Al, Thank you for your ideas. Here are my results:

- There was no continuity between the drain wires and any of the conductors.
- With the drains disconnected from the ground lug – there was no continuity between the ground and the drain wires.
- There is no continuity between the drains and the motors or the router frame.
- I can ground any individual drains separately and everything seems okay.
- I tried all the combinations. Whenever I connect 2 or more drains, whether grounded or not then I have problems with the corresponding motors that are connected. Clicking and squealing as well as stuttering.
- I plugged a circuit tester into the 120V side of the controller and I have a good electrical ground. The only other item on the A/C circuit is a refrigerator. There is no other electrical equipment nearby except the computer. I moved the controller and cables about 3 or 4 feet away from the monitor and computer but there was no improvement.

I don’t have a scope to see what the interference looks like. Do you see any potential for problems down the road that would necessitate tracking this down?

Thanks,
Mark
Reply With Quote

  #4  
Old 03-21-2010, 04:43 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

I guess technically you could run the stepper motors unshielded, the principle object is to prevent radiated EMI, steppers are typically low impedance devices so in theory they should not suffer from received EMI as would be servo encoders for e.g. that you want to prevent receiving motor EMI.
I am surprised that they appear to be affected this way.
The only other thing I could suggest if you really want to try using the drain in order to shield the stepper conductors is to try grounding the stepper supply common, as long as this is electrically feasible.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #5   Ban this user!
Old 03-21-2010, 05:45 PM
 
Join Date: Dec 2008
Location: USA
Posts: 13
mmcleod is on a distinguished road

Well, I'm out of ideas. I'll just clip the drain wires and run it that way. It is a mystery and it bugs me that I can't figure it out.
Reply With Quote

Sponsored Links
  #6   Ban this user!
Old 03-21-2010, 08:47 PM
 
Join Date: Jan 2005
Location: USA
Posts: 2,347
mactec54 is on a distinguished road
Buy me a Beer?

Hi mmcleod

It sounds like you have both ends of the sheild connected, you can only have the input end connected to ground, clip the motor end flush with the end of the cable & ground the other end
__________________
Mactec54
Reply With Quote

  #7  
Old 03-21-2010, 08:53 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

I believe he already performed that test that I suggested earlier.
Although that brings up another possibility, are all the motor frames bonded to earth ground, if any are above ground it could be one root cause of the problem.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #8  
Old 03-22-2010, 12:31 AM
Gold Member
 
Join Date: Oct 2005
Location: Australia
Posts: 2,247
RomanLini is on a distinguished road

Don't connect the shields directly to ground, connect them through a 100 ohm resistor.

That should fix your problem with the high frequency ground loops and still provide a fair level of RFI suppression.

If you haven't already done so, it's also a good idea to add a large capacitor (1000uF or 2200uF) at each stepper motor driver directly to it's PWR+ and Gnd pins, mounted as close to the driver as possible. That will help to keep the chopper recirculating current local to that driver and its motor and not looping back through driver-motor-main psu.
Reply With Quote

  #9  
Old 03-22-2010, 09:36 AM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

The recommended approach to ground/bonding is to take a separate ground conductor from ALL motor frames back to the common earth ground point.
Another possibility is to earth ground the power supply common to the star point also.
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

  #10   Ban this user!
Old 03-22-2010, 03:33 PM
 
Join Date: Dec 2008
Location: USA
Posts: 13
mmcleod is on a distinguished road

Well the router frame isn't grounded, it sits on a wood table and the router motor is attached to the frame using non metallic (wood) brackets. I meant to ask about that earlier.

I'll run a test to a grounding rod and let you know what happens. Do I really need to ground each stepper motor separately or would I get most of the benefit by just grounding the frame?

Thanks for your help,
Mark
Reply With Quote

Sponsored Links
  #11  
Old 03-22-2010, 03:43 PM
Al_The_Man's Avatar
Community Moderator
 
Join Date: Dec 2003
Location: Canada
Posts: 16,539
Al_The_Man is on a distinguished road
Buy me a Beer?

Strictly speaking the common bonding technique is to take a ground conductor back to the central earth ground point from each motor and any metallic parts of the machine, gantry etc.
There is no real need for a ground rod, the service supply ground should be sufficient.
The concept behind bonding is to make all metallic parts of the machine one potential, this attempts to rule out the possibility of a ground loop, this can only occur if the grounded metallic/shield/supply common parts of the machine have a different potential between them.
Don't forget the router motor frame, either.
http://www.cnczone.com/forums/showthread.php?t=71923
Al.
__________________
CNC, Mechatronics Integration and Machine Design.
“Logic will get you from A to B. Imagination will take you everywhere.”
Albert E.
Reply With Quote

Reply




Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Drain Tube Problem hgporter@porter Shopmaster/Shoptask 1 07-31-2008 04:56 PM
TM-1P chips plug drain too fast juxtoposed Haas Mills 2 05-06-2008 05:52 AM
Drain Pre-screen Mooser Tormach PCNC 1 03-13-2008 11:37 PM
Wow the VF3 Drain holes for coolant get clogged up! Rocko1 Haas Mills 4 03-11-2008 01:43 PM
SL-10 Coolant Drain Upgrade Edster Haas Lathes 3 01-20-2008 10:01 AM




All times are GMT -5. The time now is 06:37 PM.





Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2012, vBulletin Solutions, Inc.
Content Relevant URLs by vBSEO
Template-Modifications by TMS

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147 148 149 150 151 152 153 154 155 156 157 158 159 160 161 162 163 164 165 166 167 168 169 170 171 172 173 174 175 176 177 178 179 180 181 182 183 184 185 186 187 188 189 190 191 192 193 194 195 196 197 198 199 200 201 202 203 204 205 206 207 208 209 210 211 212 213 214 215 216 217 218 219 220 221 222 223 224 225 226 227 228 229 230 231 232 233 234 235 236 237 238 239 240 241 242 243 244 245 246 247 248 249 250 251 252 253 254 255 256 257 258 259 260 261 262 263 264 265 266 267 268 269 270 271 272 273 274 275 276 277 278 279 280 281 282 283 284 285 286 287 288 289 290 291 292 293 294 295 296 297 298 299 300 301 302 303 304 305 306 307 308 309 310 311 312 313 314 315 316 317 318 319 320 321 322 323 324 325 326 327 328 329 330 331 332 333 334 335 336 337 338 339 340 341 342 343 344 345 346 347 348 349 350 351 352 353 354 355 356 357 358 359 360 361