The E-Stop circuit should cut power to all of the output devices.
For inexpensive high power relays, I like these or similar. Google ''PRD relay'' https://www.automationdirect.com/adc...AD-PR40-2C-24D
Never use a solid state relay in a safety circuit, many times their failure mode is a dead short, this has the effect of it being turned on and you can't shut it off. I do like to use solid state relays with zero crossing turn on in series with an electromechanical relay to mitigate some of the inrush. These turn on when the sine wave crosses 0 volts and brings the power up to max over about 8 ms, gives the caps a chance to charge more slowly thus reducing the average current on the feed.
The enable signal should also be cut on an E-stop. And should not power back up until you press the Enable button after the E-stop condition is cleared.