No or maybe if I misunderstand your question.
Most switching drives depend on a reference voltage. Once the motor current sense reaches that reference, the drive reverses the direction of current change and the current revereses. The result is the motor current oscillates between the peak value set by the reference level as a peak and some value below that.
The motor responds only to the average value (0.5 peak to peak subtracted from the peak value). This introduces a negative offset equal to 0.5 peak to peak value. This in turn results in a crossover distortion equal to that value. Our means of compensating for this error is to introduce a constant positive adjustable offset via the ADJUST trimpot to null this V/L error. The result is a motor phase current that passes thru zero without any discontinuity.
Kreutz. You are a very smart guy. I have followed your posts and I am impressed with your thinking. Why don't you PM or e-mail me at
geckohall@cox.net so I can meet you. We are not at cross-purposes at all. You are doing unpolar drives and I would like to take the oppertunity to talk you out of that.:-)
Mariss