    Question Split phase on industrial devices
    Hi there,
    I want to build a professional CNC router for my garage.
    I want to use the residential split phase configuration for power to my VFD and industrial power supplies.
    I cannot find any straight answer regarding connecting 240V 1ph (L/N/E input) apparatus to 120V/120V (L1/L2/E).
    Can I feed the other line to neutral terminal?
    I asked the same question to my EE at my job and his head exploded! He said don't do that... why?
    How do you guys runs your CNC at home? (step up transformer?)
    I'm trying in hope to have a clear answer
    Thanks a lot!!!
    Laurent
    Member ger21's Avatar
    Mar 2003
    Shelby Township
    Default Re: Split phase on industrial devices
    What country are you in?
    UCCNC 2017 Screenset
    Mar 2017
    Canada... 60hz in fact the same as US regarding residential power.
    120v - 0v (center tap) - 120v
    Dec 2003
    Simple if using 240v feed to the VFD, no neutral is required.
    Just come off of a dual breaker.
    If only using 120v then you would need a 120v VFD, but i would recommend you use 240v
    Use 120v for the rest of the control.
    Mar 2017
    There is no neutral available (NEMA 6-15 receptacle). I don't mind supplying 240v to the power supplies (and all the cabinet).
    Example:
    Take my 24V meanwell power supply. There is a 240v switch but can you put two LINE on it? Clearly state LINE + NEUTRAL on the terminals.
    Dec 2003
    That is for countries such as UK etc that have 240v and N, in N.A. if using 240, just wire L1 and L2 to the N&L no neutral required.
    Ensure you have a ground.
    Member john-100's Avatar
    Mar 2007
    uk
    if you have equipment designed for a 240V single phase supply like I have in the UK
    you can connect it to your 240V split phase suppy
    provided the equipment has a two pole on/off switch and both L1 & L2 has the correct fuse or MCB
    just connect L1 to L , L2 to N and E to E
    John
    PS
    with switch mode power supplies the single phase AC supply is rectified to produce about 340V DC which
    is then converted to a high frequency AC so it can be stepped down using a small ferrite cored transformer ,
    then rectified to produce the DC output
    If I remember correctly
    with 3 phase VFD drives for the spindle motor
    you can connect a 240V supply to the 3 Phase supply terminals L1(R) and L3(T) do not connect to L2(S)
    using a single phase supply instead of a 3 Phase will reduce the maximum power available to 60% ??? - will need to check the manual
    PPS see ATX power supply circuit
    Split phase on industrial devices-atx-power-supply-jpg
    the LRS-350-24 power suppy is simpler circuit with a single 24V DC output ( and no standby 5V circuit !)
    Last edited by john-100; 03-24-2017 at 07:39 PM. Reason: add ATX circuit example and ref to 24V supply
  8. #8
    Mar 2017
    Thanks guys for all your reply!
    Everything make sense now!
    PS: Grounding is not an option, everything will be star grounded in the cabinet.
  9. #9
    Member mactec54's Avatar
    Jan 2005
    Quote Originally Posted by ELCouz View Post
    The Power supplies you have are not suitable for you to run them on 240v in Canada, for NA you use 120V ( 1 ) Hot Neutral and Ground, they can be run on 240v, in NA but the failed rate is quite high
    For your VFD and depending on what VFD you have most use L1 to ( R ) and L2 to ( S ) for the 240 Volt connection that is ( 2 ) Hot and a Ground, that is all you connect for the input Power for the VFD
    Mactec54
  10. #10
    Dec 2003
    In many cases the 1ph connection for VFD can be arbitrary, any combination of R,S,T. as most have just a 3 phase rectifier on the input.
    For e.g on the popular Huanyang I have used any combination and works OK.
    There is only one that I have come across that required two particular inputs and that was a Mitsubishi, because the low voltage supply was fed off of two particular inputs, instead of created internally after the bridge.
    Jan 2005
    Quote Originally Posted by Al_The_Man View Post
    Huanyang can run on any combination, but most sellers will say to use R and T for the single Phase connection, this has the best reliability than any other connection combination
    Mitsubishi, is only one of many that you have to use a specified connection for the input power, Yaskawa, Bosch, Emerson, Delta, Teco, Nowforever, the list is endless, most of the quality VFD drives will use R and S connection only for input power connection
    It also depends how the internal DC Bus is connected, as to what input connections are best to use
    Mactec54
  12. #12
    Dec 2003
    I DID SAY in MANY CASES, over the years I have used many of the main manufacturers and this is what I have personally found the case to be.
    As a rule, if the manual does not specify otherwise it is safe to assume any 1ph connection will work.
    If as is common the input is just to a 3ph rectifer, it does not matter.
    In the case of the Huanyang, et-al. the low voltage supplies are derived and fed after the 3ph rectifier, as is seen at power off where the logic stays active for some seconds.
    You appear to insist on this regardless as per the recent post where you responded to a poster that claimed it to be so for Powertran, when an email to the company contradicted it.!
    Mar 2003
    Shelby Township
    Here' the message I got for the Huanyang I just bought.
    Regarding the wire connection, please connect "R" and "T" (at the inverter) to the shingle phase power supply (actraully, connect "R" and "S" or "S" and "T" both are ok.) If you use it as three phase input, then please connect the three phase power supply to "R, S T". "U, V, W " connect to a motor.
    I think that this means you can use any two?
  14. #14
    Dec 2003
    Quote Originally Posted by ger21 View Post
    A lot clearer than my Huanyang manual,
    "The power source is put into through the RST terminal, output on the UVW terminals. 220v can connect wilfully two phase of R.S.T."
    AL.
    Jan 2005
    That is correct you can use any 2 connections, the most reliable though has be R and T for this VFD with 240v NA supply
    Mactec54
  16. #16
    Dec 2003
    Detailed Technically based reason for the recommendation?
    Dec 2003
    Just to put this to bed once and for all.
    Opening up the Huanyang on the bench, the R,S,T terminals go direct to a 3phase rectifier, therefore there is exactly no electrical difference between ANY combination of 2 out off the 3.
    Jan 2005
    The hundreds of postings speak for themselves, when users have had trouble with these VFD Drives it is usually how they have been wired, when they have changed there wiring connections to R and T there problems are usually gone, some also run fine on R and S, there are so many copies of this VFD it's hard to know what is going on Technically, they are all using a 3 phase rectifier, it may be how the DC Bus is connected across the rectifier as this can make a difference as to which connections are used, this simple snip speaks for it's self, how these cheaper VFD drives are configured inside
    This shows why R and T is a better Balanced connection
    Attached Thumbnails Attached Thumbnails Split phase on industrial devices-simple-rectifier-dc-bus-connection-2-png
    Mactec54
  19. #19
    Jan 2005
    And don't all VFD connect the same way, with some taps for internal low volt supply, R, S, T to the 3 phase Rectifier is normal, it's how the rectifier has been used, configured after the input as to what is the best connection to use, it has very little to do with the first Rectifier stage
    Mactec54
  20. #20
    Mar 2003
    Shelby Township
    DMM recommends R & S for their Dyn4 servo drives.
    The Huanyang manual says any two, but the seller recommended R & T first, but any should work.
    So I guess their is some difference.