I have 6A per phase motors and on the gecko G203V it says with that amperage use a current set resistor that is 282Kohms but the only thing close to this is 270Kohm or 300Kohm can i go with the 300Kohm or do i need to use the 270Kohm |
| I think I would error on the low side. The stepper may not like the extra amperage....
__________________ Walking is highly over-rated |
How do I obtain 3500 ohm resistance? My motors are 4A but being run on a G540 so 3.5A max........3.5 x 1000 = 3500 ohm or 3.5k ohm? What combination of common values will give me the above? |
| I was going to give a link to Mouser electronics, but then noticed you were in the UK. I've been hunting for a supplier that has 3.2k in single qty. Mouser and Digikey has a min order of 1000 pcs. Don't need 1000 resistors. Although I was able to get 2.8k in single qtys. from Digikey. Mouser does offer 3.5k in singles (Digikey 1000 min) Sorry I couldn't help, Maybe somebody will be able to, Jack
| I believe I can get 3.48k ohm from RS here in the UK with 0.125w rating. I guess the resistance is ok - what about the rating? Will this be sufficient for a current set device? RS will happily sell in 10's and then only cost pennies / cents - as you say don't really need 999 spares ! |
| will these resistors work for a 6.1amp motor setting on G203s? Might be a good source for others as well, as 5 pieces is just right, and they are cheap! The metal film is fine to use, right, i mean it doesn't matter what type of resistor does it? Also it has 1% instead of 5% tolorence, but thats fine, or even better, right? 280k for 6a motor 316k for 6.1a motor (318.5k is equation answer) Last edited by Wolfesmetalfab; 12-07-2008 at 08:57 PM. |
Metal film resistors with leads may have too much inductance for high frequency circuits but should not be a problem for these drives. Depends on the circuit design's sensitivity to small inductance values. An online parallel resistance calculator is at http://www.1728.com/resistrs.htm and can calculate for up to 10 resistors in parallel. If you need something like 3500 ohms (3.5K) double that value (7100) to start with. Then pick the next higher and the next lower standard resistance values and see what that gives you. You can then raise the higher standard value to the next higher value again to raise the parallel resistance, or lower the smaller value resistor if you need to achieve a slightly lower parallel resistance. CarveOne
__________________ "A $1,000 electronic device will almost always protect a ten cent fuse." |
#10
That's what I used and it works fine. Gary |
#11
The 67% rule for power supply, is because you are never going to be pulling the full load on every motor, so you dont need to have enough power to do so, but the individual motors may pull 6 amps or close every once and awhile, thats why you need to have the current set resistor set at 6 amps in your situation. Does that make sense? |
| Current set resistor-G203v | C.Michael | Gecko Drives | 7 | 02-02-2008 05:22 PM |
| Please help, current limit resistor calculations | scratch_6057 | Open Source Controller Boards | 5 | 01-24-2007 09:49 AM |
| Help with current set resistor math | Hack | Gecko Drives | 9 | 04-29-2006 12:07 PM |
| Current limiting resistor | pyrojon | General Electronics Discussion | 8 | 04-19-2005 09:47 PM |
| Current Set Resistor | CRFultz | Gecko Drives | 0 | 08-06-2004 01:48 PM |